Designing a Simple Lighting Circuit

03/01/2009 11:47 AM

For a college project I decided to do a simple lighting circuit, however the more I have done the more interested and the further into it I have wanted to go. I have now got an Idea that I am going to run two lighting circuits in one area and use an impulse relay to switch between the two.

I have done a drawing trying to show the circuit but I dont know if I have drawn it correctly. Am I going in the right direction? I have never done electrical drawings like this before so am unsure of the correct way to draw certain things such as contacts and the impulse relay!

<img src="http://i205.photobucket.com/albums/bb51/danny_utch/HNC%20Project%20Bits/scan0001.jpg" border="0" alt="Photobucket">

My next question is I want to work out what protection to use and what size cable. For example if I was to use 12 x 16W lamps on one of the circuits. What dictates what protection I use and where in the circuit it will go. i.e shall I just put some kind of trip on the whole circuit or on each individual 'branch'? off the live? Is there anything on the net that gives a good explanation of what I would need to do to protect this circuit and select the right cable sizes?

This isnt going to be built, it is simply me being a little inquisitive. Thanks for any advice/information.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Tips?

03/01/2009 11:48 AM

the picture didnt work sorry lol,

http://i205.photobucket.com/albums/bb51/danny_utch/HNC%20Project%20Bits/scan0001.jpg

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Tips?

03/01/2009 4:51 PM

Your link is broken. Protection depends on the wire ampacity rating. You need to check the conductor ampacity according to your local code. The ampacity must be equal to or greater that the load. Example: if the conductor is rated at 15 amps, then you can use a breaker that has and ampacity of 15 amps or less.

Reply
Active Contributor

Join Date: Nov 2008
Posts: 17
#3
In reply to #2

Re: Tips?

03/02/2009 8:53 AM

why are you switching the neutral?

Reply
Commentator

Join Date: Feb 2008
Location: Virginia Beach, VA
Posts: 69
Good Answers: 6
#4
In reply to #2

Re: Tips?

03/02/2009 11:09 AM

WAR EAGLE!

Reply Off Topic (Score 5)
Reply to Forum Thread 4 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); jerryalan (1); Old Submarine Sailor (1); wareagle (1)

Previous in Forum: University vs. Institute   Next in Forum: Can a 48-year Old Novice Earn a PE?

Advertisement