Parallel Fusing

11/07/2006 5:51 PM

In the transformer protections by different transformer manufacturers, parallel fuses are used to protect the transformer. My question is these fuses are just redundant (but I don't think, they improve reliability, because unless both open there will be a fault current path through the other) so is not advantage to have two fuses in parallel, so could someone explain to me what is the theory behind it? Thank you.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Apr 2006
Location: USA
Posts: 252
Good Answers: 6
#1

Re: Parallel Fusing

11/07/2006 6:05 PM

Fuses are used in parallel to increase their rating. For instance, it is acceptable to put (2) 2000A fuses in parallel to protect a circuit rated for 4000 amps continuos.

There are codes and guide lines that need to be followed to ensure fuses share the load evenly.

The practice is used to save money since it may be that a 4000 A fuse costs more than (2) 2000A fuses.

Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#2

Re: Parallel Fusing

11/08/2006 12:54 AM

One fuse gone means both fuse gone.

becoz second fuse can not servive even for seconds, once first one is fused.

normally they carry 50% of of total current and if one fuse gone 100% of current will pass by second one and make it burnt.

its perfectly ok to use them in II if used correctly.

Reply
Active Contributor

Join Date: Nov 2006
Posts: 11
#3

Re: Parallel Fusing

11/09/2006 4:09 AM

There is no issue in parallel fusing, if selected properly as per the load pattern. There is no risk of one fuse blown but the circuit will remain energised and can lead to accident because the second fuse also will be blown automatically within second as the total laod current will pass through that.

Use of fuses in parallel is done mainly to standardise the inventory.

Reply
Anonymous Poster
#4

Re: Parallel Fusing

11/09/2006 7:21 AM

In a parallel set of fuses where each fuse is half the "safety load", both fuses will blow every time

Reply