AHU capacity

11/21/2008 11:22 PM

hi everybody!

has anybody know how to determine the required AHU cooling capacity in a room.?

I want to know what is the guidlines to design/install the air cond system in our packaging room?

thanks & regards

syachah

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#1

Re: AHU capacity

11/21/2008 11:40 PM

Hire an air conditioning Consultant or sit down with one to help you out. It's engineering and not rule of the thumb.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Active Contributor

Join Date: Nov 2008
Posts: 16
#2
In reply to #1

Re: AHU capacity

11/21/2008 11:53 PM

dear ducon

Definitely i'll discuss with them, I only need some information with you all before i go further with them.i have to source it in many ways not only depend on the consultant? am i right?how you going to discuss with other people which have better knowledge than you.

syachah

Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#3
In reply to #2

Re: AHU capacity

11/22/2008 11:46 PM

I totally agree with you but take it like this - a person going for a complex surgery requirement. Now how much knowledge does he need to talk with a Surgeon. Obvious with all his test reports(data) he trys 2-3 Surgeons and finds out about reputation from friends/ friend's friends before he decides.

Yours too, is a complex system involving engineering, so you have to go with your data of room size, amb. temperature, required temp. etc. to an HVAC Consultant to first advice you what other data more is required. You then take the missing data and he/others discusses with you on your system highlighting requirement of chiller/AHUs/ ducting etc. etc. etc.

You then try the next one & the next. Makeing your decision since now you are aware.

Now if you think you can design it - best of luck or, hire the HVAC Consultant think best. No hard feelings about this.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Active Contributor

Join Date: Nov 2008
Posts: 16
#16
In reply to #3

Re: AHU capacity

09/29/2010 10:54 PM

THanks Ducon and everybody..your comments are highly appreciated...i never hard feeling about this :)...

Register to Reply
Associate

Join Date: Oct 2019
Location: BANGALORE. INDIA
Posts: 54
Good Answers: 1
#18
In reply to #3

Re: AHU capacity

04/19/2020 5:02 AM

Mr. ducon,

You are great,

the last line in your reply which reads as " Now if you think you can design it - best of luck or, hire the HVAC Consultant think best. No hard feelings about this."

DHAYANANDHAN.S

__________________
DHAYANANDHAN.S
Register to Reply
Member

Join Date: Nov 2008
Location: Punjab
Posts: 7
#4

Re: AHU capacity

11/23/2008 1:30 AM

hi the capacity of the AHU ( air handling unit) unit is worked out in cubic feet of cubic meter.

e.g. if lenth of room is 20feet. width is 20 feet and is 12 feet high. then the

cubic capacity =20x20x12=4800 cft.

as u need AHU for packaging area. consider 1 ton capacity for 1000 cft

so the tonnage required is 5ton

__________________
Ravinder K. Bawa
Register to Reply Score 1 for Good Answer
Member

Join Date: Apr 2009
Posts: 8
#15
In reply to #4

Re: AHU capacity

10/09/2009 8:13 AM

Hi there!

May I ask if when can I apply the computation that you gave? Does it apply in genereal estimation of AHU?.

Thank you very much!

Register to Reply
Active Contributor

Join Date: Nov 2008
Posts: 16
#17
In reply to #15

Re: AHU capacity

09/29/2010 11:01 PM

egan jade

yes ,general estimation to determine the AHU cooling capacity..we need to know the room volume in order to determine the required AHU air flow design and room air change as well.

thanks,.

Register to Reply
Power-User

Join Date: Jun 2006
Location: Manila Philippines
Posts: 171
Good Answers: 8
#5

Re: AHU capacity

11/23/2008 4:20 AM

Hi Ducon and syachah,

You guys both have valid points, we're all members must help each other. maybe we just misinterpret each other. be patient. I do beleived that this is not a group of forum to criticize each other, I agree with Ducon better to hire the consultant, however syachah also want to know before dealing with the contractor or consultant to give him little idea and guide how the contractor come up with the proposal, "if you don't know you ask" not to pretend you know everything and then later found you're stupid in doing wrong things by your own. on your side syachah, you better have tell that in the beginning so we know how we supposed to help, keep calm guys

my contribution base on my knowledge.

W x L x H multiply by 50 or 60 then that the total Btu you can fit.

10' x 20' x 9' x 50 = 90,000 Btu capacity you can fit. or

10' x 20' x 9' x 60 = 108,00 Btu capacity or nearest Btu capacity available you can fit. this are the calculation I apply if i want to put air-con in the room.

reason why the multiplier is not fixed in simple reason that depending on the place of application, like packaging room need not to be same maintaining room temperature with the Hospital ICCU. consider also the room location if it is in the middle of the dessert or in the middle of building structure where heat load is not too excessive. Hope will help you to have small idea on my small knowledge in air-conditioning calculation.

