end switch

10/04/2008 8:21 PM

I am connecting a boiler to a Taco 504 switching relay and the wiring diagram calls for a wire from the XX end switch of the 504 to the TT of the boiler.

Can someone explain to me what this connection actually does?

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: end switch

10/04/2008 8:31 PM

Post the drawing.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#2
In reply to #1

Re: end switch

10/04/2008 11:44 PM

It sounds like it may be the switch, that if not installed properly, will cause a couple of city blocks to be leveled.

.

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Anonymous Poster
#3
In reply to #2

Re: end switch

10/05/2008 11:59 PM

No thats only if the red wire is cut. Connecting the wire will cause implosion, black holes or something.

Register to Reply
Power-User
United States - Member - US Citizen - Born & Raised Engineering Fields - Control Engineering - HVAC/R Simplified Using PLC Controls Engineering Fields - Instrumentation Engineering - HVAC/R Simplified Using PLC Controls Engineering Fields - Energy Engineering - HVAC/R Simplified Using PLC Controls

Join Date: Mar 2007
Location: Brick, NJ (USA)
Posts: 110
Good Answers: 5
#4

Re: end switch

10/06/2008 5:16 AM

Working with a boiler start circuit, the end switch could be from a combustion air damper or water flow switch that must be proved before the boiler start circuit is completed. A complete system layout showing all devices in your system would help.

ilcllc@comcast.net

www.innovativelogicalcontrols.com

__________________
"Memorize the calculations, you look like a fool searching your notes while teaching class"
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#5

Re: end switch

10/06/2008 8:52 AM

From the Taco wiring diagram that you apparently have - very first statement after diagrams:

Operation:

When any thermostat calls for heat, the appropriate circulator

is energized and the isolated end switch (X and X) will start the

boiler.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Anonymous Poster
#8
In reply to #5

Re: end switch

10/06/2008 11:36 AM

Thanks for your response, I understand it now, and in my case I did not have to use the end switch.

Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#6

Re: end switch

10/06/2008 9:05 AM

chibcha38; the thermostat & 24 ac volt transformer are wired to operate the zone valve, when valve is opened to allow water to flow the end switch closes to turn on the boiler & circulating pump. the end switch connected to the T T terminals on the boiler or the zone control panel. perry

Register to Reply
Anonymous Poster
#7
In reply to #6

Re: end switch

10/06/2008 11:35 AM

Thanks for your response, I understand it now, and in my case I did not have to use the end switch.

Register to Reply