Variable Speed Drives 2

03/04/2009 2:58 PM

Is the output of a variable speed drive protected against overloads and short circuits??? Do ordinay devices provide protection or do need to protect the cable that connects the VSD to the electrical motor with fuses and overload relays?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Variable Speed Drives 2

03/04/2009 3:22 PM

In general, the VFD does provide the protection for the motor circuit down stream, but not up stream. This is not however universal and should be checked out before assuming anything.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#2

Re: Variable Speed Drives 2

03/04/2009 9:59 PM

All VFD's must be fuse protected before power enters the VFD, doesn't matter it you are feeding from a power board, MCC, CB Panel. VFD must be protected.

__________________
"Real Bass Players" do not use picks
Reply Off Topic (Score 5)
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#3

Re: Variable Speed Drives 2

03/05/2009 5:14 AM

check the data with you vendor.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Variable Speed Drives 2

03/05/2009 2:47 PM

The VFD and the motor are only protected against motor overloads if the overload parameter in the VFD has been correctly set to the full load current stated on the motor nameplate.

In general, the cable downstream should be no smaller than the cable upstream of the VFD. The primary protection for the cables, VFD and everything else against the risk of short circuit damage remains with the circuit fuses.

Please refer to existing wiring diagrams for similar arrangements as examples of current practice.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 4 comments
Copy to Clipboard

Users who posted comments:

elect-ok (1); Jimh77 (1); JRaef (1); PWSlack (1)

Previous in Forum: Variable speed drives...   Next in Forum: Three phase electrical machines with no return

Advertisement