Generator Loads and Output Voltages

01/11/2009 6:12 PM

hello,what happens when i reduce the exciting power (for example amount of water) to the shaft of a sync. generator while it is parallel to the infinite grid and working at no load? does the output voltage of the generator remain somehow or a current passes from the windings of the generator because of the difference of the output of generator and the constant bus voltage of the grid? and it is necessary to keep in mind that frequency balance becomes off.. so pls tell me the results..

__________________
jinxnao
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#1

Re: about generator and AVR

01/11/2009 9:43 PM

Generation becomes like any other motor when the power source diminishes. The phasors reverse, the generator stays in sync but the power source is now the grid.

Once the water or wind or steam returns, then the phasors reverse direction and power flows back into the grid.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#2

Re: Generator Loads and Output Voltages

01/13/2009 4:29 AM

The frequency balance is never off while the generator is hooked into the grid.

If it is running on no load !!! why to run it at all (ifl a load is drawn from the grid then all the gens will contribute to it on no load means there is no load on the grid ? ideal situation) and that means it is a homework question.

Pl go and study the portion of Sync gen in your text book (You may find a bit in the design of machines too if I remember)

Offtopic portion: (Pstt Euro not again)

getting bored of too many homeworks . hey didn't solve so many in all of my 5 years of engg (yes ot was five year then now since kids are aging faster it is reduced to 4 years proportional to life expectancy).

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Commentator
Engineering Fields - Manufacturing Engineering - Look for solutions before the problem occurs

Join Date: Jun 2008
Location: Missouri
Posts: 68
Good Answers: 5
#3

Re: Generator Loads and Output Voltages

01/13/2009 6:32 AM

This is an interesting topic that I have thought about for some time. I would like to pose a similar question that may help in answering this one. I have multiple small generators from 3kw to 10kw. I have a need occasionally at a bible camp, (it is in a remote location and susceptible to frequent power outages) to run the camp on generated power. We currently set up a generator for the well pump and one for the kitchen ( refrigeration) and bath house (for obvious reasons). Can the generators be synchronized to run more together than just the one area? i.e. additional lighting, fans, and the pool circulating pump. Both generators are rated for more than is currently being used but in order to run these additional items, the main panel would have to be fed thus opening up a myriad of possible power consumption. I currently have an automatic disconnect that will isolate the power grid that is approved by the power company. If I can sinc multiple gen sets, (of different kw ratings) then I could add the needed power to run all of the camp. If anyone has ideas please reply.

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#4
In reply to #3

Re: Generator Loads and Output Voltages

01/13/2009 6:51 AM

Yse you can, only you need a few things like governor etc, the total equipments with the automatic controls etc may fill up approximately one small sized room (obviously you need an AC to keep the temperature of room down) and the operation and control expert who will keep on looking at the alarms and adjust a knob here and there.

The alternative is to have the total control to be housed inside an AC van and bring to the camp along with the operations man (not chap you know, there is no depression in this sector)

The next alternative is get a larger generator (and thereby saving energy)

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Commentator
Engineering Fields - Manufacturing Engineering - Look for solutions before the problem occurs

Join Date: Jun 2008
Location: Missouri
Posts: 68
Good Answers: 5
#5
In reply to #4

Re: Generator Loads and Output Voltages

01/13/2009 7:08 AM

SB,

Thanks for the reply. My train of thought would lead me to believe that once the gen sets are in sinc they will remain in sinc. I believe this to be for the reasons stated in the second reply to this thread. If the grid (at this time the multiple gen sets) are in sinc then as the total load is increased then each set will supply its % of increase thus remaining in sinc. If a sudden load in incurred, i.e. compressor startup, then they will all be loaded to the proportion of rated output and then remain in sinc. If one tries to accelerate or decelerate, then the others will maintain it in sinc as it will try to "motor" from the grid. Is this true.

Register to Reply
Anonymous Poster
#6
In reply to #4

Re: Generator Loads and Output Voltages

01/13/2009 10:01 AM

Bear in mind that your small 3-10 KW generators may be induction tyope and not sybchronous type.

You will need synchroscope and interconnecting power cables sized to carry the maximum load.

Your circuit breaker s will have to be able to trip quickly to avoid damage in the event of a fault.....

Stuff we do in a power plant...

Register to Reply
Anonymous Poster
#7
In reply to #6

Re: Generator Loads and Output Voltages

01/13/2009 10:42 AM

Generators can be paralleled by making an equalizer connection to prevent one of the generators from acting as a motor running off the other generator. An equalizer is a connection between the series fields of the two gensets. This will maintain the same voltage across all series fields. The connection needs to made on the armature end of the series fields to the same polarity on both generators. Paralleling multiple small generators is not practical. One large generator is a better solution, but then the problem of the distribution wiring for the whole camp.

Register to Reply
Anonymous Poster
#13
In reply to #7

Re: Generator Loads and Output Voltages

01/13/2009 8:50 PM

I agree with this reply from the question. It is practical to use 1 generator with the specified output power needed.

Anyway, what is the purpose of connecting mulitple generators in parallel?

To increase fuel efficiency and reduce consumption? Well, we have to think more than that.

Currently, I am working (R&D) on a power generator that consumes minimal power source but produces substantial greater power output.

cheers!

Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#11
In reply to #3

Re: Generator Loads and Output Voltages

01/13/2009 1:41 PM

While the answers that were sent to you do not sound like there is a practical solution, there is always the thought of trying to collect some alternative power solutions.

Is there an abundance of wind? Convert an old belt drive ventilation fan to collect this power, and turn it into 12 volts with salvaged automotive batteries, and alternators. Just replace the belt drive fan motor with automotive alternators. Feed the power to salvaged automotive batteries. 12 volt lighting with LEDs is very efficient. If you can find an inverter of sufficient power to run your refrigerator(s), they could also be connected to your battery-wind farm.

A good project while at camp.

__________________
Bob
Register to Reply
Anonymous Poster
#8

reply for SB

01/13/2009 11:26 AM

let me explain to you the no-load SB.if you close the circuit breaker of the Generator and make it parallele with the grid, and you dont excite the shaft of it with any source like water, steam whatever, it is the no-load situ. I think you need some book-searching all the same, i hope u will get better information there...

Register to Reply
Anonymous Poster
#9

Re: Generator Loads and Output Voltages

01/13/2009 11:33 AM

I Mean you dont let extra amount of water or steam to the shaft and take any load from grid, i think Jinxnao is right, u wont get loaded without excite the shaft....

Register to Reply
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#10

Re: Generator Loads and Output Voltages

01/13/2009 11:50 AM

Connecting multiple 1 to 5 KW or so generators is going to be very difficult and require control changes that will make the project prohibitively expensive UNLESS you have Honda inverter type generators which are designed to be connected in parallel.

The Honda series in the link below and perhaps a few others are capable of this parallel connection feature. For an explanation see here: http://www.hondapowerequipment.com/products/generators/content.aspx?asset=gg_parallelcapability

This capability allows connection of two of the same type of generators in a network you construct to share load and maintain frequency. These generators are also much more fuel efficient than the common run of the mill Coleman, Troy-built, YouNameIt brand of gasoline, NG, Propane or diesel generators.

The most common result of connecting small generators (actually alternators) in parallel is that the voltage and frequency (speed) swing violently resulting in tripping or damage to one or both of the machines and perhaps the load equipment. If the engines have droop type governors and droop type automatic voltage regulators, some times they may actually parallel and share. Usually though, one takes or tries to take all of the load and the other slacks off and does nothing.

It the example of the first post, what happens if the energy source to the prime mover is lost, Well, one of two things happen. The generator trips off on reverse power protection or the machine continues to run at synchronous speed. If it is allowed to run at sync. speed then some power factor correction may be gained by adjusting the excitation to generate reactance to correct the power factor if needed.

Have FUN!
TT3

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#12

Re: Generator Loads and Output Voltages

01/13/2009 2:13 PM

Jinxnao,

If you reduce the input power (shaft) but keep the exciter power the same, the generator continues to act as a generator but with a different power factor, since both voltage and frequency are imposed by the grid it generates to. The reactive power remains quasi at the same level, while the active (real) power drops.

The input power (mechanical) accounts for the active (real) output power component and also for losses (windings, mechanical, etc) inside the machine. If the excitation power is taken from the generator (self-excitation), this also adds to the real power requirements.

When reaching a minimum level of power input, when the input power no longer is able to cover the losses inside the machine, the machine changes its characteristics from a synchronous generator to a synchronous motor (it starts turning the turbine/driving engine). The power factor of that synchronous motor is again dependent on the level of excitation power. The voltage and frequency are set by the grid.

__________________
Scientes et audaces fortuna juvat !
Register to Reply
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#14

Re: Generator Loads and Output Voltages

01/14/2009 12:05 PM

There is another consideration if the prime mover is a steam turbine. If the steam is cut off to the driving turbine, there will be no steam flow through the turbine and the windage losses from the rotor fanning the trapped steam will gradually heat up the machine until it gets so hot the rotor, housing and bearings are damaged. This is why steam turbines connected into a multiple machine network or to the grid always have reverse power protection.

I have seen both induction and synchronous types of turbines glowing from the heat of the trapped steam heated by the windage losses. More than a few machines have been damaged or destroyed this way.

Happy New Year!
TT3

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#15

Re: Generator Loads and Output Voltages

01/14/2009 3:23 PM

hii. İ GOT MY ANSWER FROM MY SEARCHİNGS. all my friends missed the point but only tomad got near it:) thr answer is while my generator is operation on no load and coupled to the grid if i reduce my driving power it will act as if it was a motor. İn fact tomad just overexplained it:) THank you all....

__________________
jinxnao
Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#16
In reply to #15

Re: Generator Loads and Output Voltages

01/15/2009 6:20 PM

Seems that you didn't read post #1? I tried for simple, same answer. Ah well, glad you got what you needed.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#17
In reply to #16

Re: Generator Loads and Output Voltages

03/05/2009 6:57 AM

ah you are right excuse me...

__________________
jinxnao
Register to Reply