Previous in Forum: PLC Test Panel Advice   Next in Forum: Effect of Voltage Leakage
Cable testing
10/22/2008 12:47 PM
After completing the testing(Insulation Resistance) on power cable (On Drum),is it required to be discharged?if so,what's the correct procedure?
Re: Cable testing
10/23/2008 1:17 AM
just touch the wire to earth wire bonding
cheer
Engineering Fields - Power Engineering - Projects Engineer
Re: Cable testing
10/23/2008 2:46 AM
Depends on the quantity of cable in drum ,50 to 60 meters will hold charge for negligible time.
otherwise momentarily ground the ends.if neccessary.
when i was in cable production industry we never bothered to do that(even for 500 M cable drum) as by the time we transfer the cable to dispatch no charge was left.
A wise person will understand more from a Foolish question than what a Fool will understand from a Wise Answer
Re: Cable testing
10/23/2008 3:03 AM
Yes. Just short it to earth, just in case.
Re: Cable testing
10/23/2008 9:41 AM
thank you.
Do i have to connect 2 ends of each core to earth or only single end is enough to touch earth?
Re: Cable testing
10/25/2008 4:56 AM
Re: Cable testing
10/25/2008 5:06 AM
Re: Cable testing
10/27/2008 12:29 PM
thank you very much...