Generator Load Sharing

03/11/2009 6:24 AM

Hi to all,

Our system has 4 Cat.generators 3512(600V;1500rpm;1500kVA;1400A), they can all work in parallel (droop mode). To about 2/3 of load they all share kW,kVAr and amps equally, but than the gen.No.4 is trying to take most of the load on him self. This action from gen.No.4 is not acceptable, for our system,because he is going in the current limit.

We are using the Basler Electric, voltage regulator AVR 63-12 (droop mode), and for load sharing&speed control for diesel engine Woodward 2301A.

We are using PT transformers 600/120V for measuring and monitoring circuits(2 PT in Aron connection) and voltage feedback, the CT transformers are 2000/5A. The voltage effects on the kVAr, and the speed on the kW.

Our system is symetrical 3phase, mosty inductive loads (DC motors), IT system, sharing the kW is no problem but the kVAr is.

The question is how come the gen.No.4 is trying to take this load on him self?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#1

Re: Generator Load Sharing

03/11/2009 9:17 AM

Are you sure the zero load speed of the generators are set correctly ?

Suppose the zero load speed of the generator 4 is highr than others, then the other generators starts working as motors, till the droop of the generator 4 (by taking extra load) brings the system to the un-balanced loding pattern ?

Just a thought

Check the droop characteristics of the generators.

May be after the load (>2/3) the droops are dissimilar - Gen 4 has a flatter curve so it is trying to compensate for the others.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#2

Re: Generator Load Sharing

03/12/2009 5:30 PM

The suggestions by SB to check the droop settings on each machine and the no load speed setting are right on.

If the droop setting is smaller for #4 it will load faster than the other machines causing it to pickup proportionately more of the system load as load is applied and the speed droops below setpoint. There is also a droop setting in the AVR which could be causing you trouble. If the droop setting on one machine's voltage regulator is appreciably tighter than the others it will load picking up KVARs faster as the system load increases.

My guess is that you will find your trouble in either the AVR settings or Speed governor settings. If the settings are correct then you may have a malfunction in one or the other of those systems or an operator with fiddly fingers.

It would also be a good idea to make certain that the AVR for #4 is set up for droop or parallel operation.

Work Safe!
TT3

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
Participant

Join Date: Mar 2009
Posts: 2
#4
In reply to #2

Re: Generator Load Sharing

03/13/2009 3:36 AM

Thank you TT3 for Your suggestions,

we are gona try to see droop setting on each AVR, our AVR is analog so is very hard to put the switch on each AVR at same position.

The droop setting on AVR is 5% for full load, our frequency is 50Hz, and all AVR are set up for droop mode. Hopefully without ' fiddly fingers '.

Does anybody had come kind of experience with the Basler Electric, digital voltage regulator DECS-100? We are planning ti install them.

Register to Reply
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#5
In reply to #4

Re: Generator Load Sharing

03/13/2009 1:03 PM

While re-reading your original post, I noticed that the machines track up to a certain load. If I understand correctly, past that load, #4 begins to pickup more of the KVAr leading to it going into current limiting before the others. This could be due to a metering problem caused by a faulty CT. I have seen similar problems before. In my case it was found by using a clamp on Amp meter to read the CT currents for each phase and comparing them to measurements made on the leads leaving the generator. IF you have other CTs on the same phases, it is probably safer to measure the current on the second set of CTs and compare them to the CTs that provide current measurement to the AVR.

A CT replacement is usually a lot cheaper than an AVR retrofit.

I suppose a PT problem could lead to a similar problem but that is not what was found on the particular job I was working to resolve. While you have the tools out and the safety gear on, it might be a good idea to check that side of things also.

Work Safe!
TT3

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#6
In reply to #5

Re: Generator Load Sharing

03/15/2009 11:56 PM

When you said "gen.No.4 is trying to take most of the load", I am assuming it is KW load, however I don't understand what you meant by "sharing the kW is no problem but the kVAr is".

Though I am not an expert of Woodward 2301A but it seems that the governor of the 4th generator is set for Isochronous and other 3 generators are set for Droop. You can verify Droop/Isochronous setting details from the Woodward 2301A manual.

If the droop setting of a generator is Isochronous, it automatically shares the total changes of load. The load sharing of the generators with Droop setting has to be done with manual intervention with increase/decrease speed control switch or a separate load sharing system.

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Anonymous Poster
#3

Re: Generator Load Sharing

03/12/2009 11:36 PM

I think the droop setting of the 4 th Machine is not matching with other machines for loads upto 66 %.

May be settings are alright for loads beyond 66 %.

Register to Reply
Participant

Join Date: Jul 2009
Posts: 1
#7

Re: Generator Load Sharing

07/02/2009 11:14 AM

Pls confirm #4 is under Droop Mode.

- make sure droop setting for all gensets are same.

- there should be a load gain potentialmeter besides the droop potentialmeter. Make sure the load gain setting should be similar with others.

My suggesttion:

apply full load for the genset and measure the dc voltage at terminal load signal. This must be done for only 1 genset. Then using the same method to adjust another 3 genset.

At full load, load signal should read 6Vdc. If unable to reach 6v, try to adjust load gain until load signal reach 6Vdc. If there is impossible to apply full load to genset, you may try to get 50% load and the load signal should be adjusted to get 3Vdc.

This is to ensure all the genset having the load capacity.

If you have solved the problem, can you share your solution?