Stopping a Centrifuge

11/26/2008 12:13 PM

Hi everybody,

I have a customer with a centrifuge which is driven by an 18.5 Kw 3 ph 400 volt motor. The motor is controlled by an Inverter. The centrifuge has been in service for about 2 years. The problem is that it takes a long time to stop, 20 - 30 minutes depending on the load in the centrifuge. Up to now this has not been a problem as the centrifuge normally ran for about 6 hours at a time. Theyare looking at a new product which will have a much shorter drying time so it will only have to run for about two hours. Therefore, they would like to do several runs every day and would like to reduce the stopping time. I am thinking that installing braking resistors to absorb the regenerated energy is the way to go. Does anybody have any other suggestions? All comments will be appreciated.

Register to Reply
Pathfinder Tags: Centrifuge
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#1

Re: Stopping a Centrifuge

11/26/2008 1:47 PM

Yep. I've used braking resistors on human centrifuges (when they vomit, you've got to get that baby slowed down ASAP). I've also (once!) used a big disk brake - baaad idea.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#2

Re: Stopping a Centrifuge

11/26/2008 3:54 PM

This is a left field response, with a Green Spin so feel free to have a laugh.

Why not put a electromagnetic break or small generator on the main shaft and when you start the "Spin-down" cycle, this can then create electomagnetic Drag without physical conatct, with a side effect of putting some power back into the system through regenerative breaking.

This would reduce spin-down cycle times and put something back.

Similar idea to hybrid cars.

Just a though.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Stopping a Centrifuge

11/26/2008 4:34 PM

I have done this many times for what are called Gold Concentrators, which are essentially a large tapered centrifuge bowl doing batch processing. They want to cycle through as many batches as possible, which means fast braking. From my experience, here are your braking options:

Mechanical brakes; bad idea on a centrifuge as mentioned above. Too much friction heat, wear parts etc.

DC Injection Braking; putting DC onto one set of windings of the motor in order to create a non-rotating magnetic field and pull the rotor to a stop. Better than mechanical, but not realistically viable for batch process centrifuge machines because the kinetic energy is converted to heat in the motor, especially the rotor where it has trouble dissipating. Very short motor life is the result. If you were doing 1 or 2 braking cycles per day, this might make sense, but it is severely limited.

Dynamic Braking using a VFD and braking resistors. Better choice because the kinetic energy is moved into the resistors and away from the motor and drive. Getting resistors that will last for very long can be challenging however, and the long term cost of ownership must be considered against the best option listed below.

Dynamic Braking using a Fully Regenerative VFD. This option uses a more expensive (most expensive) VFD that is essentially two inverse parallel VFDs. Instead of the front-end being a simple diode brige converter, the front end is actually another inverter, set to pump the kinetic energy back into the line at the fixed frequency of the line. This means that no matter how often you want to brake, there is no energy needing to be dissipated in your process equipment. it also provides some energy recovery, assuming you have other loads running when you are braking. Although significantly the most expensive hardware as far as initial cost is concerned, it is the most reliable and will provide the lowest long term cost of ownership.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2008
Location: north east
Posts: 29
#10
In reply to #3

Re: Stopping a Centrifuge

11/29/2008 2:20 PM

regen drives would be your best,but most expensive,as mentioned solution,If you switched to a dc motor and regen.type controler you would save even more enrgy than an ac drive. Replaced a 150hp ac moto run by a soft starter with dc injection braking on a large wood chipper,with a 150 dc with a 12 scr drive. Cheaper to start chipper,basicaly free to stop it,overall better performance,speed feed back controled rim speed within .5% at any load.Stopping time cut in 1/2,only draw back motor did have more mainteance.

Register to Reply
4
Guru

Join Date: Oct 2008
Location: I'm outa here
Posts: 1924
Good Answers: 196
#4

Re: Stopping a Centrifuge

11/27/2008 1:40 AM

Is this a Beckman ultracentrifuge or something similar? If so, watch out, baby. You've got no idea what you are doing.

Think about this for a minute. How long does that machine run to accelerate its rotor up to speed? In minutes? During all that time that 18.5 KW motor is sending it's energy somewhere. Where? Into that spinning rotor, that's where. It's sending it into the chamber through a mechanical connection with very little being lost to heat.

Now you want to get the energy out, but faster. Your bright idea is to take it out the same way it was put in, through the same mechanical path. Only with some multiple of the original design torque. Now suppose for a minute that mechanical path fails and 90 or 95% of the energy is still in the rotor. Where's it going to go?

Stop now and pull one of the maintenance covers off the centrifuge and look at the structure surrounding the rotor chamber. Pretty robust looking. isn't it? Why would the equipment designers do something like that?

