12/30/2008 2:32 PM
400 volts 3 phase motor with how much kw or hp would be good for driving a fire pump capacity 4000 gpm at 100 psi
Good Answers: 101
Re: Motors for Driving Fire-Protection Pumps
12/30/2008 5:51 PM
pump hp input= (flow*pressure)/(1714*efficiency)
flow=gpm
pressure=psi
efficiency=pump efficiency % (pump calculated 75%)
(Electric motor efficiency calculated= 90%)
I would size for ~350hp
325hp min
12/31/2008 10:48 AM
thank you it is good formula I like it.
Further to this if we use a diesel engine ,would it be enough with 350 hp out put.
Good Answers: 101
12/31/2008 10:54 AM
HP is HP, but when sizing for a diesel motor, you have to take into account the power-band and rpm ranges for the motor. It's easy to get "burned" by selecting an inappropriate motor for the job.
12/30/2008 11:28 PM
shankar from india
another simple formula:
HP = (gpm(imperial) x head in feet)/ 3300 for 100% efficiency
HP= (4000 x 220)/3300 = 266 hp for 100 percent efficiency
For 70% efficiency it is 266/.7 = 380 HP.
you will have to make another correction if the gpm given by you is american gallons.
1 psi = 2.2 head in feet
i stand to be corrected
bye - shankar
12/31/2008 10:55 AM
thank u for good reply what about diesel if we use that would its hp 380 enough or some correction is to be made.
Good Answers: 101
12/31/2008 11:37 AM
I would suggest contacting your pump manufacturer (if you have the pump already), and have them recommend you an engine. Without knowing more of the details it would be hard to give an accurate answer here, as i would be assuming many key elements. Like i said before, its quite easy to select a inappropriate engine for the job.
Good Answers: 19
12/31/2008 12:36 PM
Trust but verify!
Talk to the pump manufacturer and run the calculation. If there is a difference in the numbers ask questions and find out why. Learn something in the process.
01/06/2009 10:18 AM
4000 gal = 18.16m3. (Imperial gallon)
18.16m3/min = 0.302m3/sec
100psig = 689655N/m2.
689655N/m2 * 0.302m3/sec ≈ 209kW ≈ 279hp
Divide by, oh, say 80% pump efficiency, er, say 261kW or 350hp or so.
Add a bit for good measure, as one doesn't want the thing failing before the water reservoir dries up, er, say 300kW or 400hp would probably be adequate.
Would diesel-drive with a local fuel tank be a better selection, just in case the local power supply isn't available precisely when it is needed in anger?