Anonymous Poster

trippnig of one generator operating in parallel

10/13/2008 3:17 PM

what happen if two generators operating in parallel sharing equal load having same rating ,one of the GTG( gas turbine genrators )trips?.what is the effect on frequency ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: trippnig of one generator operating in parallel

10/13/2008 5:59 PM

Hello Guest,

Nobody is presently able to tell you the answer, because you fail to supply several essential details of the installation.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Anonymous Poster
#5
In reply to #1

Re: trippnig of one generator operating in parallel

10/15/2008 3:10 AM

ok

the GTG are 25 MW rated,11 kv,50hz

total load is 20MW

suddenly one gtg trips.

how thw frequency of the running GTG will vary with sudden load,

any relation with frquency and load ?

Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#6
In reply to #5

Re: trippnig of one generator operating in parallel

10/16/2008 12:43 AM

Hello again, Guest,

You have not yet advised the rotating mass, nor the rotor speed in RPM.

The brand of the unit would also be helpful, along with the nameplate details.

The reason for the brand/nameplate requirement should be obvious to you.

If those are advised, then your chances of a proper answer markedly increase, as I'm sure you must realize, if you are involved with such generation equipment.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#2

Re: trippnig of one generator operating in parallel

10/13/2008 8:24 PM

There are number of different things that can happen, and things to consider. Are the two units part of a larger system, are they on full load, and how far away from the load are they and the type of load, capacitive or reactive, is there any spinning reserve and how long for it to come on line. There are two immediate problems, over load and excessive voltage generated by the capacitive effect of the transmission lines, either could lead to the lost of the other unit. So as you may now appreciate, more information is needed.

Regards JD.

Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#4
In reply to #2

Re: trippnig of one generator operating in parallel

10/14/2008 7:50 PM

PS.

Looking for the simple answer, and here we are assuming that the other unit is not subject to all the other possibilities, yes the frequency will drop. The reason being that when the other unit takes the load, the governer will act to system frequency, and part of the govenor control is the droop unit. This is different from the govenor set point, which one might think would return the system back to it's previous frequency? The droop is set at about 3 1/2 percent of operating speed, 105 rev's for a 3000 RPM system, it's this drop in rev's that causes the govenors to open. So I suggest you Google some info on that.

Regards JD.

Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#3

Re: tripping of one generator operating in parallel

10/14/2008 8:55 AM

If the generators are more than 50% loaded and one trips, the entire load will be placed on the other generator and it will be overloaded. Then it becomes a matter of a critical race between the circuit protection device and the energy source driving the generator as to what will happen. If the circuit protection device opens, the generator will suddenly be released.

What happens when your car tire hits a patch of ice?

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Reply