Voltage question

03/14/2009 3:18 PM

I am intending to connect my wind generator to my house via a grid tied inverter.

The generator is the Hugh Piggot design (Axial Flux) which works very well at charging batteries. The generator that I have built puts out 48 volts (rectified to dc) at around 130 rpm. That is the rpm I would like to use as a rated speed but 48 volts dc is too low an input for any of the (certified) grid tied inverters I can find.

I can increase the voltage with more coil wire but most of the inverters require a minimum of around 200 volts dc. The high end of the voltage window is often around 600 volts dc, which I have no problem with.

It would be virtually impractable to wind the coils of my type of generator to fulfill this requirement.

Is there any other way round it. (maybe by using some special voltage controllers or something)

The end result that want is to be able to send 6 kw of electricity back to the grid.

My generator can produce the power easily.(The blade diameter is 6 metres).Its the voltage to the inverter thats my problem.

Register to Reply
Pathfinder Tags: Inverter input voltage
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Nov 2007
Posts: 62
Good Answers: 1
#1

Re: Voltage question

03/14/2009 10:49 PM

From this distance, and not knowing the type of generator/alternator you have selected, it is difficult to be specific.

However, the principles are clear. In an electric motor, torque is proportional to current and speed is proportional to voltage. The same applies to a generator, so if you need to increase voltage by a factor of 4, you need to increase the shaft speed by a factor of 4. You could do this with a gearbox or with a cogged belt.

Alternately, you could use a DC to DC converter that would output 200V DC to the grid tie inverter you have chosen. It could be designed to operate over an input voltage range of 24 to 48 volts, providing additional battery charging that would not be provided by a fixed gearbox.

HAVE FUN

Register to Reply
Power-User

Join Date: Oct 2007
Posts: 102
Good Answers: 8
#2

Re: Voltage question

03/15/2009 12:45 AM

The alternator you have could be modified by bringing out the three windings separately.Three bridge rectifiers, could then be connected, one to each winding, and their DC outputs connected in series. This will be worth a try if the alternator was delta connected, but less likely if star. You could wind, or buy, three (single phase) auto transformers to give adequate voltage to an appropriate rectifier.

You could alternatively collect discarded power supplies from personal computers and extract their 200V working mains rectifier electrolytic capicitors(you could buy new but recycling scrap is so much more worthy!). In the power supplies they are connected to "volt double" 117V inputs. If you volt double all your three windings and connect their DC outputs in series, you will have over the 200V for your suggested inverters. The six diodes and required capacity will depend on the altrrnator's power, rpm/ Hz, and if star or delta connected before winding separation.

My solar cells feed a nominal 48V to an Australian made "Latronics" grid connected inverter. I doubt that it has worldwide certification but it might be acceptable.

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#3

Re: Voltage question

03/15/2009 1:20 AM

THe DC DC converter I feel is better choice. However I am not sure why the line tied inverters can not invert from the 24V.

Got it you are outputting 250A @24V for the 6KW power. I feel this is too much current.

Better way is to transform the Votlage at the alternator outlet to high AC say 600V , rectify to DC then invert it ?

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru
Hobbies - Fishing -

Join Date: Feb 2009
Location: Burnt Ranch, State of Jefferson
Posts: 688
Good Answers: 20
#4

Re: Voltage question

03/15/2009 1:48 AM

There are a few US companies that make an export model inverter which is grid-tie and uses a nominal 12/24/48VDC input. I'd try Outback Power Systems. I think you'll need a battery bank to ballast the incoming current and a diversion load controller to dump excess current.

__________________
“Sometimes I wonder whether the world is being run by smart people who are putting us on or by imbeciles who really mean it.” -Mark Twain
Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#5

Re: Voltage question

03/15/2009 7:58 PM

Greetings miik999 ,

Whatever solutions we could suggest here on this forum will be overshadowed by the requirements of the grid owners.

Your local power supply company probably has a great deal of specific information on how and what is required to connect to their grid, and it's free for the asking.

If you plan to grid connect on the sly, we can't help you - it's simply dangerous and probably illegal, but mostly foolish since the grid owner will be happy to help guide you free if you just ask.

Regards, CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6
In reply to #5

Re: Voltage question

03/15/2009 8:24 PM

The original poster could theoretically kill a lineman if its not done correctly, or more likely blow up your equipment......

As You said, its simply not worth trying to do it wrongly......you won't get paid your money for the power for an illegal system either.....

I have heard that in some countries the equipment is not cheap though.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Commentator

Join Date: Nov 2007
Posts: 62
Good Answers: 1
#7
In reply to #6

Re: Voltage question

03/15/2009 9:18 PM

Mr Germany,

If your ref to the original poster is to jcrock, let me clarify. I agree with you that 200V DC can kill a lineman. However I did not suggest connecting that to anything other than the "grid tie inverter" of choice. I presumed when I wrote that, and I am clarifying it here, that the chosen "grid tie inverter" would be one with technology fully approved by the local utility.

