Earthing

11/04/2008 3:06 AM

Hi I recently went to have a look at a bulk fuel depot (Petrol, Diesel etc). When they are filling the road tankers they connect an earth to the tanker to get rid of any static that may be present. Now they say to me that if the earth is not connected to the tanker then the pumps wont start. My question is How ? If its a true earth then there cant be any voltage or current flowing in the cable, so how does the starter know its connected ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Earthing

11/04/2008 5:56 AM

Generally, earthing is done to get rid of static electricity (& lightning) that may spark & cause fire. Now coming to pump, if it is an externally mounted pump, what they say is not true. If the pump is connected to battery source of the truck, then it may or may not require the ground based on surrounding conditions.

Register to Reply
Commentator

Join Date: Nov 2008
Location: S.E. Asia
Posts: 91
Good Answers: 1
#2

Re: Earthing

11/04/2008 7:08 AM

Take a look at the below website. It is very self explanatory.

http://www.staticelectricity.com.au/index_NewsonGale.php

__________________
"If you try to keep a leg each side of a barbed-wire fence, you'll do yourself a mischief." - Joh Bjelke-Petersen.
Register to Reply
Active Contributor

Join Date: Jul 2008
Location: Malawi
Posts: 20
#4
In reply to #2

Re: Earthing

11/04/2008 8:58 AM

Thanks Guys

http://www.staticelectricity.com.au/index_NewsonGale.php

That website answered all the questions.

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#3

Re: Earthing

11/04/2008 8:25 AM

When any vehicle is in motion it generate static charge. This charge if not properly earthed can cause electrical spark. The spark can cause fire if it happens while the petrol/diesel is pumped . To avoid any fire hazard the truck is earthed first before the pump is started.The operation of the relay for the pump motor is interlocked with the earth connection of the truck to avoid manual error of not connecting the earth as a safety precaution.

Register to Reply
Guru

Join Date: Sep 2007
Location: Wrong end of the yellow brick road in Oz
Posts: 930
Good Answers: 15
#5
In reply to #3

Re: Earthing

11/05/2008 12:10 AM

A Spark can cause a fire any time there is fuel vapour available in the area where the spark (ignition point) is located, this could also be in the hoses and/or the fittings that are being used to transfer the fuel.

Remember, Fuel (liquad) will not burn, but the gasses of the fuel is what burns (explodes when in the wrong conditions)

__________________
Qn, Whats the differance between a Snake and a Onion? Ans, No one cries when you chop up a Snake
Register to Reply
Associate

Join Date: Oct 2008
Posts: 39
Good Answers: 1
#6

Re: Earthing

11/06/2008 12:36 AM

My friend,

Many fuel depots' electrical designs include primarilly the grounding system (earthing) of all exposed steel structures and one of them is the motor pump aside from area classification requirements.

It is normal to all fuel depot that wasted fuel flowing from the tankers, spill over and leaks are accummulated to the ground or flooring of the fuel depot. In usual way, this should clean once in a while, but if the depot does not have good maintenance and house keeping, it will happened just what you have seen.

Don't you worry about the static current that might be a source of disastrous incident (fire and explosion). It will not be happened since all steel structures are fully grounded, it is matter of maintenance (again). Retighten all grounding systems' connections exposed to untidy unloading terminal.

"The tanker should be grounded (clamps) from fuel depot grounding system before tapping or filling the tanker."

In some instances, the fuel depot is design that the above grounding to tanker gives signal (permissive) to start the filling pump, which grounding sensor (w/ relay contacts; NO and NC) connected to motor pump controller(s).

Eren

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#7

Re: Earthing

11/06/2008 8:20 PM

The major source of the static charge in fuel transfer systems that is bled off by bonding the various portions of the delivery system (tank - piping - pump - hose - receiving vehicle) to each other, is not caused, as has been suggested, by the motion of the vehicle through air prior to the filling process. The actual source of the static potential is the flow of hydrocarbons through the various portions of the actual delivery system.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Register to Reply 7 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Borrowdale Dan (1); elkangorito (1); ereneduarte (1); North of 60 (1); Snaketails (1); V.I.Abraham (1)

Previous in Forum: creeping voltage   Next in Forum: Equipment rating

Advertisement