protection failure....

11/17/2008 12:18 AM

a thundering evening our transformer failed to supply and feed loads, on investigation it is found that fuses of transformer are blown and unfortunately the fault propagated into the loads side instead of the external circuit breaker and internal equipments fuses and circuit breakers and grounding/earthiing protections. this event is repeated.....plz help me .....what should i do, not to face it ever in future....thanks .....

waheed gul

lhr...pak

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator
India - Member - New Member

Join Date: Nov 2008
Location: India
Posts: 72
#1

Re: protection failure....

11/17/2008 5:09 AM

dear waheed sir,

Please explain your system once again to understand still better.i.e transformer connections, voltage levels,protection schemes etc.

Kind regards

gova

Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#2

Re: protection failure....

11/17/2008 8:59 AM

Please check up weather you have installed Surge arrester of proper rated voltage for the system. If yes check up weather it is functioning ( If it is non functional replace it) Also ensure that earthing system for the same is proper. If not installed install it immediately to avoid similar damage due to lightening in future.