Generators and Power Factor

11/30/2008 4:02 PM

I need something clarrified.

As I understand it, Generators generate Voltage and supply current in phase.

Generators are rated at PF=0.8 lagging meaning that they can handle loads down to that Power Factor before stalling or going offline.

I also understand that they can handle slightly leading Power Factors (PF=0.95-1.0) and after that the Generator controller will shutdown due to overspeed.

Which in the real world means that a 1000kVA Generator can Generate 800kW or better lagging and 950kW or better leading.

So in theory at PF=0.99 either way you can get 990kW without any problems.

But in CR4 posts I often see contradictory information or that a 1000kVA Generator can only generate 800kW.

So what I would like is to understand clearly is which is correct.

I'm quite happy to accept than my understanding is flawed, thus the question, but some of the answers I have seen don't make sense.

Thanks & Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Pathfinder Tags: Generator Power Factor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: Generators and Power Factor

11/30/2008 8:06 PM

Hello Sapper

The PF of the load varies, and more often the connected load is inductive (lagging current) rather than capacitive (leading current).

Because most uses of an alternator are going to have transformers, motors and other inductive loads connected, the alternator is rated at the PF 0.8 figure, as that is a "normal" status of most alternators.

A very rare load for any alternator would be one which is purely resistive, and of course there is still the alternator winding inductance itself to be taken into the calculation.

Most alternators are designed to cope well at the 80% figure above without any bother, but as overload is approached, most alternator control systems lose control of the alternator more and more easily.

Thus the 80% in kW of the 100% kVA rating is quoted as a safe working standard for alternators.

In cases of emergency, the 80% rating may be exceeded, but for a very short time only, as if damage occurs during such a period, the cost is quite extensive and expensive = a rewind job.

If a user regularly is needing a larger output than the 80% rating, it is more prudent to purchase a larger alternator unit.

I have also seen quite large crankshafts broken in the diesel motors of gensets, because of sudden overloads, and this means the genset may be out of action for many months, waiting replacement crankshaft + bearings and more.

Power transformers are similarly rated, with the normal effective kW being some 80% of the rated kVA rating on the nameplate.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Good Answer (Score 2)
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#2

Re: Generators and Power Factor

11/30/2008 9:10 PM

I suspect that if you read the specifications provided by the manufacturer, you will generally find that they derate the generator capacity for power factors greater than 0.8. As usual, if one reads the manufacturer's literature closely, the information is normally included. One should also note whether the generator capacity is rated for "standby" operation, or as a primary supply- again, one generally must adjust the rated capacity for operating conditions...

Register to Reply
2
Power-User

Join Date: Aug 2007
Location: San Francisco Bay Area
Posts: 266
Good Answers: 21
#3

Re: Generators and Power Factor

11/30/2008 10:22 PM

There are many people here that I am sure will answer this better than I but I dealt with gens and gen controls for quite a while so I'll try and help.

As I understand it, Generators generate Voltage and supply current in phase.

Only in theory on paper. Yes, if one hooks a purely resistive load to a generator you get a unity pf of 1. But reality is no. When you hook up a big resistor bank the cables you hook it up with will have an amount of capacitance and will also have an amount of inductive properties even if you are careful and have no coils rolled over at all. I've seen .995 or so on both sides of unity with 1MW resistive load banks. You look twice then realize your error and run to find out why the load bank fans aren't going.

Generators are rated at PF=0.8 lagging meaning that they can handle loads down to that Power Factor before stalling or going offline.

No...never heard that one before. An overloaded generator is just that ... overloaded. The engine is going to its knees and is about to get tripped off by protective relaying like under freq., overcurrent, undervoltage. If a 480v gen rated 1500kW/1875kVA is humming along at say...1500amps @ 0.8pf then a dip to 0.7 or 0.6 is not going to knock the unit off as there's plenty of kVA headroom. Now...bear in mind in multiple unit paralleling to the grid you'll usually find var/power factor controllers and associated protective devices for this application but this is designed by the engineer for system operation and protection, not because the generator can't handle it.

There are other issues of wasted energy, eddy currents and rotor heating from power factor being to far out there.

I also understand that they can handle slightly leading Power Factors (PF=0.95-1.0) and after that the Generator controller will shutdown due to overspeed.

Nope, never ran into that one either. Overspeed is a function of throttle control and usually occurs when a significant load is slammed on and the generator responds by going balls out and then ...just as copious amounts of beautiful black smoke is pouring forth...the load trips off. If the gen governor gain and damping aren't set to handle this the governor will not respond fast enough to back off fuel and then over rev.