Thanks for the opportunity to clarify. I have spent my 40+ year career seeking to make possible the safe and healthful use of hazardous processes and hazardous materials. I'd hate to deviate from that now.

JC ROCK

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8
In reply to #7

Re: Voltage question

03/16/2009 3:41 AM

It is amazing to me how some (overly?) sensitive people on CR4 react to a possible criticism, that I might add here for clarity "WAS NOT MADE NOR INTENDED!".......

I was actually only AGREEING with another poster (which was I replied/linked to him and him ONLY) and adding a few extra comments to his already (to my mind at least!) correct answer.

Either you cannot read English, or you cannot understand it properly, and can only write it!!!!

I personally cannot see the connection between my post and yours at all. If there, its pretty far fetched, maybe you are aware of something I am not?

Please understand, nothing I wrote was aimed at you personally, therefore its all in your imagination only......

Stop being petty and overly sensitive, it will help you considerably further in this life........

WAW !!! (A Very British comment!!)

There is also a US comment that partially escapes me "What a (**)ROCK of shit!"

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#9

Re: Voltage question

03/16/2009 3:59 AM

Again let the agony aunt intervene.

Let us not make it personalised or CL will close this thread .

As far as AG is concerned I don't know who he meant but OP is the original poster ie miik999 and not Jrock.

And a pre-cautionary comment need not be taken as a personal attack.

BTW: I too had commented like AG on an earlier thread where 700V was being played with by the OP. I still have misgivings about that thread whether to let him try out. So I can always support AG .

As on now the topic was moving smoothly without the OP interference or feed-back . Let us keep it thatway.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#10

Re: Voltage question

03/16/2009 4:07 AM

Assuming you are using an alternator, I still prefer using a transformer to go to higher voltage and then rectify it to DC - then invert on the line commutated inverter to AC.

Why do you rectify at lower voltage ?

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Jun 2008
Location: Waterford, Southern Ireland
Posts: 74
#11
In reply to #10

Re: Voltage question

03/16/2009 7:03 AM

SB are you suggesting to use a step up transformer after the generator and then rectifing the current to dc.Is that better than rectifing the current directly after the generator.Is it as safe ?.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#12
In reply to #11

Re: Voltage question

03/16/2009 8:45 AM

since you are working at 24V and 6KW, the current is quite high on DC side it is 6000/24 = 250A.

All the costs will go up at this amperes (conductors, diodes, etc all have to take care of the current). However even if you use a 220 V, it is only 27A , and no specific over insulation is necessary.

As far as safety is concerned, you are going to work in high voltage any way at the inverter level (for feeding to the grid)

so

a) Either you work in 24VAC/144A 3 ph -> 24VAC/250A DC(rectifier) -> Reqd DC (DC-DC Converter) -> Line commutated inverter -> grid

b) 24VAC/144A 3 ph -> Rectifier(24VAC/250A DC)-> (Line commutated inverter) 24V AC -> transformer (grid V to 24V step up)-> grid

c) 24VAC/144A 3 ph -> transformer (24VAC-> reqd HV) -> Line commutated inverter -> grid

The underlined area is the low V (hence safe) but high current hence costly.

the transformer + rectifier+ Inverter can be made as a single module.

Only problem as far as I can see is the charging of batteries in case you don't want to off load all the power to the grid and want to save some in the batteries but then why ?

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Commentator

Join Date: Jun 2008
Location: Waterford, Southern Ireland
Posts: 74
#13
In reply to #12

Re: Voltage question

03/16/2009 9:05 AM

Thanks SB Have you any experience with Axial Flux Generators ?.

I can wind the coils to produce higher voltage but there would be a limit which I dont know yet.

What way would you tackle the situation. Would you send the max allowed back to the grid and store the balance ,if any, in batteries.

If you were to do this how would you split the power between the inverter and the batteries. Would 2 inverters be needed or could the battery power be inverted by the same inverter.

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#14
In reply to #13

Re: Voltage question

03/16/2009 10:11 AM

I am sorry, no relation with these. I am only in MW generators that also in 100s.

What I am commenting on is from my long ago Electrical Engg knowledge (Esp power electronics, my major in MTech- MS for you)

There is no use of rewinding when a simple transformer can step up at a cheaper cost, provided the frequency is not very low. You can have the number of poles in your gen to have an acceptable frequency (lower frequency will make the transformer not work properly)

If the line commutated inverters are used, there will not be any balance, (however will your electricity supplier pay for your feed-back ?)

