Water Supply Pipe in Utility Trenches

11/25/2008 3:39 AM

WHAT Pipe material is recommended for water pipeline (200 mm-500 mm) for above ground installations on supports.

What are the technical aspects to be considered/ evaluated if DI and HDPE are the available options?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: WATER SUPPLY PIPE IN UTILITY TRENCHES

11/25/2008 1:29 PM

http://www.dipra.org/pdf/DIPvsHDPE.pdf

(although it is going to be biased towards ductile iron )

Register to Reply
Participant

Join Date: Nov 2008
Posts: 2
#2
In reply to #1

Re: WATER SUPPLY PIPE IN UTILITY TRENCHES

11/25/2008 1:36 PM

THANKS, BUT I ALREADY REFFERED THAT, I AM LOOKING FOR real life EXPERIENCES FROM SOME SENIOR FELLOWS.

Register to Reply
Guru
Hobbies - DIY Welding - pipewelder

Join Date: Apr 2007
Location: North Georgia, USA
Posts: 671
Good Answers: 33
#3

Re: Water Supply Pipe in Utility Trenches

11/26/2008 9:00 AM

I look over and inspect several thousand feet of 36" above ground and below ground water pipe. I have some HDPE water pipe that is not in the ground but most of the 36" and up size is underground. HDPE is great for underground water lines IMO. Most of our above ground water pipe runs through 36" and 30" Sch. 40 SA-53 steel pipe. If you are thinking using HDPE for above ground there are a few things I would suggest.

1. The pipe is going to move allot during the day so it is best to have a support system that allows it to move.

2 Be carefull to fully support under the pipe at required intervals because it will start to sag in between the supports if not. This is really important if it goes over or through an area where it is heated by some other source or if the water inside the pipe is heated. It will sag more the warmer the air or the contents of the pipe gets.

3. If you are considering have long pumped runs of pipe where you could form a vacuum on the pipe when the pumps shut down I would suggest that you install a vacuum breaker every so often in the line. I had some above ground 20" HDPE that had a problem with this.

__________________
pipewelder
Register to Reply
Power-User
United States - Member - New Member

Join Date: May 2008
Location: Arizona
Posts: 355
Good Answers: 4
#4

Re: Water Supply Pipe in Utility Trenches

11/26/2008 9:53 AM

Good morning naveed.engr. I would highly recommend using the proper HDPE of the appropriate DR for the pressure and temperature involved for your underground piping. I would not bring it above ground, for many reasons. Make the transition below ground to the DI (or steel) pipe. For the underground portion of the DIP, clean and coat the pipe with the proper mastic and tape; and braze the proper anode and cathodic protection checking system to DIP.

The best HDPE pipe is made by Phillips Petroleum, trust me. Be sure to install 6" of fine sand (</= 1/4" dia) bedding prior to installing the HDPE, and 6" of the same cover. Use butt-fusion for your joints. Go have a beer with your girlfriend.

Register to Reply
Commentator

Join Date: Feb 2007
Location: Nashville, TN
Posts: 61
Good Answers: 4
#5
In reply to #4

Re: Water Supply Pipe in Utility Trenches

11/26/2008 5:12 PM

Phillips and Chevron merged their respective pipe groups to form Performance Pipe a division of the Chevron Phillips Chemical Company, Plano, TX, www.driscoplex.com.