Tolerance of Transmitters and Gauges

12/13/2008 2:26 AM

Hi,

I'm preparing a calibration plan for our transmitters and gauges for our power plant. These transmitters and gauges handle pressure, flow, temperature, level, pH and conductivity.

What will be the acceptable tolerance for these process and non-process instruments?

We categorized these instruments as process and non-process to identify those that are directly involved in the main process of producing steam for power generation and those that are indirectly related.

Is 2% of FS acceptable for tolerance on these transmitters and gauges?

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#1

Re: Tolerance of Transmitters and Gauges

12/13/2008 4:35 AM

Ahem, that's the same problem I faced in 1994 (and still do).

While working for our ISO9000 accreditation, I asked the guys in production for their process tolerances. Two answers were all I got:

"As accurate as you can make it."
"Zero error."

The first answer is as vague as you can get. The second answer is worse...it's impossible to achieve.

Speaking with the corporate automation head, he said that the production tolerances are supposed to be in the factory manager's office, only available on request by certain persons and for eyes only (not to be taken out of the vault).

What we did was to take the accuracy figures stated by the manufacturer and multiply them by four. For example, if your instrument has an accuracy of 0.25%, we set the calibration tolerance as 1%. Worked for some loops but not all. We had difficulty factoring installation and environmental effects (especially true for weighscales)

Several years later, we're still groping in the dark.

If your production people can tell you how deviation in psi/bars/MPa of steam they can tolerate, you can specify a slightly tighter tolerance for your calibration. If they can't tell you, sit down with them and come to an agreement, on paper.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#2

Re: Tolerance of Transmitters and Gauges

12/14/2008 12:10 AM

Why do not we take the basics of the measurement ?

What we need to measure and what is our required tolerance (for the system)

Say we measure flow and it shoulf be not less than 100 lpm and not more than 120 lpm then our value is 110≠ 10,

The gauge should have tolerance not more than 1/10 of this ie ≠ 1 LPM

Now convert it to whatever way you want - FSD or otherwise.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#3

Re: Tolerance of Transmitters and Gauges

12/14/2008 1:05 PM

What you need is first to know the process tolerances. You cannot define the uncertainty of a measurement without knowing what it is used for.

From a probability point of view you should define the risk limit for your measurement and after it define with which reference (uncertainty of the reference) you will try to calibrate it.

There is many times a misunderstanding between tolerances and uncertainty. The tolerance is prescribed as the limits within the result of the process should be found with certain level of risk.

The tool used to measure presents an uncertainty which is the consequence of its calibration according to procedures against a reference which also was calibrated and presents as well an uncertainty.

This is the chain of traceability to the basic reference at International Bureau of Standards. This chain is the guaranty that all measurements where ever they are done and with which ever devices are comparable with respect to given results.

Register to Reply
Participant

Join Date: Jan 2014
Posts: 1
#4

Re: Tolerance of Transmitters and Gauges

02/04/2014 9:39 AM

Instrument tolerance values should vary with the cricticality of the application in the process, e.g. custody transfer, SIS, monitor & control, indication only. In addition to this, test equipment capability and manufacturer tolerance specs must be taken into consideration.

Are there any standards that can guide in determining these tolerance values?

Register to Reply