Maximum Demand

10/30/2008 6:23 AM

During commissioning of my plant, way back in 2001, we had declared 70,000 kW/ month as our maximum demand to our utility supplier. I'm not sure how they come out with that 70000 figure. Anyway, as the electricity price is already increasing, i am required to look on how to reduce cost on this area. I just join in this company 2 years ago.

Basically, as for historical data, our maximum ever usage per month is around 49000 kW. On average, it is 46000kW / month. Which mean, we still have access more than 20000 kW extra every month, that we need to pay as maximum demand charge.

Based on these data, i plan to propose reducing the declared maximum demand per month from 70000 to either 65000 or 60000 or 55000 kW.

My question is, from our 49000 kW taken from our maximum usage historical value, what is the recommended % value in order to set our maximum demand? I mean, 10% or 20% or any value higher than maximum ever usage?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Maximum demand

10/30/2008 8:06 AM

Stats isn't my best subject, but you need to look at:

  • What is the distribution of usage - does it vary widely from month to month, or stay near the average with occasional excursions?
  • What factors affect your usage, and are these likely to vary in future?
  • What are the consequences of exceeding your declared maximum demand?

Just a few thoughts...

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Member

Join Date: Oct 2008
Posts: 7
#6
In reply to #1

Re: Maximum demand

11/02/2008 1:31 AM

JohnDG:

1. The usage is is not vary too much. The value is at around 44000 kW to 46500 kW. Basically, it will not exceed it during our normal operation. Except, if we have a plant turnaround/shutdown, the power intake will be much much lower.

2. Our plant operation. But as per last August and September, we are running at full swing, and the value is 46,483.0 kW & 45,218.00 kW respectively. Our higher consumption was 48,279.00 kW, which is way back on May 2004.

3. There are some penalty if we exceed 70,000 kW (our maximum declared demand).

Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#2

Re: Maximum Demand

10/30/2008 11:08 PM

Demand is a measured thing and your electric meter will have a demand pointer that goes up as you place a load on your service, but it does not go down.

The electricity company charges a demand fee based on that peak. The meter also counts all the kilovoltamps you use in a month and they charge you for that.

So what makes your demand go high?

The answer is the large load of startup of large machines, after which they fall back to a lower value.

The solution to this lies in several methods.

1 phased startup. Do not start all machines at once, start them slowly over one hour, even if you must hire someone to come in early, the demand saving may offset the wage costs.

2 Smart electronic starters for large motors that start with a low voltage ramp instead of a huge current inrush.

3 machine scheduling with shifts etc. See if you can avoid operating all the large machines at the same time. That might lead to a rule that machine "A" is never run while machine "B" is also running.

4 replace one large machine with several small machines that are brough into operation as production demand increases.

Now some of these things may not be practical, but some will.

There are "demand consultants" who earn a living from coming to places like yours and doing a demand audit. Once they leave you pay them and the savings are permanent as long as you follow their rules of demand useage.

__________________
Per Ardua Ad Astra
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#3

Re: Maximum Demand

10/31/2008 8:53 AM

I'm a little confused . . . When you say, " . . . our maximum ever usage per month is around 49,000 kW," do you mean 49,000 kWh?

What is the maximum instantaneous demand? It may average 49,000/(30 X 24) kW, but that will not necessarily be anywhere near the peak load during any one hour. Whatever the peak load is is what you need from the power company.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Anonymous Poster
#4

Re: Maximum Demand

10/31/2008 11:55 AM

Your maximum usage appears to be monthly demands, not hourly. 49000 is your monthly averaged peak demand, what is your actually short-term peak demand? What is the highest peak hour you have used? your electrical engineers that designed the facility should have calculated the peak demands based on the equipment and proposed operations. You should be able to get the peaking factor from your electrical design engineer and see how you current average demand compares to that estimated by the EE , use the peaking factor to estimate peak demands.

Register to Reply
Anonymous Poster
#5

Re: Maximum Demand

10/31/2008 12:41 PM

I spent over 30 years with one of the largest electric utilities in the US and here are my thoughts on your question. First 70,000 kW is a very large load. Second, if your peak demand has historically been 49,000 kW there is really no reason to contract for any larger demand. You should set your contract capacity as close to your actual needs as possible. Rates and terms of service are different in every state, even for a utility that serves many states, because retail rates are governed by the state utility commisions. In my state, for my company, the peak demand period was 15 minutes and you got billed for your highest 15 minute peak, subject to a minimum of 60% of your contract capacity, or 60% of your highest previous demand during the last 11 months. Contracting for 70,000 kW would simply set your minimum demand at 42,000 kW, but would not cause you to be billed for 70,000 kW. Contracting for 70,000 kW will not give you any assurance that the utility will supply you with 70,000 kW of capacity. Perhaps they would initially install a substation large enough for that kind of load, but if other growth in the area uses up transmission or generation capacity, you can only get what they can supply. Lastly, the comment someone else made about start up is not correct and is one of the most common misconceptions. Inrush current for motor startup lasts only a matter of seconds and the demand period is 15 minutes. Staggering start up for motors does not lower your demand. The only time start up really has an affect is if your are starting thermostatically controlled loads, such as melting furnaces or heat treating where the start up time is long. If that is the case, wait until one is up to temperature before starting any thing else.

Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#7
In reply to #5

Re: Maximum Demand

11/02/2008 1:53 AM

this is strange. A place where I worked had 60 3 roll ink mills that took close to a minute to get up to speed and they had no clutch. They varied from 2 HP to 20 HP, 5550 VAC 3 phase, and we had a start up procedure staggered over more than an hour to reduce Demand peak.

__________________
Per Ardua Ad Astra
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#8
In reply to #7

Re: Maximum Demand

11/02/2008 10:41 AM

That would make for about one a minute. Not to bad. Another reason for the start up of the mills being staggered, could be how "stiff" the supply from the utility was. What was the HP demand of the mills upon start up, 2 or 20 HP?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#9
In reply to #8

Re: Maximum Demand

11/02/2008 11:57 AM

550 volts AC 3 phase, no phase correctors, so there might have been phase angle penalties as well.

This was in 1960 =summer student, so I am not up on these details. It was an old factory, now converted to lofts.

I expect the supply was not that stiff, so that could have been a reason for the slow startup. I recall I was told it was to keep the demand low.

__________________
Per Ardua Ad Astra
Register to Reply
Member

Join Date: Oct 2008
Posts: 7
#10

Re: Maximum Demand

11/03/2008 1:03 AM

The demand period is 24hrs. Every month, the utility company will gives us the daily demand (together with the invoice) and the 49000 kW is the maximum ever usage in a single day since 2002.

Register to Reply
Register to Reply 10 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); aurizon (3); Bill (1); JohnDG (1); North of 60 (1); pisemude (2)