Neutral Current from 3-phase, 4-wire line connection

10/17/2008 9:33 AM

Are there restrictions in Europe for a 3-phase, 4-wire line connection for current drawn from the Neutral line?

Register to Reply
Pathfinder Tags: LINE NEUTRAL CURRENT
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#1

Re: Neutral Current from 3-phase, 4-wire line connection

10/17/2008 11:29 AM

lightningrod; i would say for the maximum un balanced current & insulation for maximum voltage rating. perry

Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#2

Re: Neutral Current from 3-phase, 4-wire line connection

10/17/2008 11:08 PM

The neutral should be capable of handling all single phase connections on a 3 phase system.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#6
In reply to #2

Re: Neutral Current from 3-phase, 4-wire line connection

10/18/2008 3:16 PM

garth; if the load is equal in all single phase loads there is very little or no neutral current

andy is right, double the neutral size, less heat from 3rd harmonics perry

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#3

Re: Neutral Current from 3-phase, 4-wire line connection

10/18/2008 2:40 AM

I have (at the recommendation of my electrician) in the past doubled up on the neutral cable to prevent volt drops etc. up to the maximum allowed current for the circuit in use. This has worked well for me and I am not seeing any surges/drops when switching on and off any loads on those lines.....

Of course the fusing/circuit breakers will set the maximum allowed load current, and should not be higher than is correct for the circuit in question.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Anonymous Poster
#4
In reply to #3

Re: Neutral Current from 3-phase, 4-wire line connection

10/18/2008 9:13 AM

You are right the good practice is calculate short circuit currents and fault currents and size the neutral conductor in a three phase circuit i have seen 10 out 10 times it works out double the main conductors size still some countries the disgeners assume neutral conductor size as half the main conductors size and land every body in trouble

i am just sharing my experience

Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#5
In reply to #3

Re: Neutral Current from 3-phase, 4-wire line connection

10/18/2008 10:00 AM

Very prudent Andy, with all the switch mode power supplies , inverters and fluorescent lighting excessive current can flow in the neutral due to harmonics which add to the normal single phase current in the neutral .

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Member

Join Date: Aug 2007
Posts: 9
#7

Re: Neutral Current from 3-phase, 4-wire line connection

10/21/2008 3:33 PM

Some three-phase loads have a half-wave rectifier on each of the three phases. The net DC current is then routed through the neutral line. In other words even with a balanced line load there will be a very large DC current.

I know that some locations have restrictions on drawing currents from the neutral line.

Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#8
In reply to #7

Re: Neutral Current from 3-phase, 4-wire line connection

01/29/2009 5:43 PM

lightningrod; generally there are 6 devices, i guess i could see a use for half wave, the peak voltage would be 120 degrees apart. we built a 5 phase generator with 10 diodes that worked out good. perry