ELI the ICE man... old industry saying. Purely resistive is unity or 1.0. eli the ice man is easy to remember which side of unity you are on if inductive or capacitive. I've seen plenty of big data centers that were running .65pf leading and added synchronous motors to bring the pf back up towards unity.

Which in the real world means that a 1000kVA Generator can Generate 800kW or better lagging and 950kW or better leading.

No...it's the same leading or lagging it's still (IE)(pf)

Yes in theory at .99 you get 990kW.. but it's the reality that kills. It can be really expensive to add enough cap banks to pull back towards unity. An engineer has to try to meet a happy medium between different expenses.

I've seen some wild whacked pf. I once did a job out at a new gold mine in Nevada where they were to operate two huge P&H shovels. They put in 3 paralleled Caterpillar 3516 gens at 2000kW each for 6MW. We built the switchgear and tied the gens to the grid which was a long skinny line up a little desert valley. One of the wildest things I ever seen. They put the gens in to hold up the line while the shovels ran and then to absorb the regenerative power when the shovels stopped. Those 3 gens literally would slam from .2 one direction to point 2 the other. Shovel would go...wham .2pf and i gotta hold all 3 together and on the grid while shoving so hard to push the pf back up... then slammo...shovel stops and we were using the gens to literally absorb....motor the power off the line. The gens would literally slam back and forth on the frames. They parked a welder in the compound because the peckerhead frames broke so often and they stuck a box of 100 diodes at each gen because they would frag out diodes several times a day. The mine ran like that for 6 months while the utility was running a 235kV dedicated line to them. So..point being... I know the abuse these modern gens will take.

Hope this does help some... also you can do some chasing with good ole Google. Lots of very good info regarding inductive and capacitive loads. Go to Basler and perhaps Woodward and read some of their generator control white papers.

__________________
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Jul 2008
Location: Mombasa, Kenya
Posts: 24
Good Answers: 1
#4

Re: Generators and Power Factor

12/01/2008 12:58 AM

Upto a point, the active component (KW) of apparent power (KVA) is determined by the prime mover characteristics (fuel control, governor response and the engine itself). The reactive part (KVAr) is handled by the voltage regulator and in a way dependends on the alternator/ generator characteristics. You may find that 1000KVA rated genset will be comfortable with 800 KW output 0.8PF, because the design stage made it that way. As soon as the PF starts decreasing due to more inductive load, though the active power remains constant, the armature reaction will increase forcing the prime mover to deliver more torque to overcome this reaction to maintain the constant speed requirement. So you may notice a slight increase in fuel demand with reduction in PF at constant KW output. Now, if you were to maintain PF at 0.8 and increase the KW to your 950 level. The prime mover may not handle it. The prime mover was designed to give you 800KW with about 10% short time overloads. You will notice, may be, undesired increase in temperature of the cooling medium and other components of the prime mover. The alternator/ generator may not feel much worse off because the amperage output is still within its design limits.

That is my take, though I am not an authority on these matters.

__________________
Curiosity has its reasons for existence - Albert Einstein
Register to Reply
Active Contributor

Join Date: Sep 2006
Location: France (Mulhouse)
Posts: 15
#5

Re: Generators and Power Factor

12/01/2008 5:02 AM

I will give you my point of view on this subject:

I will answer without taking into account the engine that must dirve the generator but only by looking at the generator.

The generators are design for a voltage [V] and a apparent power [kVA]. that mean you will have at disposal a certain amount of Current [A]. The manufacturer of the generator will design the windings taking into account this level of nominal current.

For the lagging loads:

The first limitation of the generator will be the current level in the generator winding, independantly form the pf, the maximum available current will be the same.

The second limitation, will be due to the rotor current limit. if you want to have a low power factor, you must increase the generator voltage, and for increase the generator voltage you must increase the rotor current.

The level of 0,8 pf factor limit comes from the normes on which the generator are design (IEC 34) which defines that the generator must withstand a pf of 0,8 for the nominal current without any special agrement between vendor and seller.

For the leading loads:

The limitation will be due to the underexcitation of the generator, as you have to have a low voltage to consume the reactive power, you will to decrease the rotor current, ana there will be an other phenomenone that will appear: the electrical torque that stuck the generator rotor to the electrical field will decrease, and you will increase the the chance to have pole slipping phenomenone.

On other limitation for the leading load could be due to the excitation supply system, for example shunt excitation system could not accept leading loads.

Just a drawing (do not take into account the line turbine Power)

__________________
marconet
Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#6

Re: Generators and Power Factor

12/01/2008 5:07 PM

Thanks Gents,

Between the different responses, I now understand were my original misconceptions came from and the flaws in the description I was given when I started working around generators.

Many Thanks for your time,
Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Register to Reply 6 comments