VFD Application in slip ring induction motor...

11/19/2008 2:27 AM

Dear all, In a cable manufacturing company, the wire stranding machines are operated with slip ring induction motors of capacity 50HP. it requires lot of start and stop in a cycle. At starting it takes about 70kW for a moment and when it comes to normal speed, it consumes only 10kW and the pf at this point is only 0.50. My question is whether these machine is operated with normal induction motor with VFD having less rating..please give your valuable advice.....

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: VFD Application in slip ring induction motor...

11/19/2008 3:29 AM

Hello kmshanavaz

You have not advised your Location or Country (Easily done by you in your Member Profile) - so this reply is a general one.

You do not advise the number/size of the strands.

The machinery is perhaps quite old, as these days a VFD with each squirrel cage motor would normally be used, instead of wound rotor motors, the units variable speed and synchronised for the production rate at the cable drawing plant.

So, from the figures you quote, it would be more efficient to change to squirrel-cage motors with VFD's.

If you do the changeover, and the Cable Makers can afford the extra, it would be efficient to also install an Automatic Power Factor Correction Unit to the Works.

You would need to carefully cost out the above, as the energy savings may take a couple of years or more to recover the capital cost of changing over.

Advise your progress here please.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Score 1 for Good Answer
Participant

Join Date: Nov 2008
Location: Cochin, Kerala, India
Posts: 2
#2
In reply to #1

Re: VFD Application in slip ring induction motor...

11/19/2008 5:43 AM

thank you Mr.Sparkstattion for your quick response....again i would like to know whether the VFD can withstand these high starting torque? whether the motor will run?.....

Register to Reply
Power-User

Join Date: Jan 2008
Location: Silvis, IL (Quad Cities)
Posts: 141
Good Answers: 5
#3
In reply to #2

Re: VFD Application in slip ring induction motor...

11/19/2008 6:34 AM

Yes it will run. Just make sure you get a VFD that will take the amount of current you are putting through it. Also, don't skimp on the VFD that you get. You can get rather inexpensive drives, but I would go with a heavier duty for something this critical. I would also highly recommend doing as Sparkstation suggested and going to an inverter duty squirrel cage motor.

I have put VFD's into wound rotor motor applications before by just shorting the sliprings on the motor, but it's usually for something that isn't critical to production if it breaks.

__________________
Perfection is achieved, not when there is nothing left to add, but when there is nothing else to take away
Register to Reply
Commentator

Join Date: Dec 2007
Posts: 74
#4

Re: VFD Application in slip ring induction motor...

11/20/2008 6:59 AM

Yes. a VFD can stand high starting torques assuming the rating of the VFD matches the motor. I've been using VFD for quite sometime in our extruders.

However, i think it would be an issue if you will be using it in a high rpm plastic granulator as the starting is very slow. If the granulator "ate" too much of plastic, the VFD is slow in regaining speed.

Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#5

Re: VFD Application in slip ring induction motor...

11/20/2008 10:41 AM

Be aware to select a VFD with a high starting torque.

Slipmotors usually have high starting torques, and not all VFD can control the motor to deliver the high starting torque.

Do not use VFD that are normally used for pumps or ventilation.

good luck

Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#6

Re: VFD Application in slip ring induction motor...

11/20/2008 10:43 AM

For the fundamental frequency (50 or 60 Hz according where you live ), you do not need a Power factor capacitor. The Power factor will always be 1. This is not correct for the higher harmonics...

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

kmshanavaz (1); Nelson de Leon (1); rudy.leurs (2); Shawn_V_Elect (1); Sparkstation (1)