Synchronous Motors versus Induction Motor

11/04/2008 12:37 PM

TO All....

The scenario is this...we are working on a water pumping station upgrade (located in Maryland, USA) that is currently fitted with four 1,500 hp, 900rpm, 2,400 Volt synchronous motors. Would there be, from an electrical perspective some virtue in encouraging the process engineers to replace these motors in-kind or at least with new synchronous motors as opposed to induction motors?

Unfortunately, that is all the info I have on the issue/question.

Thanks in advance for all the help.

jjbad

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#1

Re: Synchronous Motors versus Induction Motor

11/04/2008 1:07 PM

The only advantage of an induction motor is less maintenance.

The synchronous motor will not change its speed with different loads, while the Induction motor will. This will cause slower response to load changes, and thus more pressure fluctuations.

You may find that newer synchronous motors are more efficient. You will have to do some calculations to see if it is worth the cost.

How close are the old ones to the end of their expected life expectancy? Has the maintenance cost started to escalate? Are parts starting to be hard to find?

__________________
Perfection is a subjective and abstract concept.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Synchronous Motors versus Induction Motor

11/04/2008 2:10 PM

There may also be some serious ramifications in Power Factor penalties if the Synchronous motors are removed. In many cases, Synchronous motors are used on loads that are somewhat continuous because they can be run in a leading power factor and compensate for lagging power factors from other smaller motor loads that are running throughout the day. Replacing them with Asynchronous motors will remove that capability and even if you correct the pf on the bg motors with capacitors, you may find yourself having to go through and do that with all of the others as well.

It should not be undertaken lightly.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#3

Re: Synchronous Motors versus Induction Motor

11/11/2008 2:17 AM

It may be worthwhile to to consider replacing them with AC sq.cage induction motors from the maintenance point of view.The DC system and slip rings wound rotor all these and associated maintenance will be avoided.Further induction motors are rugged and trouble free.Only thing to be taken care is the starting current and Poor factor.Pf can be improved by providing capacitors across each motor.Starting current if system cannot withstand then suitable means can be adopted.If system can withstand the starting then dol starting will make it more simple.Considering that driven equipment is a pump acceleration time and hence duration of starting is likely to be low.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JRaef (1); nesubra (1); techno (1)

Previous in Forum: Polar-Mohr Guillotine   Next in Forum: two wattmeter-Earthing
You might be interested in: AC Motors, Linear Motors, Brushless Motors

Advertisement