Cable Selection

10/13/2008 8:09 AM

Dear sir,

In our proposed plant 230kv/11 kv substation will be located nearer to the gate as per the local electricity board rules and regulations.But the equipments loads and panel rooms are located in the centre of the plant ie 500 metres from the switch yard.

We will using 230kv/11kv 50MVA transformer - 4nos .The out put voltage11 kv to be transmitted to the panel room for distribution at a distance of 500 metres from yard.

The total no.of transformers of capacity 3600 KVA - 25 nos to be connected to the one 60MVA transformer.For this we planned to use 3150A,40KA VCB as a incomer ( group controlled VCB ) for one transformer.To withstand 3150A current rating , how many number of cables to be laid from swich yard 50MVA 230kv/11 kv power transformer to Group control VCB.Cables to be laid exposed to air, ambient temperature 35 deg c,cable to be used is 11kv/xlpe cable.pl explain in details.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Cable Selection

10/13/2008 10:53 AM

........and what warranty does an installation of this size have in the event of an anonymous user of CR4 making a mistake?

The correct way to address this task is to consult a qualified person locally to carry out the calculations.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Cable Selection

10/13/2008 4:43 PM

Your question is a little difficult to understand. It sounds like you are saying the following:

1. You have 4 - 50 mva 11 kv transformes feeding your plant

2. There are 25 - 3600 kva transformers connected to a 60 mva substation.

3. You are looking for the cable size for 3150 amps

I am totally confused oner the 60 mva and 50 mva. Can you please be more clear as to how this will be done.

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#3

Re: Cable Selection

10/13/2008 5:30 PM

Hi Friend,

Design of such large substations are the job of competent licenced Electrical Engineer and a matter of safety and normally needs the approval from the electrical supplying agency. How ever I can provide general guidance for selection of cable. you will have to make your own calculations depending on the data available at site.

1. Short circuit rating

It will depend on its size ,insulation,initial temperature,finial permissible rise of temperature of the cable ( The data will normally be provided by the cable manufacturer)It will also depend on the type of cable PILC/PVC/ XLPE , Earthed or un earthed system etc. Duration of short circuit depending on the protective system and back up protection which are other important point to be considered.

2.. Voltage drop

You must check the likely voltage drop for which standard chart is available which should be referred.

3. Power loss.

The power transmission loss in cable should be calculated as per the data provided by the the cable manufacturer.

4. Type of cable laying / depth of cable laying soil conditions etc. and other de rating factors to be considered for the calculation.

Register to Reply
Anonymous Poster
#4

Re: Cable Selection

10/15/2008 12:16 AM

please let me knoe ampere load u required to feed for your proposed plant. then after cables has to be selected.

Register to Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#5

Re: Cable Selection

10/16/2008 11:31 AM

When you are bidding on a contract, you should have an intimate knowledge of both the code and the prices of standard size cable and equipment. Because anything that ever goes wrong always goes wrong when you try to save a few dollars! You MUST follow the code book, it exists for only one reason and that is safety.

That being said, the electrical code book will only tell you minimum size. Since "normally" smaller sizes of wire are cheaper, this is useful if you are bidding on a job. However, a few things can mess up the best inended calculations. You should have a good knowledge of what cable sizes are readily available, and their prices. You never know...sometimes a larger cable than necessary according to calculations is cheaper and more readily available because it is a standard size. Same goes for electrical boxes. The only reason why a larger cable might not be suitable is if you are dragging it through a conduit. But if you are laying it on a tray in the open, that helps. Your engineering firm may have in-house standards that are even higher than the minimums laid down in the code book. You should check. Don't let yourself be rushed.

__________________
If it was easy anybody could do it.
Register to Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#6

Re: Cable Selection

10/21/2008 1:39 AM

first, you must calculate the Full Load Current (FLC).

in this case 60MVA, FLC = 60MVA/√3*11kV = 3149.1832A≈3150 A

second, you may find in the catalog, how many cables size wiil be used.

for example : if you see cable 1 core, 500 mm2, having Current Carrying Capacity 650A (direct burried), its mean you need 5 cables to service your 3150 A load.(5x650 =3250A).R needs 5 cables,S needs 5 cables,T need 5 cables.

third,you can calculate voltage drop by :

Vd = I.R.cosΦ + I.XL.sinΦ

Vd 3ph = √3(I.R.cosΦ + I.XL.sinΦ)

R & XL can be found in vendor catalogue(dont forget to multiply with lenght cable will you lay). if you find, Vdrop still not reach your specification(ex:Vdrop=2%), may be you need to add cable become 6 cables.

R = 6 cables, S= 6 cables, T = 6 Cables

thank you...maybe helpfull

Register to Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#7
In reply to #6

Re: Cable Selection

10/21/2008 4:41 AM

first, you must calculate the Full Load Current (FLC).

in this case 60MVA, FLC = 60MVA/√3*11kV = 3149.1832A≈3150 A

second, you may find in the catalog, how many cables size wiil be used.

for example : if you see cable 1 core, 500 mm2, having Current Carrying Capacity 650A (direct burried), its mean you need 5 cables to service your 3150 A load.(5x650 =3250A).R needs 5 cables,S needs 5 cables,T need 5 cables.

third,you can calculate voltage drop by :

============================================================

value of R & XL can be found in vendor catalogue.

let say, R = 0.0241 Ω/km , reactance = XL = 0.052 Ω/km

if our cable length is 500 m ,so that R = 0.0241 Ω/km * 0.5 km,

XL = 0.052 Ω/km * 0.5 km.

if we use 5 cables : R = 1/5*(0.0241 Ω/km * 0.5 km)

XL =1/5*(0.052 Ω/km * 0.5 km)

============================================================

Vd = I.R.cosΦ + I.XL.sinΦ

Vd 3ph = √3(I.R.cosΦ + I.XL.sinΦ)

R & XL can be found in vendor catalogue(dont forget to multiply with lenght cable will you lay). if you find, Vdrop still not reach your specification(ex:Vdrop=2%), may be you need to add cable become 6 cables.

R = 6 cables, S= 6 cables, T = 6 Cables

thank you...maybe helpfull

Register to Reply
Anonymous Poster
#8
In reply to #7

Re: Cable Selection

11/22/2008 12:15 AM

really a good answer.

i have some query regarding same question. me going to install a mcc having rating oof 1000 a bus, 40ka sc rating. our consultant has considerd incoming cable of 6 nos. 3.5c x 400 sqmm cables. as the 400 mmsq al cable as current carrying capacity of 375 a in air and load to be feed of 1000 a. please gouding regarding selection of 6 nos. 400 sq mm cables for this mcc of 1000 a.

Register to Reply Off Topic (Score 5)
Anonymous Poster
#9

Re: Cable Selection

09/29/2010 3:31 AM

Download from Excel base calculation sheet from

www.ziddu.com/download/9669204/CableDesign.xls.html