Tripped by Differential Rele (87)

03/15/2009 7:16 PM

Dear all

We have new generator by rating 4,400kW;5,500kVA power factor 0.8. Whenever that generator to be loaded 700kW - 800kW that generator was normally run. If those generator has been loaded 1500kW the generator was tripped by differential rele (87)

Could you please help us to find this problem

Thanks,

-kg

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Tripped by Differential Rele (87)

03/15/2009 7:39 PM

You say it's a new generator - what do the suppliers have to say about it?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Associate

Join Date: Aug 2008
Posts: 31
#2
In reply to #1

Re: Tripped by Differential Rele (87)

03/15/2009 7:49 PM

Somebody who has commisioned this generator. But in fact that generator always tripped by 87 after loaded appox 1500kW

Register to Reply Off Topic (Score 5)
Associate

Join Date: Sep 2007
Posts: 54
Good Answers: 3
#3

Re: Tripped by Differential Rele (87)

03/16/2009 2:37 AM

Check the polarity of the current transformers.

Check the setting of the relay.

Register to Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#4

Re: Tripped by Differential Rele (87)

03/16/2009 3:03 AM

Is that generator already tested by Load Bank during commisioning ?

Is the function test of the protection relay ok ?

Register to Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#5

Re: Tripped by Differential Rele (87)

03/16/2009 3:13 AM

is the Generator already tested by Load Bank during commisioning ?

is the function test of protection relays correct ?

how much ratio of CT that put in frontside & backside of generator winding ?

is the connection correct (wye-delta or delta-delta or delta-wye) ?

is all of wiring already meggered?to make sure there are no leakage current.

is the setting of its Digital Protection Relay correct?

Register to Reply
Associate

Join Date: Aug 2008
Posts: 31
#7
In reply to #5

Re: Tripped by Differential Rele (87)

03/16/2009 6:28 PM

Hi,

All of the function of protection relay was correct, CT's ratio frontside & backside, the connection (wye-delta,delta-wye or delta-delta), no leagake current were correct as well.

CT's polarity was correct, in my opinion if CT's polarity wasn't correct then the circuit breaker will trip if we close

Your kindly advice is highly appreciated

Thanks,

Kuncoro

Register to Reply
Commentator

Join Date: Mar 2009
Location: delhi india
Posts: 79
Good Answers: 2
#6

Re: Tripped by Differential Rele (87)

03/16/2009 4:36 AM

Plz check relay setting used for o/P contactor

Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#8

Re: Tripped by Differential Relay (87)

03/16/2009 6:48 PM

There have been cases where the manufacturer labeling on the CT was incorrect, both for polarity and/or ratio. Has the ratio and polarity of each CT been verified to match the markings? If the secondary amps are expected to be 1 amp at marked load, and in fact are 5 amp at rated load, this would give you the results you are experiencing. CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#9

Re: Tripped by Differential Rele (87)

03/18/2009 2:01 AM

My Assume is :

may be there is already happen differential current. But still not detectable by Digital protection relay. may be because of wrong setting.because you only load 700KW . I dont know how muct your voltage system. but this load is only 16 % full load. so relay not yet detect the differential thing from your generator.

And then after you increase the load. Digital relay can detect the differential of current and command the breaker to trip.

That is MY ASSUME. For Further and Clearly information, please CONTACT your vendor as soon as possible.

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#10

Re: Tripped by Differential Rele (87)

03/18/2009 8:12 AM

dear,

Considering that the installation & wiring of the relay is error free,

Considering that you have already caliberated the relay with current injection kit,

& working OK,

then, if relay trips,

May I know the nature of load ? is it high frequency load like induction furnaces,

then May be due to Current Harmonics generated in the system due to load.

In this case, precautions are required to eliminate the same from sensing CTs.

__________________
Exploring the Science of Electricity
Register to Reply Score 1 for Good Answer
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

CJMcGill (1); dineshpandit80 (1); elect-ok (3); harry potter (1); JohnDG (1); Kuncoro (2); TITO60 (1)