Calculating Power Consumption

09/25/2008 9:32 AM

how to calculate the power consumption in kva for a site with 3ph and 1ph loads

the only parameter i had is the per ph amper consumption

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Calculating Power Consumption

09/25/2008 10:18 AM

To calculate power consumption

KVA x power factor = kilowatts

KW x hours used x cost per kwh

Add 1 phase and 3 phase together.

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#2

Re: Calculating Power Consumption

09/26/2008 10:09 AM

If you don't have actual voltage, you should at least be able to get nominal voltage of both load types from equipment nameplates. A good estimate of apparent power (KVA) can be obtained using the procedure shown below.

For the 3ph system, calculate the average current for all 3 phases:

(I1 + I2 + I3)/3 = Iaverage

Using average current and nominal voltage, calculate 3ph KVA:

(Vnominal3ph x Iaverage x 1.732)/1000 = KVA3ph

For the 1ph system, use the measured current and nominal voltage to calculate 1ph KVA:

(Vnominal1ph x I1ph)/1000 = KVA1ph

The total apparent power used is the sum of the 3ph and 1ph power flows:

KVAtotal = KVA3ph + KVA1ph

__________________
Experience: The knowledge you gain just AFTER you needed it.