over compensation of reactive power

11/08/2008 8:57 PM

Dear sir

At very low lagging power factor,the real power and reactive power required by the load is supplied by the Tfr.Hence the load draws more current from tfr and therefore more losses,more KVA demand and poor voltage regulation.In this case power flow is from tfr to load.

To compensate lagging reactive power due to low lagging PF ,we provide capacitor bank at the load end.therefore we reduce the larger KVA demand,voltage drop,losses ect., by providing correct KVAr of capacitor bank.

But if we overcompensate the lagging reactive power,now the reactive power flow is from capacitor bank only.Now in this condition also the tfr is not overloaded i.e KVA demand not increases.

Then why the Utility company charges the penalty to consumers if we overcompensate.

pl share ur views.

regards

gova

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: over compensation of reactive power

11/08/2008 10:29 PM

Hello gova1467

It is really best not to use txt language here at please - your <"....Tfr....tfr....pl....ur...."> as misunderstandings may occur.

If you have an over-leading Power Factor (Over-compensated by too much capacitance) in your installation, that leading PF is spread through the load end of the Network.

The leading PF may result in nasty Harmonic Resonance, Switching Spikes, Overvoltage, tripping of protection relays, and other undesirable local effects for your installation, the local Supply Network, and your nearby neighbours in the Supply Network.

So Utility Company penalizes you to encourage you to correctly compensate so you are not endangering/damaging your own installation, their local network, and nearby consumers on that local network.

Please download and read the .pdf document: http://www.osti.gov/bridge/servlets/purl/654078-6lcddX/webviewable/654078.PDF

Please Download and read this 8MB .pdf document: http://www.osti.gov/bridge/servlets/purl/654078-6lcddX/webviewable/654078.PDF

Apart from that, it is foolish to overcompensate PF, as it results in energy wastage.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Good Answer (Score 2)
Commentator
India - Member - New Member

Join Date: Nov 2008
Location: India
Posts: 72
#2
In reply to #1

Re: over compensation of reactive power

11/10/2008 10:38 AM

Dear sparkstation,

Thank u very much sir.I saw ur document attached.I will refer the document and get back to u sir.

chears

gova

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#3
In reply to #2

Re: over compensation of reactive power

11/11/2008 7:39 AM
Dear Gova,

Effect of Leading pf is equally negative as of low lagging pf.

there are so many factors such as

1. Transmission line losses / Distribution losses are drastically reduced near unity pf

2. Voltage levels are improved near unity pf

3. operating stability is improved on lagging pf. with leading power factor , that is over compensated system leads to inm stability in genearting plants. ( that is why, we switch off extra capacitors while running local dg sets )

4. Over compensated system will lead to more line losses / instability in supploes / etc...

harry potter.

__________________
Exploring the Science of Electricity
Register to Reply Score 1 for Good Answer
Anonymous Poster
#4

Re: over compensation of reactive power

12/31/2009 2:09 PM

Not sure that utility company charges the penalty to consumers when overcompensation. over compensatation helps neutralize other lagging power factor loads. If we can immagine most consumers are overcompensating, which is not practicaly possible, utility company recources would be partialy occopied by reactive current, heated up by losses & has to remove generated heat.

Best Regrds

Yehya Egypt

Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); gova1467 (1); harry potter (1); Sparkstation (1)

Previous in Forum: Grounding, Earthing and Bonding   Next in Forum: Neutral - earth

Advertisement