CALCULATION OF PERCENTAGE IMPEDENCE

11/07/2008 1:20 AM

SIR I WANT TO FIND CALCULATION OF PERCENTAGE IMPEDENCE OF TRANSFORMER OR ANYOTHER.KINDLY SEND THE PROCEDURE

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: CALCULATION OF PERCENTAGE IMPEDENCE

11/07/2008 9:55 AM

Percentage relative to what?

Perhaps you can restate your question.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: CALCULATION OF PERCENTAGE IMPEDENCE

11/07/2008 10:57 AM

You do not calculate the % impedance of a transformer. The MFG has a procedure in which they measure the % impedance.

Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#3

Re: CALCULATION OF PERCENTAGE IMPEDENCE

11/07/2008 9:42 PM

Dear All,

To measure the % impedance of a transformer,

1 To short circuit Low voltage terminals (secondary terminals).

2 Apply voltage to the high voltage terminals (primary terminals).

3 Adjust the applied voltage so that the primary current is rated full load current of the transformer.

4. % impedance of the transformer = applied voltage / rated primary voltage.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply Score 1 for Good Answer
Commentator
India - Member - New Member

Join Date: Nov 2008
Location: India
Posts: 72
#4

Re: CALCULATION OF PERCENTAGE IMPEDENCE

11/10/2008 11:30 AM

dear sir

My Answer is as follows

% impedance is calculated by conducting short circuit test on Transformer.

1)short LV terminals r,y,b and n.

2)apply LT 3 phase volatge on primary side and note down the voltage measured using multimeter.the voltage is "V".

3)Measure the current on LV side using tong tester which is short circuited current.convert the current to the primary side using transformation ratio.It is "Isc"

3)now percentage impedance is ,

%Z = (Rated HV current/Rated HV Voltage)*(V/Isc)*100

Cheers

gova

Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Akihito Shigeno (1); gova1467 (1); NotUrOrdinaryJoe (1); wareagle (1)

Previous in Forum: Electrical Rotating Machines (Motors)   Next in Forum: Detecting Momentary Dips in Current

Advertisement