Hi to all,
Our system has 4 Cat.generators 3512(600V;1500rpm;1500kVA;1400A), they can all work in parallel (droop mode). To about 2/3 of load they all share kW,kVAr and amps equally, but than the gen.No.4 is trying to take most of the load on him self. This action from gen.No.4 is not acceptable, for our system,because he is going in the current limit.
We are using the Basler Electric, voltage regulator AVR 63-12 (droop mode), and for load sharing&speed control for diesel engine Woodward 2301A.
We are using PT transformers 600/120V for measuring and monitoring circuits(2 PT in Aron connection) and voltage feedback, the CT transformers are 2000/5A. The voltage effects on the kVAr, and the speed on the kW.
Our system is symetrical 3phase, mosty inductive loads (DC motors), IT system, sharing the kW is no problem but the kVAr is.
The question is how come the gen.No.4 is trying to take this load on him self?