Current Transformer

11/25/2008 6:50 AM

What is the difference between Protection CT and Measuring CT.What will happen if they wrongly connected.

__________________
shyam_gupta2630@hotmail.com
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: Current Transformer

11/25/2008 8:09 AM

I am not familiar with any differences.

I am speculating here but I would guess that it is in the way they are used. The CT just outputs a current that is proportional to the primary current. I use CTs for measuring current quite often. We just put a know resistance on the secondary and figure the primary current is (N*Vout/ R), N being the turns ratio. My first guess would be that a protection CT is used to measure current in the same way but the associated circuitry takes some protective action like current limit or shutdown if the measured current is too high (or low). That would imply that it is really a protection circuit that uses a CT as a sensor.

Still that is all speculation.

Anybody else have direct experience with the terms?

Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#2

Re: Current Transformer

11/25/2008 9:24 AM

shyam gupta; the protection ct is required on electrical services to protect equipment from short circuits on the load side power in the USA on service 1000 amps & larger. perry

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Current Transformer

11/25/2008 1:11 PM

Have a close look at the specs and datasheets for each of them (if you have them, and this is not some theoretical or homework question). You will find that the turns-ratio, accuracy, class, etc are all (generally) different. They are designed for different applications (purposes) and designed to interface to different equipment. They are still CTs thou.

If you connect them round the wrong way, your protection and measuring systems will not work properly (or at all).

__________________
jack of all trades
Register to Reply
Commentator

Join Date: Nov 2008
Location: S.E. Asia
Posts: 91
Good Answers: 1
#4

Re: Current Transformer

11/25/2008 1:31 PM

Accuracy Class & Burden are 2 critical things when considering the use of CT's. A good engineer will make the right decision regarding the situation i.e. will not spend money on 0.5 class high burden CT's when the situation does not require it.

CT's can be connected incorrectly but this is only a problem for the equipment connected to the secondary (incorrect operation). Your biggest concern should be to ensure that shorting links are provided in the secondary circuit of the CT so that maintenance can be done SAFELY.

__________________
"If you try to keep a leg each side of a barbed-wire fence, you'll do yourself a mischief." - Joh Bjelke-Petersen.
Register to Reply
2
Associate
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2007
Location: India
Posts: 42
Good Answers: 3
#5

Re: Current Transformer

11/25/2008 11:34 PM

Dear Shayam Gupta,

1)Measuring CT is used to measure currents in the system whereas protection CT is

used to protect the system on faults.Hence both intend to serve different

purposes.

2) As the measured quantity ie Current has to be very accurate which will be used for Metering viz KW,KVAr,KWH etc ,the accuracy of measuring CTs shall be very high.Normally accuracy will be 0.5 or 0.2 as per the requirement.This measurng CT will saturate on overload.

3)The protection CT is used for protection of feederes etc.It should be abe to carry the overload for short time and designed not to saturate for the overload.However the measuring accuracy of Protective CT will be very poor.In the case of say 5P10 and 10P10 , the CT will be able to carry 5xI and 10 x I without saturation with the overall accuracy will be +/- 5% and +/- 10% respectively.Hence measuring accuracy is very poor.However for overload current which is of very high order this amount of accuracy is suffcient for operation of Protective relay.

Hence if Protection CT is wrongly connected for measurement ,the measuring error will be very high .On otherhand if measuring CTis wrongly connected for protection purpose, it will not protect the system as it will be saturated on overload.

V.Ambarani

==============================================================

__________________
Best Regards
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Control Engineering - New Member China - Member - New Member

Join Date: Sep 2006
Location: CHINA
Posts: 2945
Good Answers: 14
#6
In reply to #5

Re: Current Transformer

11/27/2008 3:13 AM

if measuring CTis wrongly connected for protection purpose, it will not protect the system as it will be saturated on overload.

Although I dont agree to this words, I still vote you as a good answer.

I guess the protect ct will has more thick second wire than front. (Im out of door to electrician)

Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); cnpower (1); elkangorito (1); jack of all trades (1); perry (1); V.Ambarani. (1)

Previous in Forum: Test Methods for Halogen Lamp Emissions   Next in Forum: WRIM Resistor Grid

Advertisement