Equipment Grounding Conductor - Required or Not?

02/10/2009 12:40 AM

Is it require the equipment grounding conductor between transformers and low voltage switchgear, switchgear and Auto transfer switch and Motor control centre to the motors if all the equipments already grounded with same grounding mesh of the plant.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#1

Re: Equipment grounding conductor required or not

02/10/2009 2:08 AM

Not sure about what you mean. All the equipments are already grounded. If your ground is of sufficient capacity, you do not again connect the ground (or earth wires) above ground why should you? We have a large factory where each individual machine has its own earth pit and they are grounded there - why carry another extra cable and connect each earth pits ?

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: Equipment grounding conductor required or not

02/10/2009 7:52 AM

In which jurisdiction will this equipment be installed? Read the codes for your area!!

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#3
In reply to #2

Re: Equipment grounding conductor required or not

02/10/2009 9:50 AM

Also make sure you understand the differences between grounding and bonding and the requirements for each. It can be important; particularly under ground fault and surge conditions; such as lightning discharge.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Equipment Grounding Conductor - Required or Not?

02/10/2009 11:32 AM

Quote by SB "

"Not sure about what you mean. All the equipments are already grounded. If your ground is of sufficient capacity, you do not again connect the ground (or earth wires) above ground why should you? We have a large factory where each individual machine has its own earth pit and they are grounded there - why carry another extra cable and connect each earth pits ?"

SB

would you describe what you mean by "earth pit". In the US a piece of equipment is grounded by an equipment grounding conductor(EGC) that is electrically connected to the main switch and electrode grounding conductor. Connecting equipment to earth is not allowed as a replacement to the EGC. A phase to ground fault would not trip a breaker if the earth was the only return path for the fault current.

Register to Reply
Member

Join Date: Feb 2009
Location: Doha Qatar
Posts: 9
#5
In reply to #4

Re: Equipment Grounding Conductor - Required or Not?

02/11/2009 12:18 AM

Mr. SB I appreciated your answer In our case all equipments are inside the building and earth pits are located outside the building but all earth pits are connected with 120mm2 electrode grounding conductor pvc sheathed (5*5 meter) mesh below grade level and near each equipments grounding riser tapped through cadweld joints.In case of phase to ground fault the current will not flow through earth, it will flow through electrode grounding conductor,Each equipments ground are interconnected through electrode grounding conductor. Is it required the equipment grounding conductor for above case.

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#7
In reply to #4

Re: Equipment Grounding Conductor - Required or Not?

02/11/2009 2:17 AM

In our factory all the machines are having individual earth (and pit) that checked up- 2 for each machine/

However after your post had a doubt and checked the local codes and also IEC- yes we should have had a earth mesh - got to find out what loophole of the code we have used or the specific code is not applicable under this much of heavy load (when each machine is forced to have its own full set of protection).

No earth mesh is sure (the factory is under expansion and an extra bay is added and since it is in front of our eyes i could see that there is no grid).

Catch the Electrical Safety officer of the factory. Especially i am unfortunately the HSE co-ordinator for the microcosm. (Enquiry under progress, the report will be submitted soon - as you are aware enquiry commission take a couple of years to complete the task so it will be soon enough).

Will keep you posted.

PS: WE - seen your mail, but my firewall (office) do not permit me to open linked-emails (may be passing on some through them, at least that is that they think)

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2007
Location: Transcendia
Posts: 2963
Good Answers: 93
#6

Re: Equipment Grounding Conductor - Required or Not?

02/11/2009 1:17 AM

Have you taken a meter and checked to see what shows on the wires between the neutral and the ground? If the overall system, circuit is well grounded it ought not be necessary to ground individual components on that system. However when running lights I have had cases in heavy rain, when the ground for the circuit system was not good enough, and we all got bites. It is not at all unusual for grounding of a system to be inadequate. I suggest you get an electrician to meter all phases and see what is running in the wires and where it is going. I also suggest you make sure all phases are as balanced as practical. Regardless, grounding is good.

__________________
You don't get wise because you got old, you get old because you were wise.
Register to Reply