two wattmeter-Earthing

11/04/2008 1:07 PM

dear Engineers,

practically y phase PT is earthed before energy meter in wattmeter method.what is the need of it.

please share ur views

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: two wattmeter-Earthing

11/04/2008 8:45 PM

Hello gova1467

I realize that English appears not to be your first language.

Also note: Texting language is better left for texting messages on your cellphone.

Could you please reply, with further information and/or a clearer Question.

Reply here, with

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Anonymous Poster
#2
In reply to #1

Re: two wattmeter-Earthing

11/05/2008 2:36 AM

Dear sir

what is the input quantity required to energy meter ?

Ans:voltage from PT and current from CT considering HT service.

Then, PT secondary (any one phase) is earthed purposely leaving neutral in floating.

My question is '

1)is there any advantage to meter if any one phases of PT secondary is earthed.

2)what are the factors we have to consider for determining the rating of fuse used in PT secondary side?

thanks and regards

gova

Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#3
In reply to #2

Re: two wattmeter-Earthing

11/05/2008 8:49 AM

GOVA, the reason for earthing is always safety. In the USA every circuit lower than 300 volts is required to have one grounded leg, even in metering. This enhances the function of protective devices. You will also find that the CT secondary is referenced to earth at one point; again for safety.

What you have described is a corner grounded delta secondary, in which case the "neutral" , probably a center tap of one of the PT's, if also grounded would cause a catastrophic short circuit and so is left purposely floating.

For the fusing, the purpose is to protect either the wiring or the devices in case of a fault, which could involve the primary voltage available and should be so rated. Current value of the fuse is determined by the meter circuit to protect the meter.

May I inquire why you mentioned "two wattmeter" in your question?

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Commentator
India - Member - New Member

Join Date: Nov 2008
Location: India
Posts: 72
#4
In reply to #3

Re: two wattmeter-Earthing

11/05/2008 10:55 PM

Dear CJMcGill,

Phase earthing is done only in two wattmeter method connection.The neutral is kept floated and not connected to meter.

But in three wattemeter method,neutal earthed and connected to meter.

This is we followed in our Electricity board.

Pl share ur views.

Regards

gova

Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#5
In reply to #4

Re: two wattmeter-Earthing

11/06/2008 4:05 AM

I now recognize the terms 'two wattmeter' and 'three wattmeter' to be the equivalent of 'two element' and 'three element' meters in our terms. Additionally it is clear that the voltages available to you for metering purposes as stated are the secondary values of Potential Transformers, and the currents the metering will see are the secondary currents from Current Transformers. Both of these circuits are required to be grounded, or 'earthed', at one point only, for safety purposes.

Determination of whether to ground a phase or the neutral conductor will be dictated by the voltages and configuration (Wye or Delta) of the meter circuit. Whether to run the neutral to the meter or not is dictated by the voltages required by the meter and the form of the meter.

Since there are 45+ meter forms available, it is clear that your Electricity Board has chosen to keep the choices simple, which can be a good thing.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Commentator
India - Member - New Member

Join Date: Nov 2008
Location: India
Posts: 72
#6
In reply to #5

Re: two wattmeter-Earthing

11/06/2008 4:28 AM

dear CJMcGill

Thanks for ur immediate response.

regards

gova