Earth Resistance - Limits!

11/02/2008 11:28 PM

Hi,'

In what range that the resistance of earth/ground wire will fall??

Hari

__________________
[Information is knowledge]
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Aug 2008
Location: East
Posts: 117
Good Answers: 6
#1

Re: Earth Resistance - Limits!

11/02/2008 11:37 PM

Hari

Hey cool guy, please elaborate your question.

In present form it makes no sense.

__________________
Atlas Shrugged - JGD
Register to Reply
Commentator

Join Date: Oct 2008
Location: India
Posts: 76
#2
In reply to #1

Re: Earth Resistance - Limits!

11/03/2008 1:16 AM

Hi current,

We are measuring the earth resistance & that seems to fall under the range of 1~ 3 ohm. We don't know whether it is a good earth to relieve from shock, hazardous ,etc.,

Is there any standard that define the good earth connection must have a resistance of this much ohm?????

Now I hope, that you got my point.

Hari

__________________
[Information is knowledge]
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Oct 2008
Location: Cairns, Qld, Australia
Posts: 968
Good Answers: 65
#3
In reply to #2

Re: Earth Resistance - Limits!

11/03/2008 1:38 AM

Is your supply multiply earthed neutral?

If not, the earth resistance must be low enough to reliably trip your protective devices (circuit breakers, fuses, earth leakage relay etc)'

I once installed a system for a house where earth resistance was 50 ohms! The supply authority said this was normal in the dry sandstone country of the installation.

The system only worked because the MEN effectively had a large number of similar resistances in parallel, giving an overall resistance low enough to be usable.

If you are solely dependent on the local earth then 3 ohms with a 240V supply will give a fault current of 80 amps, which will probably work although fuses may be a little slow to blow and if well cooled may not do so at all. 1 ohm would allow operation in most cases.

If your protection devices need higher current than the normal 15 - 20 amps of house circuits, you may need a better earth.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Earth Resistance - Limits!

11/03/2008 5:04 AM

There is a good article in Wikipedia on earthing.

One of the ways of solving in principle the high earth resistance situation is to install a whole-house residual current device [RCD]. 100mA imbalance between live and neutral is a typical trip point for a house with a modern TT installation in the UK.

The fuses/breakers/whatever then protect the circuit conductors, and the RCD protects against high earth resistance.

Of course, there is great advantage to be had from lowering the earth resistance.

In all cases, comply with local wiring regulations.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Oct 2008
Location: India
Posts: 76
#5
In reply to #4

Re: Earth Resistance - Limits!

11/03/2008 5:13 AM

Hi Friends,

FYI ::: I'm asking this for industry & not for home.

Hari

__________________
[Information is knowledge]
Register to Reply
Associate

Join Date: Aug 2007
Location: New Delhi, India
Posts: 33
#8
In reply to #5

Re: Earth Resistance - Limits!

11/04/2008 1:53 AM

Hi Hari,

There are various recommended values of earth resistance. It depends on the type of usage.

1. If you require is for a sub-station it should be below 0.5 ohms.

2. For panels, UPS, distribution electrical system earth resistance should fall under 3 ohms.

3. Machines and body earth should fall below 5 ohms.

If the earth resistance value is high, there are various measures to drop its value.

As far as my understanding you are not using it for any sub-station. Thus. 1-3 Ohms is OK.

ashish

__________________
Ashish Gupta
Register to Reply
Anonymous Poster
#16
In reply to #8

Re: Earth Resistance - Limits!

12/18/2008 8:32 AM

how can i get 0.5 homes for sub station

Register to Reply
Power-User

Join Date: Aug 2008
Location: East
Posts: 117
Good Answers: 6
#10
In reply to #2

Re: Earth Resistance - Limits!

11/04/2008 2:53 AM

Hi Cool Guy

For industrial plants the following naximum earth resistance values are recommended:

For electrical equipment : 1 ohm for large generating stations and large substations

For electrical equipment : 5 ohms

For static discharge : 1 megaohms

For lightning discharge : 10 ohms

Please note that the objective from the point of view of safety consideration is not only to obtain a minimum value but to also keep in mind that there is adequate co-ordination between the value obtained and the setting of the protection relays/ devices.

__________________
Atlas Shrugged - JGD
Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#19
In reply to #10

Re: Earth Resistance - Limits!

12/25/2018 8:20 AM

For Overhead power lines pylons?

__________________
Either exist as you are or be as you look. Rumi
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Oct 2008
Location: Cairns, Qld, Australia
Posts: 968
Good Answers: 65
#6

Re: Earth Resistance - Limits!

11/03/2008 8:26 AM

My ancient copy of the SAA wiring rules (Australia) states that an earthing system's resistance should be no greater than (Voltage to earth)/(5x current rating of largest fuse). Obviously "fuse" should be also taken to include "circuit breaker".

The standard I used is ancient, but the rule given is probably still relevant.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#7

Re: Earth Resistance - Limits!

11/03/2008 6:09 PM

Haricool

1 -3 ohms is a very low earth resistance. What method are you using to measure it?

Register to Reply
Commentator

Join Date: Oct 2008
Location: India
Posts: 76
#13
In reply to #7

Re: Earth Resistance - Limits!

11/04/2008 10:42 PM

Hi Wareagle,

We measure the earth resistance using earth tester by following mode:

Normally ,three earth wire(covering a area of around 10 Sq.ft) are connected with the meter. And "Resistance of the earth" to be measured is connected to the earth terminal in the meter .

Hari

__________________
[Information is knowledge]
Register to Reply
Commentator

Join Date: Aug 2011
Posts: 76
#18
In reply to #7

Re: Earth Resistance - Limits!

08/24/2011 1:56 AM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Register to Reply Off Topic (Score 5)
Anonymous Poster
#9

Re: Earth Resistance - Limits!

11/04/2008 2:36 AM

Hello Hari,

Your measurement of 1 till 3 ohms looks good I've to agree with ashuashi. But Wareagle makes also a good point. How was it measured. And more-over what is the soil-resistivity and how is that measured as well? For further reading I would like to refer to IEEE 80-2000, IEEE 142-1991 and BS 7430:1998. In these literature you can find solutions.

Regards,

Robert

Register to Reply
Anonymous Poster
#11

Re: Earth Resistance - Limits!

11/04/2008 8:44 AM

You will find that if there is 5 ohms resistance to ground-you have a problem.

Michael Leiwig

Oil States Industries

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#12
In reply to #11

Re: Earth Resistance - Limits!

11/04/2008 11:02 AM

Michael

Why does a 5 ohm resistance cause a problem? IN what type of enviornment? Please explain.

Register to Reply
Associate

Join Date: Aug 2007
Location: New Delhi, India
Posts: 33
#14
In reply to #12

Re: Earth Resistance - Limits!

11/05/2008 7:27 AM

We do earthing to provide lowest resistive path to the fault current. If the earth resistance is high ~ 5 ohms or more & fault current receives path less than 5 ohms will travel to it and might cause serious issues.

regards,

Ashish

__________________
Ashish Gupta
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#15
In reply to #14

Re: Earth Resistance - Limits!

11/05/2008 11:37 AM

ashuashi

When you use the term "earthing" are you referring to bonding with a conductor or using EARTH itself as the fault clearing path? In the USA earth is never used as a fault current path. Equipment bonding conductors are installed for this purpose.

Register to Reply
Anonymous Poster
#17

Re: Earth Resistance - Limits!

04/23/2009 2:36 AM

ZERO TO CUSTOMER REQUIREMENT

REGARDS

THIRD PARTY