Elevator System

01/06/2009 3:03 PM

I amhaving trouble with an elevator driven by a siemen VFD and a 10HP motor. The VFD is showing an f011 fault meaning motor is drawing too much current, but the motor is good when run independently. what can be the problem?

__________________
Give Thanks 4 Life
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: Sep 2008
Posts: 31
#1

Re: Elevator system

01/06/2009 3:35 PM

Hello,

What is the specification of Siemens VFD? It seems Thyristors have failure then drain much current than need. by increasing setpoint in hand-mode and check current each phase you might detect the failure phase of VFD

Regards

DBT

Register to Reply Score 1 for Good Answer
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#2
In reply to #1

Re: Elevator system

01/06/2009 4:21 PM

Motor runs fine when disconnected from the elevator? How may amps and are they low as you would expect? Balanced phases?

If so:

Drive and motor are probably good.

Something mechanical is likely to be hanging up or dragging on the elevator equipment, based on what you posted. I would look all the bearings and sheaves over real close and check for debris caught in something.

Good luck, K T

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Active Contributor

Join Date: Mar 2008
Posts: 12
#4
In reply to #2

Re: Elevator system

01/06/2009 9:10 PM

Elevator roll OK when the brake is removed.

__________________
Give Thanks 4 Life
Register to Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#5
In reply to #4

Re: Elevator system

01/07/2009 12:41 AM

You may consider JRaef's post below--

I hadn't considered the braking mechanism--We tried a VFD on a motor that had a mechanical brake and gave up on it--The drive couldn't develop enough torque to release the brake before faulting. I don't know much about elevators so I will leave this to someone who does.

Sorry, K T

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Elevator System

01/06/2009 7:10 PM

Using drives on elevators is VERY tricky, potentially dangerous, and should not be undertaken by those not familiar with the specific challenges involved. Was this nstallation done by someone who knew what they were doing?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#6

Re: Elevator System

01/07/2009 8:05 AM

Is this an old or new installation?

If it's old, then the problem might be in the VFD since the motor checks out okay. It can also be in the elevator's construction. Something jamming the car?

If it's new, is the motor matched to the drive? If memory serves me right, elevator motors are high-starting current devices. Also, starting a motor with low-voltage and low-frequency will naturally increase the starting current, possibly exceeding the drive's limits.

In one non-elevator application, our VFD tripped when the brake didn't disengage fast enough. We rigged up the program so that the brakes were disengaged about a half-second before the VFD actually started.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Anonymous Poster
#7

Re: Elevator System

01/07/2009 9:49 AM

You need a constant tork vfd, ran into the same problem last friday.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#8

Re: Elevator System

01/07/2009 11:06 AM

You need to answer a question...

Does this elevator carry people?

If the answer to this is "yes" you need to get a person who is approved by the Elevating Device legislation in your jurisdiction to repair elevating devices to check this unit out. Doing anything more then this opens you to huge possible legal and liability issues.

As JRaef has correctly pointed out... drive control on a lifting device is tricky and, again if the lifting device carries people, is best left to those authorized and capable of making these repairs.

Caution and prudence is called for.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#9

Re: Elevator System

01/07/2009 11:09 AM

It would help if you state more detail.

Is this a new problem developing in old equipment?

Is this a new installation?

Have any parts been replaced lately, etc?

Only you know what detail questions I could have included here, Please add as needed.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Appliedtech (1); CJMcGill (1); dbt (1); JRaef (1); Kilgore Trout (2); North of 60 (1); Vulcan (1)