The one way (if you are storing for your rainy day- we have power cuts, but you don't have them- at least thats what people say) is to store at 24V stage, then use a normal inverter (line commutated not bnecessary, since there is no line) to light your home. The rest can be fed to the grid. That way you are independant of the grid as far as your home lighting is concerned.

ie

Gen-> rectifier (24V DC)-> battery-> Inverter -> Home

-> transformer-> rectifier-> line commutated inverter-> leftout power to grid

(free of cost ? )

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#15

Re: Voltage question

03/16/2009 10:14 AM

BTW another link is active on Feeding the Grid.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Commentator

Join Date: Jun 2008
Location: Waterford, Southern Ireland
Posts: 74
#16
In reply to #15

Re: Voltage question

03/16/2009 1:08 PM

SB what do you mean (BTW another link is active on Feeding the Grid.)

Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#17
In reply to #16

Re: Voltage question

03/16/2009 2:00 PM

check this one

http://cr4.globalspec.com/thread/34730/Feeding-the-Grid

There directly the alternator is being output to the grid. It is not like you. However there are some discussion about the regulatory mechanism.

I prefer the line commutated inverters of you, since the DC link will have more stability on the system.

But keep a watch on that only since some discussion on the feeding and regulatory mechanism too are on. Most of the CR4 members look to be not watching this link. Why ? I dont know.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Off Topic (Score 5)
Guru
Hobbies - Fishing -

Join Date: Feb 2009
Location: Burnt Ranch, State of Jefferson
Posts: 688
Good Answers: 20
#18
In reply to #17

Re: Voltage question

03/16/2009 8:00 PM

Hi there

I'm not sure what the specs are on the Irish grid, but if this was a set-up for the US, I'd have a pair of 3.5kVA inverters (Outback GFX3524) a MX-60 charge/load controller (or other suitable diversion load controller) and as many L-16H (6 V) batteries as I could afford (minimum 4). This would give me 3.5 kVA @ 240VAC or 7kVA @120VAC with a grid-tie and a back storage bank for when the grid goes down, and, where I live, it will go down. Series/Parallel inverters can be fed by two 125amp feeds instead of 250 amps. The more you step up/down the current the less efficient the system is.

Chris

PS I set up small off-grid/grid-tie systems for a living.

__________________
“Sometimes I wonder whether the world is being run by smart people who are putting us on or by imbeciles who really mean it.” -Mark Twain
Register to Reply
Commentator

Join Date: Jun 2008
Location: Waterford, Southern Ireland
Posts: 74
#19
In reply to #18

Re: Voltage question

03/17/2009 5:07 AM

Hi Lightasmass, In Ireland it is 220v @ 50hz.

The grid will only accept 6kw max from domestic users. They pay 19 cents to the supplier whereas the normal cost of electricity is 16 cents to the general public, therefore it makes sense to send back as much as possible to the grid.(up to 6kws)

My target audience are farmers who use a lot more than 6kws. I was hoping to design a system in such a way that the power from the generator could be split. Some to the 6kw grid tied inverter and the balance possibly to batteries . My thinking is that if the farmer say uses 10kw or so, he could store the 4kw in batteries. This 4kw could always be used first before having to draw from the grid, therefore he may have free electricity.

It is probbably a stupid idea or do you think it might be possible and what would be needed.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#20
In reply to #19

Re: Voltage question

03/17/2009 9:23 AM

If your grid is ready to accept the power and pay for it, why will it be stupid ?

(If you pay back 6KW to grid and draw the same you gain 3cents/KW is it like a PMM ? )

Any way lighter side aside. I feel you have a running idea- with a load controller, you can divert to charge the batteries, but check the amount of battery bank required.

If you have a 10KW gen, and based on the wind condition (that you must know), the average load- generation should balance out in the way

Average Load - Average use <= 6KW

Also (Max generation-6KW) has to be matched by the battery bank. The battery bank can be used only to smoothen the power flow (like an electrical fly wheel) to avoid overcharging it.

I don't see technical infeasibility, but I don't know the commercial part.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru
Hobbies - Fishing -

Join Date: Feb 2009
Location: Burnt Ranch, State of Jefferson
Posts: 688
Good Answers: 20
#21
In reply to #19

Re: Voltage question

03/17/2009 2:16 PM

Not stupid at all. The systems I set up essentially prioritize the battery bank and then the grid. When the batteries reach bulk charge the excess is "dumped" to the grid. If the grid is down, you have a diversion load to take the excess, ie H2O heater. The inverters can be set for the amount to sell back, etc....

Here the utility will only cancel your power usage, not pay out.

__________________
“Sometimes I wonder whether the world is being run by smart people who are putting us on or by imbeciles who really mean it.” -Mark Twain