Parallel Transformers

01/28/2009 2:30 AM

Can we parallel 2-idenrical transformers {each 2000 kVA / (20 kV/0.660 kV Voltage ratio ) / 6.5 % impedence / 50 Hz / 3-Phase / Dyn11 vector group/ } from the same one incoming hight voltgae feeder and supplying to same one out going low voltage feeder to cater the toatol load not exceeding 2000 kVA ( capacity of one Tr. ) to avoid running one TR. with high temperature and aslo to increase the life . Though the system will have more No-Load losses. This system will be for short time for few months till we receive higher capacity single Tr.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Sep 2008
Posts: 31
#1

Re: Electrical-Transformer

01/28/2009 5:33 AM

Yes you can. Need a synchrony transformer device. It is simple compare to synchrony generators.

Register to Reply
Commentator

Join Date: Jan 2009
Posts: 62
Good Answers: 4
#2

Re: Electrical-Transformer

01/28/2009 6:29 AM

Yes it is possible. However, be aware that the fault current at LV side will increase. You may have to reconfigure the protection system.

If you're transformers have OLTC's then you'll need a synchronizer to synchronize the changing of taps. Same OLTC's doesn't mean they will behave the same way when their txfrs are paralleled. Each OLTC will always behave differently even if the two are of the same brand, type, rating, etc. That's just the way they are.

__________________
Patriotism is the last refuge of scoundrels
Register to Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#3
In reply to #2

Re: Electrical-Transformer

01/28/2009 6:39 AM

are you brother with JRAEF? because i see your avatar picture is same

Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#4

Re: Parallel Transformers

01/28/2009 8:24 AM

Please be aware that failure of one protection device on single transformer will result in overload of other transformer, so protection devices must be slaved to each other.

Also, just because impedance is 6.5% on nameplate, it doesn't necessarily mean that the number is exact, and if they are indeed not identical transformers one will be a slight load on the other. Temperature monitoring and incorporation into protection circuits is recommended.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Anonymous Poster
#5

Re: Parallel Transformers

01/29/2009 4:34 AM

A paper mill I am working at is currently installing 2x 20 KVa transformers in parallel. Each will be at half load, so loss of one will not affect the mills capacity. This is due to lead in times of order a replacement.

Register to Reply
Commentator

Join Date: Oct 2007
Location: Caribbean
Posts: 79
Good Answers: 2
#7
In reply to #5

Re: Parallel Transformers

01/29/2009 7:57 AM

But you have independent switchgears. In the first case mention here , he is electrically paralleling using single swichgear on primary and secondary sides.

__________________
Learn more, Do more , Be more
Register to Reply
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#6

Re: Parallel Transformers

01/29/2009 7:54 AM

If your company has the funds, it might be better to parallel the two 2000 KVA xfmrs in a redundant format rather than replace them with a new single xfmr. This would give you the ability to take down a certain amount of equipment and maintain or repair it without taking down your entire facility. The question would be the cost of new equipment over the cost of a new large xfmr and how far you want to take the redundancy.

Register to Reply
Register to Reply 7 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Bill (1); dbt (1); djacob (1); elect-ok (1); GRAY HAIRED OLD GOAT (1); myn1996 (1)

Previous in Forum: Temperature Measurement Circuits in Power Systems   Next in Forum: Motor & motor skid grounding
You might be interested in: KVA Meters, Transformers, Electronic Transformers

Advertisement