Motor winding dry out?

01/04/2009 7:25 AM

Recently we have faced a motor winding burnt after installed the new motor(90HP). I found that the motor burnt due long storage.we are using controlled temp and humidity storage room for storing all motor.even though the motor was burnt. i want to discuss the problem and find a permenant solution.

Q.1.If the motor stored in long period(more than 6 months),need to dry out winding?

Q.2. If need dry out ,what is the procedure for dry out?

Q.3.Is dry out procedure vary depends on capacity of motor?

Q.4. Is it any dry out equipment available in market,please give the details of manufacturer.

Register to Reply
Pathfinder Tags: Electric motor dry out
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#1

Re: Motor winding dry out?

01/04/2009 7:31 AM

paramasivan4u; you could use low voltage direct current to warm the winding.perry

Register to Reply
Active Contributor

Join Date: Oct 2006
Posts: 17
#2
In reply to #1

Re: Motor winding dry out?

01/04/2009 7:40 AM

i want details about all my question,can u explain me details

Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#3
In reply to #2

Re: Motor winding dry out?

01/04/2009 7:54 AM

paramasivan4u: usually motors are dipped & baked in varnish or an epoxy when they are manufactured, you could use a controlled oven to bake them again. were all the winding in the stator burnt or dis colored? the motor may have single phased which would burn out one winding, rather then all windings, perry

Register to Reply
Active Contributor

Join Date: Oct 2006
Posts: 17
#4
In reply to #3

Re: Motor winding dry out?

01/04/2009 8:43 AM

all phase winding are burnt

Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#5
In reply to #4

Re: Motor winding dry out?

01/04/2009 9:34 AM

paramasivan4u; do you use motor overload protection? it sounds like it is undersized for the load, or the load was dragging the motor down, may be mis wired or wrong voltage. how long did the motor run before it smoked, was it under operating conditions? perry

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Motor winding dry out?

01/04/2009 12:45 PM

I have previously posted this in another forum.

http://www.eng-tips.com/faqs.cfm?fid=1157

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Commentator
Engineering Fields - Power Engineering - Siswanto

Join Date: Mar 2008
Location: JAKARTA. INDONESIA
Posts: 73
Good Answers: 15
#7

Re: Motor winding dry out?

01/04/2009 1:11 PM

Hello..

How and what ...for.. Motor winding cleaning and dry out, has been discussed in this forum, please read the topic title as below, posted dtd Dec 24, 2008

Motor externally by spraying water?

Good luck

Rgds

Sis

__________________
LOVE FORUM AND DISCUSSION
Register to Reply
Anonymous Poster
#8

Re: Motor winding dry out?

01/05/2009 12:17 AM

Dear PAramasivan,

By your statement, It is saying that, motor burnt, because of moisture aberve while storage, But there are so many reasons behind motor burning after replacement of existing burnt motor. naturally you may have checked ohmic valve, megger value and free roatation of motor before installation.

there may be different reason behind this, may be over loading / wrong wiring / wrong voltage , this are the reason burnt all three windings. moisure observing may damge insulation failure not complete winding burning.

for better understanding, send photo's of defective motor.

bye

Keshavamurthy

Register to Reply
Guru

Join Date: Dec 2005
Location: Queensland Coalfields Australia.
Posts: 697
Good Answers: 11
#9

Re: Motor winding dry out?

01/05/2009 1:27 AM

To decide if a motor has absorbed moisture conduct a polarisation index test. Look up how to do this either in earlier threads I've subscribed to or google the topic. Moisture shows very plainly by this test. If you decide there is moisture to remove a DC welder adjusted to provide no more than full load current will warm it up gradually. Considering that DC will not excite all 3 windings equally swap connections as necessary.

Of course an oven is better but not always available.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2008
Location: Anywhere I may be at the time
Posts: 661
Good Answers: 16
#10

Re: Motor winding dry out?

01/05/2009 10:04 AM

As already stated, low voltage DC is a common option. I've seen people carefully use welding machines for this purpose.

Large motors and generators in most cases easily accept heaters (heat strips) that are simply plugged into a wall socket.

Register to Reply
Associate

Join Date: Dec 2007
Location: Dubai
Posts: 32
Good Answers: 1
#11

Re: Motor winding dry out?

01/05/2009 12:20 PM

Please see recommended action before you replace yoour burnt motor:

1. if all phsaes of winding is burnt - you may have a lock rotor or your load side may have been stuck up, safety control enterlock suck us motor overload, timer had malfunction (XL, partwinding etc.)

2. as mentioned that unit, was put in long storage - possible cause is winding had been moistiorized, grease degreaded/moisturize and stuck up bearings.

3. to avoid such scenarios, please see list below prior to unit start up:

a. dry run controls

b. megged motor windings and resistance test

c. apply heat to motor winding (1000amps flood light at motor body) and monitor megger value for any improvments - you should achieve increasing megaohm value above 1000Mohs or infinity - if moto megger below <4Mohms

d. check motor sensors resistnace and connect to control enterlocks

e. if unit is installed with internal heaters, follow motor epcs concerning installation

f. run motor with out or with load and observed motor RLA

g. if motor megger is in doubts, monitor motor resistance say every 1hour or higher)

if above instruction will be followed accordingly, then i'm pretty sure that you will run the motor at normal operation .

Feel free to email: nlparedes2006@yahoo.com for more info if required.

__________________
nlp
Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#12
In reply to #11

Re: Motor winding dry out?

01/05/2009 11:14 PM

nelson1; i sure you meant 1000 watts, not amps in answer "c" . perry

Register to Reply
Associate

Join Date: Jul 2006
Location: OZ
Posts: 33
Good Answers: 3
#13

Re: Motor winding dry out?

01/06/2009 11:05 PM

I was involved for twenty years in the manufacturing of electric motors for ABB in Australia.

The motors are dipped & baked in an epoxy varnish and baked until the epoxy goes hard.

We use to store motors in an open warehouse some time for more than two years.

No drying precaution was taken before shipping motors out.

All our motors were manufactured to be installed outdoor.

The baking was done by passing DC current through the windings.

I would suggest that the problem was not caused by moisture during storage.

To dry a motor out, you could pass DC current through the windings or in an oven.

The temperature will depend on the insulation class "F" or "H".

__________________
Shocking from OZ
Register to Reply
Guru

Join Date: Dec 2005
Location: Queensland Coalfields Australia.
Posts: 697
Good Answers: 11
#14
In reply to #13

Re: Motor winding dry out?

01/11/2009 5:51 PM

As an answer to you rather than the OP. I've certainly seen brand new high quality motors with the effects of moisture in storage. A couple of specifics involved though, tropical maritime environment and incorrect use on anti condensation heaters (wired via a time clock). The motors were not damaged as the moisture was detected by routine polarisation testing and the timer bypassed. After around a week the polarisation test revealed the motors were all again dry. This event has convinced me of the worth of polarisation and I have used it as a decision making tool in the 25 years since to good effect.

Register to Reply Off Topic (Score 5)
Anonymous Poster
#15
In reply to #13

Re: Motor winding dry out?

10/28/2010 5:08 AM

can u give me information regarding with seminar topic on "MOTOR DRYING OVEN"

OR

Books refer for same.

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16
In reply to #15

Re: Motor winding dry out?

07/10/2024 7:13 AM

Try Microsoft Copilot, and Amazon.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 16 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Emjay4119 (2); JRaef (1); nap (1); nelson1 (1); paramasivan4u (2); perry (4); PWSlack (1); Siswanto (1); Tim in Mexico (1)

Previous in Forum: active power, reactive power   Next in Forum: HV-Surge Arrester

Advertisement