Kind regards

Roman

Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#7
In reply to #5

Re: AHU capacity

11/23/2008 1:16 PM

Thanks & i agree. syachah, I' m sorry.

Thanks for teaching me too 'cause i'm a heating guy.

OK now here we get A/C Split Unit 1.5 T = 18000 Btu. & 1 T = 12000 Btu

So

90000 Btu/18000 Btu = 5 T = 3 nos A/c split units of 1.5 T+ 1 no 1 T ?

108000 Btu/18000 Btu = 6 T = 4 nos A/c split units of 1.5 T?

Is this correct ?

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Power-User

Join Date: Jun 2006
Location: Manila Philippines
Posts: 171
Good Answers: 8
#8
In reply to #7

Re: AHU capacity

11/24/2008 12:57 AM

Hi ducon, great!!! on my calculation you are 100% right, now syachah at least have an idea and deal with the contractor on the capacity required. now duco how nice you feel we both help syachah on his question. keep it up being patient and keep helping others someday somehow me too i need your input, if you can have a look on yesterday forum I posted tha "wind turbine generator" at least a lot of our member contributed and I gained from that info. well done!!!

kind regards

Roman

Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#9
In reply to #8

Re: AHU capacity

11/24/2008 1:12 AM

Thanks buddy you brightened my day

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Active Contributor

Join Date: Nov 2008
Posts: 16
#10
In reply to #5

Re: AHU capacity

11/24/2008 11:57 PM

dear ducon/roman/bawa/jcchiefeng

i just went back from my leave.Thanks for the good information, its very useful for me.ducon , sorry for that, i dont have any hard feeling on that.

ducon/roman

why you use the WXLXH (m3) to get the capacity .I have told by my consultant to use only m2 ( wxL) to get the capacity .which one is correct?. Is it correct from the room volume we can determine the required air flowrate and air change for the AHU?.

I have checked the internal heat load of the room ( lighting/human/general power/

machine heat load).for the lighting load and general power- how to determine their heat load?.is it power in KW for each equipment multiply with 860 kcal/hr.please confirm.

thanks

Register to Reply
Power-User

Join Date: Jun 2006
Location: Manila Philippines
Posts: 171
Good Answers: 8
#11
In reply to #10

Re: AHU capacity

11/25/2008 4:06 AM

Hi Syachah,

He was also right due to different aprroach in calculation base on the below;

Heat Load - the amount of heat generated is know as the heat load. Heat is measured in either British Thermal Units (BTU) or Killowatts (kW). 1 kW is equivalent to 3412BTUs.

The heat load depends on a number of factors, by taking into account those that apply in your circumtances and adding them together a reasonably accurate measure of of the total heat can be calculated.

Factors include:

The floor area of the room

The size and position of the window

The number of room occupants (if any)

The heat generated by equipment

The heat generated by lighting

Floor area

The amount of cooling required depends on the area of the room. to calculate the are in square meter

To get Room Area BTU = Length (m) x Width (m) x 337

Window Size and Position

If your room has no window then you can ignore this part of calculation, how ever as rule of thumb there are window you need to take and orientation into account.

South window BTU = south facing window Lenght (m) x Width (m) x 870

North window BTU= North facing window Lenght (m) x Width x 165

If there no blinds on the window multiply the results by 1.5

Add together all the BTUs for the window

Window(s) BTU = South window(s) BTU + North window (s) BTU

Occupants

You will have to take into account people who normally working in the space. the heat output is around 400 BTU per person.

Total Occupants BTU = Niumber of Accupants x 400

Equipment

Clearly most heat in the roo is generated by the equipment. this is trickier to calculate that you might think. the wattage on equipment is the maximum power consumption rating, the actual power consumed may be less. However it is probably safer to overestimate the wattage than underestimate it.

Equipment BTU = total wattage for all equipment x 3.5

Lighting

Take the total wattage of the lighting and multiply by 4.25

Lighting BTU = Total wattage for all lighting x 4.25

Syachah, hope that the above information will help you on your project.

Take note:

If your monthly energy bills cost you more than $75,000 a month should need my services in making it 15% to 30% lower with zero investment from your side send me your email add and will send you proposal I am starting a new business of Energy Management services. Remember ZERO investment from your company just let me manage your energy without adversely affecting your production or operation.

