Cable Voltage Rating

10/13/2008 5:20 AM

Dear Frnds

As per my project scope of work cable voltage rating shall be 600/1000V ,

Now one of my vendor is offering me Cable with voltage rating of 300/500V

What will be the technical conseq if I use 300V rating cable.

Regards

Jose

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Oct 2008
Posts: 1
#1

Re: Cable Voltage Rating

10/13/2008 5:53 AM

Clarify on your load.

First consequence, the cable with the lower rating current carrying capacity would be lower than the 'proper cable' hence might fail in use.

Register to Reply
Commentator

Join Date: Aug 2008
Posts: 56
#2

Re: Cable Voltage Rating

10/13/2008 10:50 PM

Dear Josej

first of all usually all the cables are checked by giving double of its rated voltage. if u need to use a cable on 600V servive it would be checked at 1200V. but it does not mean you start using this cable. such a amargin is given to withstand the voltage spikes in the line.

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#3

Re: Cable Voltage Rating

10/14/2008 8:38 AM

Dear friend,

If your project requirement of a cable is for 600/1000V, then accept only the cable with same voltage range. Half the rated cable offered by the vendor will not be suitable for your project. When the specification of cable is rated for specific voltage by the manufacturer it means that the insulation of the cable is capable of withstanding a voltage level specified with out insulation failure. The requirement of a cable with 1000 volts means the cable can be safely used with out insulation failure for 440 volts system. This is for considering the possible insulation failure due to the overvoltage and spike voltage that may arise in the circuit internally or externally due to various reasons.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Cable Voltage Rating

10/15/2008 8:07 AM

<...What will be the technical conseq if I use 300V rating cable....>

If the circuit is 24VDC, absolutely none...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

Edd (1); PWSlack (1); RAJ KUMAR (1); V.I.Abraham (1)

Previous in Forum: Electronic switch   Next in Forum: Diff. Pressure Transmitter
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement