Cable lenght -250Mtr
Load in amp - 163Amp
What is voltage drop
What is the cable size
Re: cable sizing
01/12/2009 2:53 PM
I dunno......Depends on the type of cable!!
Good Answers: 22
Re: cable sizing
01/13/2009 5:55 AM
resistance of your length of cable will be:
r=ρl/a
where ρ is the resistivity of the medium (probably copper, in which case 1.75E-08)
l is the length in metres
a is the cross sectional area of your cable (in square metres).
The voltage drop will be v=ir, where i is your load amps.
You can see that for a long cable, its thickness is the key to a low voltage drop at high amps - tradeoff is that copper is not cheap...