Re: Generator Stator Earth-Fault Protection at Low Frequency Injection
10/11/2008 6:10 AM
The relay measurement unit shall be blocked out of 10-40 HZ, because in this frequency range a zero voltage can also be generated by generators starting up or slowing down.