Kind regards

Roman

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2008
Posts: 16
#12
In reply to #11

Re: AHU capacity

11/25/2008 5:04 AM

Dear Roman

Very good information! thanks a alot.Now , i have confident to further my discussion with my consultant.anyway what is ur email add? i could't find it in this page.

thanks & regards

syachah

Register to Reply
Power-User

Join Date: Jun 2006
Location: Manila Philippines
Posts: 171
Good Answers: 8
#13
In reply to #12

Re: AHU capacity

11/25/2008 7:52 AM

Hi syachah,

you can email me here: ceo@megaenercon.com

Register to Reply
Anonymous Poster
#14
In reply to #10

Re: AHU capacity

11/26/2008 12:13 AM

u r right bro, plz think a little , u want to cool ur room , that means the air in that room have to be cooled and the air is in cubic meter of cubic feet ,,u consider length and width of the room ...

what about hight of the room ,,,,consider two rooms both have same width and length 20 ft by 20 ft. now if one room is 14 feet high and other is 10 feet. than according to ur consultant the capacity of air handing unit will be same . but according to the law one room have capacity=20x20x15= 6000cft. that means 6 ton and the other will have 20x20x10=4000 means 4 ton

consider it

Register to Reply
Power-User
United States - Member - US Citizen - Born & Raised Engineering Fields - Control Engineering - HVAC/R Simplified Using PLC Controls Engineering Fields - Instrumentation Engineering - HVAC/R Simplified Using PLC Controls Engineering Fields - Energy Engineering - HVAC/R Simplified Using PLC Controls

Join Date: Mar 2007
Location: Brick, NJ (USA)
Posts: 110
Good Answers: 5
#6

Re: AHU capacity

11/23/2008 9:31 AM

Please read below. This is how complicated the engineering of a system becomes when the need to conform to local, district or national codes. I prefer to design according to ASHRAE requirements and then "tweak" as per local building requirements or owner specification. Research the books or documents for content. This is NOT an advertisement to buy these products!

Please forgive the long text, but it seems this thread needed to cover all bases for the original request.

**************************************************

Engineers know all about ASHRAE's involvement with the U.S. Green

Building Council LEED program. But in an effort to assist architects,

program managers, building owners, and others in the use of LEED,

ASHRAE has put together a new package that includes three ASHRAE

standards frequently used in conjunction with LEED v.2.2. In addition,

we include the Standard 62.1 and Standard 90.1 User's Manuals, as well

as three books from the popular ASHRAE Advanced Energy Design

Guide series, making a powerful set of tools for use with LEED.

All of the following publications are referenced in LEED v2.2 and are

available for purchase in this convenient package:

ANSI/ASHRAE/IESNA Standard 90.1-2004, • Energy Standard for

Buildings Except Low-Rise Residential Buildings

(I-P edition)

• 90.1-2004 User's Manual

• ANSI/ASHRAE Standard 62.1-2004,

Ventilation for Acceptable Indoor Air Quality

• 62.1-2004 User's Manual

• ANSI/ASHRAE Standard 55-2004,

Thermal Environmental Conditions for Human Occupancy

• Advanced Energy Design Guide for Small Office Buildings

• Advanced Energy Design Guide for Small Retail Buildings

• Advanced Energy Design Guide for K–12 School Buildings

• Procedures for Commercial Building Energy Audits

ANSI/ASHRAE/IESNA

Standard 90.1-2004

The purpose of this standard is

to provide minimum

requirements for the energy-efficient

design of buildings except

low-rise residential buildings.

This standard provides (a)

minimum energy-efficient requirements

for the design and

construction of 1. new buildings

and their systems, 2. new

portions of buildings and their

systems, and 3. new systems

and equipment in existing

buildings and (b) criteria for

determining compliance with

these requirements.

90.1-2004 User's Manual

This manual provides detailed

instruction for the design of

commercial and high-rise

residential buildings to ensure

their compliance with ANSI/

ASHRAE/IESNA Standard

90.1-2004.

In addition, this manual: encourages

the user to apply the

principles of effective energyconserving

design when designing

buildings and building

systems; offers information

on the intent and application

of Standard 90.1; illuminates

the standard through the use of

abundant sample calculations

and examples; streamlines the

process of showing compliance;

provides standard forms

to demonstrate compliance;

and provides useful reference

material to assist designers in

efficiently completing a successful

and complying design.

A CD accompanies this manual

containing supporting files.

