We are going to purchase a HART 4-20 mA pressure transmitter. Can I use this transmitter in the conventional 4-20mA current loop without using the HART functionality.
South Africa - Member -
Good Answers: 12
Re: HART Instrument
12/12/2008 2:03 AM
Hi there,
Yes you can. If you want to use the HART functionality - your input card would need this facility. The HART signal is only superimposed over the 4-20mA which is what you are interested in.
Just as a matter of interest, most trasmitters today come with HART already, but not many people use the actual functionality.
So in a nutshell - you can definately use the instrument as you would in a conventional 4-20mA loop.
Regards
Craig
Re: HART Pressure Transmitters
12/15/2008 3:50 AM
Yes you can, without anydoubt.
The Hart functionnality will remain there and you can access to them via a pocket.
The Hart signal is a digital protocol which is carried (as an FSK signal) over the 4-20mA signal.
Enjoy
12/19/2008 4:08 AM
Yes, as all the others above have indicated.
Check-out the Wikipedia page on the Hart Protocol for confirmation reading. It's a calibration/transmission system that is superimposed upon the 4-20mA analog loop without interference between them - that's the beauty of it. The transmitter will behave just like a non-Hart transmitter if the Hart stuff isn't in use. Come to think of it, it will do the same if the Hart stuff is in use as well.