Dear all

i want to know one thingh that how much power is taken by a 3 tones A/C. What is relation between kw & tones for A/c

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: A/C

03/18/2009 10:31 AM

what do tones have to do with air conditioners? or did you mean something else by A/C

Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#2

Re: A/C

03/18/2009 2:59 PM

Do you mean 3 phases alternating current? Relationship between kW and 3-ph is in any electrical handbook. Frequency has little to do with power, although inductive or capacitive loads designed for one frequency will consume more or less power at different frequencies.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply Score 1 for Off Topic
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: A/C

03/18/2009 7:19 PM
I found this information with a Google search.

What is the relationship between BTU and Watts?

A watt is approximately 3.412 BTU/hr.
2000 watts is about 6824 BTU/hr.

Cooling / Heating Capacity.

watts x 3.412 = BTU/hr
BTU/hr x 0.2931 = watts
Tons of Refrigeration x 12000 = BTU/hr
Tons of Refrigeration x 3516.8 = watts
kcal/h x 1.163 = watt

Some examples:

9000BTU IS 2.6kw
12000BTU IS 3.5kw
15000BTU IS 4.3kw
17000BTU IS 4.98kw
18000BTU IS 5.2kw
19000BTU IS 5.5kw
24000BTU IS 7.0kw
27000BTU IS 7.9kw
32000BTU IS 9.3kw
36000BTU IS 10.5kw
Register to Reply
Commentator

Join Date: Mar 2009
Location: delhi india
Posts: 79
Good Answers: 2
#5
In reply to #3

Re: A/C

03/19/2009 1:50 AM

i think this is best answer thanks

Register to Reply
Commentator

Join Date: Mar 2009
Location: delhi india
Posts: 79
Good Answers: 2
#6
In reply to #3

Re: A/C

03/21/2009 3:37 AM

as from your calculation

1 tone =3.5 kw

am i right so if we use a 3 tones A/c it will take 9.5 kw

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#7
In reply to #6

Re: A/C

03/21/2009 7:22 PM

dineshpandit80

You need to get on the Internet and do some of this research yourself.

After some more digging, 3.5 kw is way too high. I usually use 1.5 kw per ton. The problem is the efficiency of the modern compressor.

A electric nickel chrome heater element produces 3.4 BTU/Hour
The very efficient mechanical refrigeration compressor produces 8.533 BTU/Hour+/-
I had a 4 ton unit 10 SEER that pulled 28 amps. That's 28x240 = 6720 kva /4ton = 1.7 kva per ton
One ton of frig.=12000 BTU/hour
1 watt=8.533 BTU/hour compressor

4 tons x 12,000=48,000 BTU/hour

48,000/8.533=5,625 watts 1.4 kw per ton 1.75 kva per ton

5,625/240 volts=23 amps more efficient machine

If you include the SEER, then you can do it another way. SEER is defined as the heat transferred per unit of energy, that is in BTU/watthour.

P = AC load/SEER

For your 4 ton unit and SEER = 10,

P = (48,000 BTU/hour)/(10 BTU/watthour) = 4,800 watts,

then throwing in PF,

I = P/(VxPF) = 4800W/(240V x 0.8) = 25A 1.2 kw per ton or 1.5 kva per ton

This is comparable to the other result.

Register to Reply
Commentator

Join Date: Mar 2009
Location: delhi india
Posts: 79
Good Answers: 2
#8
In reply to #7

Re: A/C

03/23/2009 1:43 AM

Dear Sir

in your first answer you told me that

1W=3.41 BTU/H

But in second Answer you are saying that

1W=8.533 BTU/H

Plz tell me which one is right

Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#4

Re: A/C

03/18/2009 10:10 PM

OK...This looks like an Efficiency question to me. If I'm off the mark, that cool you will have many others to look at.

The way I read the questions is: -

"How much Power (kW) do I need to generate 3 tonnes of cooling Capacity?"

The answer to which is too complex to answer in a short lunchtime post.

The are are many variables such as: - Is it an Air cooled system, Water cooled, Chillers, condenser system or geothermal.

Without the details for your system, we can't work it out with you.

If this is theoretical system, you will need to understand the design parameters and location of your system to start working it out.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#9

Re: A/C

03/23/2009 11:46 AM

Read the new post again.

"A electric nickel chrome heater element produces 3.4 BTU/Hour
The very efficient mechanical refrigeration compressor produces 8.533 BTU/Hour+/- "

Register to Reply
Register to Reply 9 comments