ANSI/ASHRAE

Standard 62.1-2004

The purpose of this standard is

to specify minimum ventilation

rates and indoor air quality that

will be acceptable to human

occupants and are intended to

minimize the potential for adverse

health effects. This standard

is intended for regulatory

application to new buildings,

additions to existing buildings,

and those changes to existing

buildings that are identified in

the body of the standard. This

standard is intended to be used

to guide the improvement of

indoor air quality in existing

buildings.

62.1-2004 User's Manual

This manual used in conjunction

with the Standard 62.1:

• Offers information on the

intent and application of

Standard 62.1

• Explains the standard

through the use of sample

calculations and examples

• Encourages the user to apply

the principles of good

indoor air quality and

effective ventilation when

designing buildings and

building systems

• Provides useful reference

material to assist designers

in efficiently completing a

successful and compliant

design

• Gives guidance to building

operation and maintenance

personnel

A CD accompanies this

manual containing the 62MZCalc

spreadsheet that assists in

the Ventilation Rate Procedure

calculations.

PRICES SUBJECT TO CHANGE WITHOUT NOTICE. ORDER AT WWW.ASHRAE.ORG/BOOKSTORE

OR CALL TOLL FREE, 1-800-527-4723 (US/CANADA), OR 404-636-8400 (WORLDWIDE).

$110/$88 (ASHRAE Member)

Softcover; 8.5

× 11 in.; 2004

$93/$74 (ASHRAE Member)

Softcover; 8.5

× 11 in.; 2004

$60/$48 (ASHRAE Member)

Softcover; 8.5

× 11 in.; 2004

$55/$48 (ASHRAE Member)

Softcover; 8.5

× 11 in.; 2005

ANSI/ASHRAE

Standard 55-2004

This standard specifies the

combinations of indoor space

environment and personal factors

that will produce thermal

environmental conditions

acceptable to 80% or more of

the occupants within a space.

The environmental factors addressed

are temperature, thermal

radiation, humidity, and air

speed; the personal factors are

those of activity and clothing.

Advanced Energy

Design Guide for

Small Office Buildings

For developing energy-efficient

buildings, the Advanced Energy

Design Guide for Small Office

Buildings provides a sensible

approach by including practical

products and readily-available,

"off-the-shelf" technology. The

Guide offers you all the tools

you need to create an energyefficient

building where the

owners will see a 30% energy

savings compared to buildings

that only meet the minimum requirements

of ANSI/ASHRAE/

IESNA Standard 90.1-1999.

Advanced Energy

Design Guide for

Small Retail Buildings

The Advanced Energy Design

Guide for Small Retail Buildings

is the second in a series

designed to provide recommendations

for achieving

30% energy savings over the

minimum code requirements

of ANSI/ASHRAE/IESNA

Standard 90.1-1999.

This Guide focuses on small

retail buildings, which make

up the bulk of the retail space

in the US. These buildings use

unitary heating and air-conditioning

equipment and are

limited to 20,000 ft2 in size.

Advanced Energy

Design Guide for

K–12 School Buildings

Energy costs typically account

for 16% of a district's "controllable"

costs. The Advanced

Energy Design Guide for K–12

School Buildings will help your

facilities staff design new construction,

renovations, remodeling,

and modernization projects

that use substantially less

energy—at least 30% less—

than those built to minimum

energy code requirements.

Achieving this 30% target is

not only possible, but easy, and

the Guide includes case studies

that show schools around the

country that have achieved or

exceeded the target.

PRICES SUBJECT TO CHANGE WITHOUT NOTICE. ORDER AT WWW.ASHRAE.ORG/BOOKSTORE

OR CALL TOLL FREE, 1-800-527-4723 (US/CANADA), OR 404-636-8400 (WORLDWIDE).

$47/$39 (ASHRAE Member)

Softcover; 8.5

× 11 in.; 2004

$62/$49 (ASHRAE Member)

Softcover; 8.5

× 11 in.; 2004

$62/$49 (ASHRAE Member)

Softcover; 8.5

× 11 in.; 2006 $62/$49 (ASHRAE Member)

Softcover; 8.5

× 11 in.; 2008

Procedures for Commercial Building Audits

This reference defines good procedures for an energy survey and analysis for purchasers and

providers of energy audit services. Also included is a format for buildings and their energy use that

allows data to be shared in meaningful ways.

The included CD provides more than 25 guideline forms (in both PDF and Word formats) with

explanatory material, to illustrate the content and arrangement of a complete, effective energy analysis report.

$58/$39 (ASHRAE Member); Softcover; 8.5

× 11 in.; 2004

__________________
"Memorize the calculations, you look like a fool searching your notes while teaching class"
Register to Reply
Register to Reply 18 comments

"Almost" Good Answers: