What you have is two different specs on the valve. The 300 psi is max pressure rating of the valve. The 3-15 psi is the pressure needed to the pneumatically actuated port to shift the spool in the valve. The actuation pressure will vary between 3-15 psi depending on what the pressure is at the valve body inlet port.
__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Re: Valve Control - Process Pressure and Standard Pressure
01/23/2009 10:07 PM
Compare the area of your actuator's diaphragm and the area of the valve's plug.
Let's say your valve plug is 1 sq. in. and your diaphragm is 255 sq. in. 300 psi on your 1 sq.in. plug is 300 pounds. 15 psi on your diaphragm's 255 sq.in. is 3,825 pounds. The diaphragm, therefore, has more force to push or pull the valve plug even when 300 psi is acting on it.
regards,
Vulcan
__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Re: Valve Control - Process Pressure and Standard Pressure
01/26/2009 6:34 AM
It depends upon the specific design of the valve, so it is not possible to describe it mathematically without focussing on a particular valve. Vulcan's description is satisfactory.
Valve manufacturers take all the aggro out of things like this by providing the fullest of information about the valve so as to make selection a simple matter.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Re: Valve Control - Process Pressure and Standard Pressure
01/25/2009 8:12 PM
Hi, I agree with Vulcan.Some valves have "vented" plugs, with this type
of plugs the pressure is equalized on the top and bottom of the plug
requiring less force to move the valve's stem
Re: Valve Control - Process Pressure and Standard Pressure
01/26/2009 1:10 AM
Hi all,
As stated above it is area. F=MA, i.e. Force = Mass * Area.
No more no less. This is part of actuator sizing. Try to get hold of the Fischer control valve handbook. You can download it for free from the Emmerson web site. If you read it - you will get the answers you are looking for.
You can also do a search on google for control valve actuator sizing :)