Motor & motor skid grounding

01/28/2009 2:44 AM

hi,

i have confusion how to ground motor and motor skid followinf are the situation

1)motor body is directly grounded form ground grid conductor

2)there is a insulated vibrating pad installed between motor and skid

my question 1)do we need separate grounding connection from main ground grid or we can jumper skid from motor ground point which is already connected to maing ground grid kindly reply me based on NEC requirement

i have another problem

we have ground grid cable run all over plant,motor body is connected through ground grid cable.

As per above condition do we need separate ground conductor from source for motor protection,kindly reply based on nec.

thanks,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Motor & motor skid grounding

01/28/2009 6:08 AM

Supplementary earth bonding is usually carried out strictly according to the wiring codes prevailing in the country of installation.

It would be rather unwise, in principle, for the earth bonding conductor to have a lower cross-sectional-area than each phase conductor!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Active Contributor

Join Date: Jan 2009
Location: doha ,qatar
Posts: 16
#2
In reply to #1

Re: Motor & motor skid grounding

01/28/2009 6:30 AM

thanks for replying but your reply to question not clear kindly expalin me more for ur information we base our inspection as per NEC code here in qatar

thanks

Reply
Member

Join Date: Oct 2008
Posts: 5
#3

Re: Motor & motor skid grounding

01/28/2009 9:30 AM

1) you can jumper the skid as long as "connected together and to the electrical supply source in a manner that establishes an effective ground-fault path"

2) yes you need an equipment ground conductor from source overcurrent protection device to motor

Reply