Anonymous Poster

Preventing Relay Contacts from Burning

01/22/2009 6:15 AM

Hi to all

We are using relay contact in some switching circuit but during turning off the load, spark takes place and relay contact damaged frequently.

although we have used frewheeling diode across load, RC network across relay contact, and even we have used MOV across the contact even though after some switching operations relay contact get damaged fully and relay required to be replaced, can i have some imformation regarding appropriate damping circuit which is likely to be connected across relay contact to avoide such burning,

Best regrads

Divyesh patel

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Burning of Relay contact

01/22/2009 6:38 AM

What voltage & current are you switching? AC or DC? What is the load? If inductive (as I suspect), what is the inductance?

Also, do you have coil suppression? The wrong sort can slow down the relay action, and make arcing worse.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#2

Re: Preventing Relay Contacts from Burning

01/22/2009 9:36 AM

How about using a zero-crossing solid-state relay?

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Active Contributor

Join Date: Jan 2009
Location: Singapore
Posts: 10
#3

Re: Preventing Relay Contacts from Burning

01/22/2009 9:30 PM

Look like over loading of the contacts.

Reply
Associate

Join Date: Jul 2007
Posts: 41
#4

Re: Preventing Relay Contacts from Burning

01/22/2009 11:17 PM

How does blowout coil problem or a dirty or improperly mounted arc chute . both which will effect arc quenching .

Another thing that might happen is contact opening slowly due to a brass shim been worn or missing at the pivot on the coil armature .

Just a couple of thoughts of what I have run into at 3 in the morning........r

Reply
Power-User
United Kingdom - Member - New Member Engineering Fields - Transportation Engineering - New Member Technical Fields - Marketing/Advertising - New Member Hobbies - Target Shooting - New Member

Join Date: Sep 2007
Location: South coast of England
Posts: 411
Good Answers: 36
#5

Re: Preventing Relay Contacts from Burning

01/23/2009 4:19 AM

If you are in a environment with high levels of RF (for example very close to large transmitters or antenna systems) this can also lead to contact burning. Alternatively if the relay is in a corrosive atmosphere it will accelerate contact erosion. However as others have said, it is most likely due to inadequately suppressed inductive loads.

Reply
Anonymous Poster
#6

Re: Preventing Relay Contacts from Burning

01/23/2009 4:22 AM

Hi

relay contact is used for swithcing of DC load having R of 43 ohm, inductance is about 300 mH, and supply voltage is 135 V dc

Arc chute can not be provided as it is very small PCB mounted Relay,

Best regards

Divyesh patel

Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#7
In reply to #6

Re: Preventing Relay Contacts from Burning

01/23/2009 4:36 AM

What is the make/part number of your relay? As I've found recently, getting a relay or contactor rated for DC inductive loads can be quite a problem.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Anonymous Poster
#10
In reply to #6

Re: Preventing Relay Contacts from Burning

01/23/2009 10:08 AM

Check the rating of the relay to make sure it is properly rated for your application. The PCB mount may make it difficult to upgrade. Some manufacturers have spacial alloy contacts for inductive or cold lamp inrush loads. The 135 VDC supply is about 70% more erosive to the relay contacts than AC because it is always interrupting the full 3A load current @ 135V. A suppression diode across the inductive load will minimize the back EMF voltage spike as the contacts open, but this alone may not be enough to obtain the desired life. If you can not upgrade the relay, you may want to make it a socket mount to al least make it easy to change. Otherwise - back to the drawing board!

Reply
Power-User

Join Date: Apr 2005
Location: Scotland
Posts: 164
Good Answers: 8
#8

Re: Preventing Relay Contacts from Burning

01/23/2009 5:07 AM

I have a similar problem with the relays fitted in petrol pumps. They switch 240Vac motors and solenoid valves at about 6A. Although rated at 30A ac the contacts burn out or weld together after a few months and I have a large box of scrap relays as a result. A more important side effect is the 'splash' of RF noise caused by the arcing which is picked up on the nearby 5vdc tracks and this often corrupts the CPU memory! The only way to overcome this problem is to fit a good solid state relay. They are more expensive but work out cheaper when you consider the cost of 'down time', engineer's travel/work time, repair cost and the cost of holding spare boards to carry out the replacement at first line.

I wish equipment designers would sometimes listen to the maintenance people rather than the Company bean counter.

Reply
Anonymous Poster
#11
In reply to #8

Re: Preventing Relay Contacts from Burning

01/23/2009 10:15 AM

Bill's suggestion for a solid state relay having zero volt switching is not only a good idea for relay life, but also for safely keeping a 6A 240V arc away from petrol pumps - yikes!

Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#12
In reply to #11

Re: Preventing Relay Contacts from Burning

01/23/2009 10:53 AM

Zero-crossing is O. K. for AC but doesn't apply for DC, although as kilowatt0 suggested in another post, this SSR from Futurelec should work.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Guru

Join Date: Jun 2007
Posts: 719
Good Answers: 25
#9

Re: Preventing Relay Contacts from Burning

01/23/2009 10:08 AM

Many years ago, and for low current applications,
we used a "contact oil" to prevent arcing.
This was extensively used to good effect.

I have no further info. on the oil, and would suggest a
little research and/or contacting some oil suppliers for
this type of oil as a possible solution?

e.g. http://tetra.jp/eci/ecieng/05eciseihin.htm

Hope this helps.

jt.

Freedom is in the mind; don't let anyone take that away.

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#13

Re: Preventing Relay Contacts from Burning

01/23/2009 11:11 AM

Three amps on a little relay could easily be the single factor that is your problem. As others here have identified, check your relay specifications. Many relay manufacturers state a maximum interrupt current specification for their relays. Make sure that your reverse biased diode is across the inductive load side of the circuit and rated for not just the reverse breakdown voltage but the three amperes that it will briefly handle. I also recommend that this diode be a Schottky diode to minimize the turn on time. (This is not the diode across the relay coil.) Lastly, during the diode turn on lag, a snubber capacitor in parallel to the diode will instantly handle the inductive current. A rule of thumb hand wave will be to double the diode turn on time for dT, double the diode turn on voltage (1.2V) for T and calculate C by C=I*V*dT. However, adding a capacitor for snubbing in some configurations can actually hurt your relay contact because depending on the source impedance, on contact closing the surge current to charge the capacitor can now exceed the current rating while the contacts bounce.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Power-User

Join Date: Apr 2005
Location: Scotland
Posts: 164
Good Answers: 8
#14

Re: Preventing Relay Contacts from Burning

01/23/2009 11:37 AM

Some additional information for the discussion, the large box of burnt relays I've collected are from PCBs which do have snubbers, diodes, etc. They are made by Potter&Brumfield, Schrack, Omron and IMO so the only common factor is the repeated switching of an inductive load. Probably petrol pumps are the worst case as the motors switch on and off every few minutes, day after day! I had one relay which 'torched' and burnt all the components off the board within 6" of the relay, fortunately just outside the explosive zone area!

If you read the specs for solid state relays they recommend Zero-volt switching for resistive loads or motors where the power factor is greater than 0.8 and Random switching versions for inductive loads with power factor less than 0.8.

The only draw-back with SSRs is the large amount of conducted noise they make which spoils the EMC compliance somewhat. Even this can be overcome as I have developed a new SSR which is well within the EMC limits at 240Vac 80A, (full patent and EMC certification). A 440V version should be ready for sale at the end of March.

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#15
In reply to #14

Re: Preventing Relay Contacts from Burning

01/23/2009 12:08 PM

Tom,

I presume that you are not the guest who originally posted this problem. For your case, running AC motors a capacitor or better a resistor and series capacitor in parallel with your motor load will doing the snubbing quite well. The snubbers do not have to be mounted on the relay board or near the motor so space should not be too critical of a problem. Since you have an explosive zone, I recommend fixing this before things go bang.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Power-User

Join Date: Apr 2005
Location: Scotland
Posts: 164
Good Answers: 8
#16
In reply to #15

Re: Preventing Relay Contacts from Burning

01/23/2009 3:11 PM

After 30 years running a service operation with over 4,500 busy petrol stations I think I have seen every type of petrol pump design ever made since the last war and even earlier. Every manufacturer has used an electric motor to drive the pump and they all use a relay of some sort to switch the load. Some motors have relays built inside plus capacitors and additional centifugal switches, some have the relay on the power supply board in the top of the pump. They use snubbers, diodes, electromechanical and solid state relays. All I can say, in answer to the original question is electro- mechanical relays have a much shorter lifespan and are prone to contact arcing. If the motor is used infrequently, switched on for long periods or has a resistive load there should be no problem, but for repetitive switching of inductive loads you really need to consider an electronic switch such as the solid state relay.

Reply
Power-User

Join Date: May 2008
Posts: 380
#17

Re: Preventing Relay Contacts from Burning

01/23/2009 8:32 PM

There are every kind of electronics components for this and may be a RC circuit needs a so big capacitor to be useful (.5*L*I**2=.5*C*V**2,where V is voltage you accept on ),a very small component used i think was varistors its name,no any electronic supplier,just power electronic supplier for industry should offer you the best for this problem.-

Reply