Small-Bore Buried Gas Piping

10/06/2008 12:25 PM

What's the latest thinking on buried gas piping? We used to just specify coated, cathodically protected carbon steel piping for gas and other fuels, but this is a 1" line installed for a temporary process. Anyone using HDPE and getting local approval? I am checking with local jurisdiction, but they are sometimes the last to be up-to-speed on new developments.

Thanks for any feedback.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator
United States - Member - New Member

Join Date: May 2007
Location: Milwaukee, WI
Posts: 59
Good Answers: 4
#1

Re: Small-Bore Buried Gas Piping

10/07/2008 12:11 AM

Here in the metro Milwaukee area, WE Energies will make up the HDPE line with the proper fittings crimped on for you for underground use.

It costs a right penny, but you know it's done right then!!

Allen

Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#2

Re: Small-Bore Buried Gas Piping

10/07/2008 7:58 AM

It is fairly common use in Australia , widely used in natural gas reticulation, it is well accepted.

Obviously it is up to as you say local and national regulations.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Power-User
United States - Member - New Member

Join Date: May 2008
Location: Arizona
Posts: 355
Good Answers: 4
#3

Re: Small-Bore Buried Gas Piping

10/07/2008 8:26 AM

Good morning thinman56. HDPE meeting ASTM 3406 or 3408 has been in use many years in the sw US. I recommend 1" CTS SDR 11 for 60 psig or less, altho you don't mention the pressure or your location. There're several fitting manufacturers to choose from, one being R.W.Lyall Co. in Ca.

Register to Reply
Active Contributor

Join Date: Feb 2008
Posts: 21
#4

Re: Small-Bore Buried Gas Piping

10/07/2008 8:50 AM

Thanks, all, for the responses. Local jurisdiction also says HDPE is fine for low-pressure (<100 psig) natural gas and propane, so we'll go with that.

Cheers

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Small-Bore Buried Gas Piping

10/08/2008 4:36 AM

Check the colour codes, though. In the UK, gas is yellow and potable water is blue. Otherwise they are similar materials.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2006
Posts: 757
Good Answers: 12
#6

Re: Small-Bore Buried Gas Piping

10/08/2008 9:53 AM

In my jurisdiction, plastic is now the standard...and required. And preferable. Flexible for easier installation, doesn't corrode. However, cannot be continued inside building where black pipe still the way. This is the latest thinking and standard.