Transformer insulation resistance

12/28/2008 6:57 AM

Can some body tell me what could be the possible reason of low insulation resistance of power transformer. Is it Oil, the dielectric strength of oil is 50kV but the water content in the oil are approx 30ppm. or is it due to winding problem.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#1

Re: Transformer insulation resistance

12/28/2008 11:58 AM

Dear friend

HAPPY NICE HOLIDAY AND NEW YEAR 2009

Its not so simple to answer this questions, because you do not inform the detail to analyzed, could you inform what test that has been done to this x-mer, and what is the IR that has been measured, phase - phase, phase to ground ? and what is the PI and DAR (dielectric absorption ratio) status, did you test "step voltage" ?

SFRA (sweep frequency response analyzer) is good to analysis for the winding deformation and its position caused by mechanical and thermal effect.............

Following is table that taken from many literatures may can helping you to analysis.

Suggested test limit for service – aged oil by voltage class

IEEE Insulating Fluids Committee, Projects 637

Property

Test Limit

Voltage Class

≤ 69 KV

69 - 288 kV

≥ 345 KV

ASTM Test

Dielectric Breakdown Voltage 60 Hz, KV Minimum 26 26 26 D – 877
Dielectric breakdown

voltage KV Minimum

[0,040 inch gap thin ]

23 26 26 D – 1816
Neutralization Number

mg KOH / g, oil maximum

0,2 0,2 0,1 D – 974
Interfacial Tension Test

Dynes/cm, minimum

24 26 30 D – 971
PF, 60 Hz. 25

oC Max. Percent

0,65 0,39 0,31 D – 924
Moisture Contents

PPM Maximum

35 25 20 D – 1533

RECOMMENDED TEST VALUES CONTINUED SERVICE OF TRANSFORMER INSULATION OIL

Authority

NN

mg KOH/g

Maximum

IFT

Dynes/Cm

Minimum

Dielectric

D-877

KV Min.

P,F %at 25oC

Max

Moisture

Content

PPM. Max

Westinghouse

0.15 21 28 1.0

GE

0,20 24 26 0,65

Kemper

0,36 21 24 1,0 25

Factory Mutual

0,25 18 23,5 -

American Nuclear Insures

0,20 22 23,5-31 - 50

EPRI Utility Survey

0,32 23 27 0,80 34

NFPA

0,40 - 22 - -

IEC

0,50 15 30-50 - 20-30 mg/l

SUGGESTED PROPERTY REQUIRMENTS OF RECLAMED OIL FOR TRANSFORMER References : IEEE Insulating Fluids Subcommittee (proposed, April, 1980] Project 637.

PROPERTY / TEST

LIMIT

ASTM TEST METHOD

Physical

Flash point, minimum,

oC

140

oC

D – 92
Specific gravity 15

0C / 15oC, Maximum

0,91 D – 1298
Viscosity Maximum At 40

oC [mm2 / sec ]

12,0 D – 88 or D - 445
Visual examination Clear D – 1524
IFT minimum [dyne / cm] 35 D – 971

Electrical

Dielectric Breakdown Voltage 60 Hz, Min. KV 30 D – 877
Power Factor at 60 Hz, 100

oCMax. %

1 D – 924

Chemical

Neutralization Number [NN]Max. mg KOH/g 0,05 D – 974
Oxidation InhibitorMax. % by weight 0,3 D – 2668
Water Maximum, ppm 35 D - 1533

Gas Qualitative and Quantitative Interpretation

TYPES OF PROBABLE FAULTS

Detected Gas

Interpretation

Nitrogen + 5 % or less of Oxygen Normal operation of sealed transformer
Nitrogen, Carbon dioxide, or Carbon monoxide, or all Transformer overloaded or operating hot, causing some cellulose breakdown, check operating conditions
Nitrogen and Hydrogen Corona discharge, electrolysis of water, or rusting
Nitrogen, Hydrogen, Carbon dioxide, and carbon monoxide Corona discharge involving cellulose or severe overloading of transformer
Nitrogen, Hydrogen, Methane, with small amount of ethane, and ethylene Sparking or other minor fault causing some breakdown of oil
Nitrogen, Hydrogen, methane, with carbon dioxide, carbon monoxide, and small amount of other hydrocarbons, acetylene is usually not present Sparking or other minor fault in presence of cellulose
Nitrogen with high hydrogen and other hydrocarbons including acetylene High energy arc causing rapid deterioration of oil
Nitrogen with high hydrogen methane, high ethylene, and some acetylene High temperature arcing of oil but in confined area, poor connection or turn to turn shorts

INSULATION RESISTANCE

R = Insulation Resistance of Winding to Ground at 20oC

C = 0.8 for oil filled transformer at 20oC

C = 16 for dry compound filled or un tanked oil filled transformer

E = Voltage rating of winding under test

KVA = Rated Capacity of winding under test

Good luck

Rgds

Sis

__________________
LOVE FORUM AND DISCUSSION
Register to Reply Good Answer (Score 3)
Anonymous Poster
#5
In reply to #1

Re: Transformer insulation resistance

02/25/2009 8:33 AM

wht ia the basis of this formulla

Register to Reply
Commentator

Join Date: Mar 2007
Location: Chicago suburbs, USA
Posts: 73
Good Answers: 21
#2

Re: Transformer insulation resistance

12/29/2008 12:26 AM

The problem sounds like it may be high moisture content, or insulation degradation (aging or perhaps high temperature damage). A power transformer's associated cellulose-based insulation readily absorbs moisture, lowering insulation resistance. Although it may be possible to use vacuum treatment on the oil to remove moisture, if this does not correct the problem transformer rebuilding or replacement may be the only other option.

__________________
Stoneridge Engineering - Wreaking Havoc with Electrons for over 40 Years!
Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#3
In reply to #2

Re: Transformer insulation resistance

01/06/2009 5:54 AM

Do Formaldehyde content test, it will guide how much insulating papers are healthy.

__________________
BNDas
Register to Reply
Associate

Join Date: Feb 2009
Posts: 34
Good Answers: 4
#4

Re: Transformer insulation resistance

02/17/2009 6:02 PM

This is a common occurance that confuses many people.

Simply put. If you have a high moisture (water) content in the total insulation system (cellulose + oil) you will get that water migrating between the paper & the oil during the heating and cooling cycles the transformer goes through. as the transformer heats up water migrates to the oil & conversely when it cools the water goes back to the cellulose insulation.

If you take an oil sample & get 30ppm it will depend on what temperature you took the sample at. As well the dielectric strength can still be 50KV with that level of moisture but not be a problem. If the IR is low you need to assess that at the temperature it was taken. So if you took the oil sample at high temperatures then did IR at a cool temperature then the moisture will be high in both as you are measuring some of the moisture twice because it has been migrating.

You need to try & do both tests at similar temperatures that way you will see the true level of moisture. If the same readings are obtained then I would consider looking at drying out the transformer to remove as much moisture as possible.

I hope this helps

__________________
Murphy was an optimist....
Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); BertHickman (1); biswanath.das (1); KRW43 (1); Siswanto (1)