Motor Fuse Size and Overload Settings

01/26/2009 5:18 PM

Hi

I have a 132KW 415v 3 phase motor in a compressor

I would like to know what size fuses should I run with it ?

I have been told that the FLC divided by route-3 to set the overload

is this also the amps that i should get the fuses with?

as the FLC for the motor is 132 000 / 415 = 318 approx

do i get 350A fuses ?? or go for the overload setting ???

I have 120mm PVC SWA PVC XLPE cable feeding the motor direct from a 500A switch with 300mm feed existing from transformer and i want to mainly protect the new 120mm cable as the motor has protection in the compressor control panel its star delta start if this helps

Cheers for any help :)

__________________
lost.instro
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: motor fuse size and overload settings

01/26/2009 6:22 PM

You should check the name plate for the Full Load Amps(FLA). If you must use the

132 kw, the approx amps = 132 kw/(.415 x 1.73) = 184 amps. IF you apply the power factor the amperage will be higher. Using a PF of 0.80, the FLA is 230 amps. What is the ampacity of you conductor? You need to go by the local code for this information if you have a code.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: motor fuse size and overload settings

01/27/2009 1:30 AM

On a Star-Delta starter, you size the over load relay at 58% (1/1.732) of the motor nameplate FLA because you are using 6 leads going to the motor, and only 58% of the current goes through the main set of conductors (connected to the main contactor).

But the fuses supply the entire motor circuit and are located ahead of where the power splits to the Delta and Star contactors, so fuse sizing must be based upon the entire motor FLA. You are obviously not in the US, so I cannot help you to size the fuses because that will depend on your local codes, but again, the basis is the entire motor FLA, not the lesser amount associated with the OL relay.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: Sep 2008
Location: Mount Isa
Posts: 22
#3
In reply to #2

Re: motor fuse size and overload settings

01/27/2009 11:37 AM

i have decided on what cable to use i just want to know is why you can't just use 132000/415 to work out the current ??

__________________
lost.instro
Register to Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#4
In reply to #3

Re: motor fuse size and overload settings

01/28/2009 3:44 AM

lost.instro,

how long have you been working in that your work now ?

for 3 phase motor as you state before, we MUST devide with square root ( three ), that is about 1.73 for calculating current.

tx..

regards...

Register to Reply
Active Contributor

Join Date: Sep 2008
Location: Mount Isa
Posts: 22
#6
In reply to #4

Re: motor fuse size and overload settings

01/28/2009 12:11 PM

thanks for all your help i have sorted it out :)

__________________
lost.instro
Register to Reply
Anonymous Poster
#7
In reply to #6

Re: motor fuse size and overload settings

06/17/2010 2:51 PM

active power = square root 3 times rated phase-to-phase voltage and also times phase to phase current of your device, multiplied again by power factor. in your system, it is 132kw=√3 *415V*I*0, then u can have the current.

Register to Reply
Anonymous Poster
#5

Re: Motor Fuse Size and Overload Settings

01/28/2009 10:31 AM

To calculate the Full load Current In 3 phase Suply as Follows.

Power =root3 XVLXILXcasphi

IL=132X1000/415X0.9 :353A.

You can Put the fues rating is :360Amps.

Thanks& Regards

P.surendra

Email:suresh6792000@yahoo.com

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Motor Fuse Size and Overload Settings

04/16/2025 5:25 AM

A <...Fuse...> is there to protect the wiring.

<...have been told...>

Circuit protection is covered under the topic of co-ordination, and can be found in the applicable national electrical standard prevailing; in the UK, for example, BS7671 applies.

If in doubt, consult a qualified local Electrician, who will design, select, install, test and certify as safe the installation being considered under the standards prevailing in the country of installation.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 8 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); elect-ok (1); JRaef (1); lost.instro (2); PWSlack (1); wareagle (1)

Previous in Forum: Size, Length and Wire Resistance   Next in Forum: Magnetoconductivity Resistance in LV Power Cables
You might be interested in: Fuses, AC Motor Starters, Motor Starters and Contactors

Advertisement