Boiler Drum level Tx. Have Range in Negative

12/12/2008 10:26 AM

I am an instrumentations engg,having only seven month exp. I saw that boiler drum have level tx.and it's range is (-50 to 0). why range is in negative in boiler, I don't know. Can you help me.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Dec 2007
Location: texas
Posts: 92
Good Answers: 8
#1

Re: Boiler Drum level Tx. Have Range in Negative

12/12/2008 6:26 PM

Hi, If what you have it's d/p cell level transmitter, it's possible that the low side of the transmitter is a "wet leg" this makes the lower range of the transmitter negative..Thank you

__________________
"The older I get -The better I was"
Reply
Participant

Join Date: Nov 2008
Posts: 1
#2

Boiler Drum level Tx. Have Range in Negative

12/12/2008 11:22 PM

In close vessels the mid point is zero,upper point is positive and bottom point is negative.If indication is zero its mean that value is 50%.If we use 0 to 50 range and system indicates that drum level is 0% ,its mean drum is empty.We avoid empty drum level.Also negative range tells us reference of water and steam in boiler.Thats why we use negative range in boiler.

Reply
Anonymous Poster #1
#4
In reply to #2

Re: Boiler Drum level Tx. Have Range in Negative

11/01/2011 5:41 AM

Hello,

At my power plant which is 87bar and 525 Temp (85TPH IJT) the distence betn upper and lower tapping on steam drum is 610mm and the range in Tx is -610 to 0 mmwc i wanna know the reason for negative range(-610mmwc) how Tx generated negative mmwc as lower tapping on HP side of Tx and upper tapping on LP side of Tx.

Regards

Sushil

Reply Off Topic (Score 5)
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#3

Re: Boiler Drum level Tx. Have Range in Negative

12/17/2008 12:49 AM

Hi there,

As stated above - it definately sounds as if you LP side of the transmitter is the wet leg.

Regards,

Craig

Reply
Reply to Forum Thread 4 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Asif Zubair (1); craigza (1); wrenchpuller (1)

Previous in Forum: HART Pressure Transmitters   Next in Forum: Tolerance of Transmitters and Gauges
You might be interested in: Boiler Services, Boiler Controllers, Drum Pulleys

Advertisement