What are the procedures for testing a cable (Power/Control) ?
Re: Cable Testing
03/19/2009 6:57 AM
what type of testing you are looking for
whether routine tests while manufacturing or testing while commisioning of the cables
if it is tests for manufacturing
for each stage hv test and insulation test will be done
while in commisioning of the cable we will check the ir values and hv test for the insulation . in critical areas we will go for the current carraying capacity test by flowing high current through the cable
also we will find the resistance of the cable by volage drop test.
hope my reply will clarify your dought
Re: Cable Testing
03/23/2009 1:25 AM
Dear Sir,
What are 1.Sheath Integrity Test 2.tan delta 3. Hot Deformation 4. HI POT Test 5.Capacitance Test 4.Inductance test & What are the procedures for conducting the tests?
Re: Cable Testing
03/19/2009 7:05 AM
One can test and record:
  • End-to-end continuity
  • Individual conductor resistance
  • Conductor to earth resistance
  • Conductor to conductor resistance
  • Insulation breakdown voltage
  • conductor to conductor capacitance
  • conductor self-inductance
  • thermal performance
  • insulation longevity
  • minimum bending radius
  • etc.
so it depends upon what is required, really.
Re: Cable Testing
03/19/2009 9:38 AM
good answar which i tryed to expalin in broad manner i should learn from you the way of presentation that what i am thinking
Re: Cable Testing
03/23/2009 1:31 AM
Dear Sir,
Please tell me some more tests & the procedures too.
Re: Cable Testing
04/23/2025 5:08 AM