I need to find out shear strength & pull out load on a 12mm dia , 200mm long Anchor bolt. I have taken the steel shear strength as 90 N/sq.mm.
Re: Steel
12/16/2008 10:09 AM
Do you know the type/manufacturer of the anchor?
Or is it a "custom" J-bolt?
For example if you know it is a Hilti Kwik-bolt you may the info here:
http://www.us.hilti.com/data/techlib/docs/Product_Technical_Guide/Anchoring_Systems/4.3.4_KB-TZ_Expansion_Anchor(316-327).pdf
or any other Hilti anchor:
http://www.us.hilti.com/holus/modules/techlib/teli_results.jsp?type=Product_Technical_Guide&subtype=Anchoring_Systems
Re: Steel Shear Strength and Pull-Out Load
12/17/2008 12:39 AM
You can use the Shear Strength to be equal to 45% of the Allowable Tensile Strength of the bolt material.
12/17/2008 7:48 PM
Allowable Pull Out loads depend on the anchoring system typically more than the bolts. You should look up the manufacturers recommendations.
Good Answers: 137
12/19/2008 4:05 AM
.....and on the concrete strength, depth of embedment and other details. 200mm is probably overall length, not embedment depth. Is it cast in (J-type or similar) or drilled hole? If drilled hole is it expansion or chemical type?