Reclosing and Relay Protection

02/06/2009 3:03 PM

Hello,

I am confised by the term "Reclosing" for protecting overhead line and underground cables etc...

I would appreciate if you could define the term "reclosing" in the above context of protection.

Thanks

mrelay

Register to Reply
Pathfinder Tags: protection Reclosing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Re closing and Relay Protection

02/06/2009 4:17 PM

This is my understanding:

After initial breaker trip, the circuit is re energized by automatically "re closing" the breaker. This can happen twice, before the circuit is shut down permanently.

In the case of a momentary short, such as a tree limb falling across the line, the re- closer saves the repairman a trip into the field, the circuit is back on line, and the customers are happy.

Register to Reply Score 1 for Good Answer
Guru
Hobbies - Car Customizing - Dances with Trees Canada - Member - because I can Hobbies - CNC - too much fun Hobbies - Target Shooting - paper shreader

Join Date: Mar 2008
Location: Ottawa, Ontario, Canada
Posts: 769
Good Answers: 10
#2

Re: Reclosing and Relay Protection

02/06/2009 5:10 PM

What Lyn said. the recourse can however close several times depending on the pre-sets determined by the utility. The second jolt can be handy if a small branch falls across the phases, the branch actually jumps off the line. Isn't it nice all those years working for an electrical utility is finally coming in handy.

__________________
Kevin "Dances with Trees" Willey
Register to Reply
Active Contributor

Join Date: Feb 2009
Location: Warner Robins, GA
Posts: 16
Good Answers: 1
#3

Re: Reclosing and Relay Protection

02/10/2009 10:03 AM

This is a little late, but to add to what the guys stated:

When there is a short in the line, the current goes high in the part of the line experiencing the fault. This high current goes through a big solenoid that pulls the switch open and clears the fault. When the current goes away a spring (which opposes the magnet), lets the switch close and, if no high current is available, everything goes back to normal. If the fault is still there, it will open again. Depending on the settings, it may open and close up to four times before it stays open. Users on the line may notice that the lights go on and off twice quickly and then twice more with more time on for the last two. The counting is done by using the insulating oil that is inside the switch with a chamber which is pumped full of the oil as the plunger is pulled into the magnet each time there is a fault. The chambers are arranged to give one timing for the delay for the first two faults and slower timing for the last two faults. This allows the line to break and drop a "minor" shorting source (goodbye Mr. Squirrel) and possibly be able to recover without blowing a fuse and requiring a visit from your local utility lineman.

I worked with a system like this and was impressed with how much is being done...

Register to Reply Score 1 for Good Answer
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Dances with Trees (1); Farmers Son (1); lyn (1)

Previous in Forum: Which is better-M.Tech in electrical or electronics ??   Next in Forum: Difference between Leakage,Earth and Residual current

Advertisement