I'd suggest you get into a substantive discussion with a technical representative of the centrifuge manufacturer before you make any proposals to your customer.

Ed Weldon (Beckman Instruments Spinco division, Palo Alto, CA 1973-1979, manufacturing engineer for rotors and centrifuge drives)

Register to Reply Good Answer (Score 4)
Guru

Join Date: Dec 2006
Location: Germany 49° 26' N, 7° 46' O
Posts: 1950
Good Answers: 109
#5
In reply to #4

Re: Stopping a Centrifuge

11/27/2008 7:22 AM

Hi,

if acceleration time equals deceleration time why not brake with an external resistor?

Faster will/may be a big problem as previous post states.

We usually brake 3KW DC motors and 2KW asynchronous motors with a switched resistance. (Disconnect power supply and connect the resistor.)

Cooling may be a problem - we once did a high power (9KW) resistor by a stainless steel stripe, this was really good unless melting started so we immersed this into purified water. Titanium is also a good choice as it can be anodised for insulation.

Oxide coating by heating and subsequent epoxy or PAI or PI coating (as class H or C insulation is strongly recommended if in contact with any fluid.

Simplest and cheapest resistor that works perfect in air: light bulbs (many if 18KW), electric heaters 9x2KW?

Best and safest: follow previous post and ask the manufacturer.

Unconventional: make a small gap between rotor and stator and inject some water: terrible fast and efficient (may be too fast so you get pieces until experience is accumulated.)

RHABE

Register to Reply
Anonymous Poster
#8
In reply to #4

Re: Stopping a Centrifuge

11/28/2008 12:10 AM

I strongly agree with Ed.I maintained and repaired Sharples and then De Laval centrifuges for 32 years.You do not stop large masses of rotating metal quickly.I do not know what kind,size or speed of centrifuge you are talking about.It could weigh ounces to tons.They can often be stopped most safely by running water through it correctly.

Caution.Centrifuges have disintegrated and killed people.

I do not even like to be around one running as I knew that it could kill me at any time.Alfred

Register to Reply
Power-User

Join Date: Aug 2008
Location: West Virginia
Posts: 185
Good Answers: 12
#6

Re: Stopping a Centrifuge

11/27/2008 9:35 AM

You've covered some great ideas. I think a VFD will probably work best. It also allows you to reduce starting heat being introduced into the motor. If you start/ stop this motor much more frequently you're going to exceed the long term heat buildup in it. Does it have a "K rotor" or anything else to allow for slow starts? Do you know it's maximum starts per day? I know most large continuous centrifuges even with K rotor motors are usualy rated for less than 4 or 5 starts per day.

Register to Reply
Anonymous Poster
#7
In reply to #6

Re: Stopping a Centrifuge

11/27/2008 2:06 PM

As per my opinion, its better to give time to stop. may be quick stopping will create damage to other functional parts.

Register to Reply
Member

Join Date: Jan 2007
Posts: 6
#9
In reply to #7

Re: Stopping a Centrifuge

11/28/2008 11:54 AM

Thanks everybody for your valuable comments. Sorry about the delay in getting back, I was away for a few days. You have certianly given me food for thought. The "Green" idea is interesting Sapper. JRaef, you have some very good suggestions, do you know where I can get more info on the Dynamic Braking using a Fully Regenerative VFD ?. I am afraid that I do not have much information on the original manufacturer of this centrifuge, it is an old one which was origionaly hydraulic and it had an electric motor with a VFD fitted. It is quite a large centrifuge as you can imagine having an 18.5kw motor. I will try to find out more info.

Once again thank you all

Register to Reply
Anonymous Poster
#11

Re: Stopping a Centrifuge

12/01/2008 4:07 PM

It's simple, do NOTHING!

you are still only going to run it a few times a day. It will be done winding down and at rest when you need it again. Have you looked at the cost of stopping and starting this 3 or 4 times a day?

Register to Reply
Member

Join Date: Jan 2007
Posts: 6
#12
In reply to #11

Re: Stopping a Centrifuge

12/02/2008 6:26 PM

Yes....it seems that might be the best option from a cost point of view.....Thanks all

Register to Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#13

Re: Stopping a Centrifuge

12/06/2008 3:09 AM

Why not just shorting the run time and use that 20 to 30 mins of free spin as an advantage.

__________________
If you never do anything you never have problems.
Register to Reply
Member

Join Date: Jan 2007
Posts: 6
#14
In reply to #13

Re: Stopping a Centrifuge

12/08/2008 6:20 PM

Thanks dadw5boys that seems like a good idea, I will check if they are not doing that already.

Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!