Gas Water Heater - Four Cracked Lines

03/19/2009 6:04 AM

We have a large house with a 100 gal water heater and recirculating pump. Since we moved in 9 years ago, we've had failure of 4 heaters, all cracked liners. Last year, we reduced the size from 100 gal to 75 gal hoping it would make a difference. No dice. Yesterday, exactly 1 year to the day, our newest A.O. Smith gas water heater failed. Could this be due to the recirculating pump? I put it on a timer when we moved in (prior it ran constantly). Could the super cold water coming in after sitting all night in the lines cause the liner to crack?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: AO Smith 4 cracked liners

03/19/2009 6:49 AM

Where is the crack? If it is at a pipe entry point, then I'd look at vibration/fatigue issues.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Participant

Join Date: Mar 2009
Posts: 2
#3
In reply to #1

Re: AO Smith 4 cracked liners

03/19/2009 10:11 AM

The crack is in the liner inside - every time. I am wondering if the guy who installed them is "rough" and bangs the unit around while installing. I know that my door frames have taken some heavy hits from his work. This time, I plan to use a different plumber just to see if it makes a difference.

Register to Reply
Guru
Popular Science - Cosmology - New Member

Join Date: Feb 2009
Location: Halcottsville, NY
Posts: 665
Good Answers: 16
#7
In reply to #3

Re: AO Smith 4 cracked liners

03/20/2009 12:40 AM

I don't think it's the temperature differential. Your supply line goes into the top of the heater, down through a tube, and exits near the bottom of the tank. The water gets somewhat preheated on the way down to the coolest water in the tank. Check your safety valve yearly, and don't use an old valve on a new heater. A stuck valve will blow the tank. You might need a small expansion tank, and check for water hammer.

I had an A O Smith heater that ate two electrodes, as well as tripping out frequently. I was kind of glad when the damn thing started leaking after five years, and replaced it with a Bradford White that is now 14 years old and no problems yet.

Both electric heaters.

__________________
De gustibus non est dispudandum.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: AO Smith 4 cracked liners

03/19/2009 8:29 AM

Also look at furring-up issues. Magnesium and calcium carbonates (in particular) are inversely soluble in water. As the temperature goes up, they will tend to precipitate on heating surfaces, insulating them, and causing the surface temperature to increase.

If the water heater is NOT used for water to be ingested, then try upstream softening by ion exchange. The substitute for MgCO3 and CaCO3, Sodium chloride, is highly soluble in water at a wide range of temperatures.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#4

Re: Gas Water Heater - Four Cracked Lines

03/19/2009 12:47 PM

Every water heater gets cold water ran into it. As that is what its for to heat water. If the water was hot it wouldn't need heating. And the water coming in from most water supplies can be pretty cold. I don,t think that would be the problem or we all face that problem.

I would look at the pressure that the recirculating pump may be placing on the tank. Maybe there is a restriction in the line that causing the pump to put pressure on the tank. That over time fatigues it.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Commentator

Join Date: Nov 2008
Posts: 80
Good Answers: 4
#5

Re: Gas Water Heater - Four Cracked Lines

03/19/2009 11:11 PM

Do you use a pressure reducer on the incoming side? This can act like a check valve.Is there a temp & pressure valve on the tank? If not, there is no means to relieve the pressure. I have seen where the cold water is heated in the tank and there is no way to relieve the pressure, the water pressure in the system in the system can rise. This can cause the hot water valves be hard to open and it could cause a tank failure. You could put a pressure gauge on the tank to measure pressure to see if overpressuring the system is causing tank failure.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#12
In reply to #5

Re: Gas Water Heater - Four Cracked Lines

03/20/2009 7:07 PM

SSkahn6, I'm going to echo the suspicion of vtbgiraud, since I think he is on the right track.

Defects and pressure are the two major causes of tank failure. We did not get any information in your post about the pressure incoming from the main source, and the fact that water heaters have a pressure relief valve testify to the need to be aware of what pressure is doing.

Once a temp/pressure relief valve has been operated, they can lose their validity from things as simple as the calcium build-up. If you are using a pressure reducing device it is a one-way device and should be coupled with a pressure relief valve and an expansion tank since there now exists a closed system. This would be separate from the valve on the water heater, and driven by pressure only. Avoid "testing" the valve, instead monitor the pressure inside the closed system by the addition of a water pressure guage to keep an eye on the pressure. It couldn't hurt to have a guage on the incoming pressure ahead of the pressure reducer.

The more information you have to work with, the better you will do in getting to the bottom of the cause. CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Participant

Join Date: Mar 2007
Posts: 3
#6

Re: Gas Water Heater - Four Cracked Lines

03/19/2009 11:13 PM

If you take a picture of the installation. Give me the specs on the pump, heaters, line sizes, length of run, and water pressure, I could probably come up with a reasonable cause for the problem and solution.The pump could definately be part of the problem, however, it could also (most likely) be water temperature shocking the tank due to rapid expansion and contraction.

What is the temperature of the water coming into the house?

Where do you live?

What is the demand for water in gpm?

Do you run out of hot water?

What temperature do you have the tank set at?

Is the tank gas or electric?

I have a system that will not crack due to the way it is piped, will never run out of hot water (as long as you pay the utility bill), will last about 20 years, and will reduce you energy bills about 40%.

You can e-mail me at rich@rgreenwald.com if you like.

Register to Reply
Power-User

Join Date: Mar 2009
Location: O'er looking the silvery Tay
Posts: 255
Good Answers: 18
#8

Re: Gas Water Heater - Four Cracked Lines

03/20/2009 6:36 AM

Re:Four cracked liners.

You do not describe where the cracking occurs in the heater. Depending on the type of burner used there will be a temperature gradient across the vessel/tube section in keeping with the volume of products of combustion; ie open flued v pressure jet type. Does this heater have independant flue tubes through the water space or is all the heat transferred to the bottom and ouside surfaces as per the 'Andrews' design. Is there any sign of wasteage in the area of cracking? if there is you probabaly need a sacrificial anode to protect the shell.

__________________
If it ain't broke,leave it well alone .........until it comes looking for you!
Register to Reply
Anonymous Poster
#9

Re: Gas Water Heater - Four Cracked Lines

03/20/2009 9:41 AM

Shut off the circulation pump. Wait and see if the problem goes away. You'll be saving money at the same time. While you are at it put in a tank-less hot water heater. You'll save a ton more of money. We are supposed to be conserving energy these days.

Register to Reply
Member

Join Date: Sep 2007
Location: Edmonton, Alberta, Canada
Posts: 8
Good Answers: 1
#10

Re: Gas Water Heater - Four Cracked Lines

03/20/2009 10:04 AM

You may wish to change to an instantaneous water heater. They are more expensive, but you save energy since you are not heating up water due to the tanks thermal losses. The domestic hot water tank is one of the most inefficent devices ever installed.

Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#11
In reply to #10

Re: Gas Water Heater - Four Cracked Lines

03/20/2009 10:43 AM

You may wish to change to an instantaneous water heater..
Which will fur up and burn out with monotonous regularity?

The domestic hot water tank is one of the most inefficent devices ever installed.
If it's correctly sized and well insulated...is this still the case?

Just asking...don't shoot the puddy tat.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Off Topic (Score 5)
Guru
Hobbies - DIY Welding - pipewelder

Join Date: Apr 2007
Location: North Georgia, USA
Posts: 671
Good Answers: 33
#13

Re: Gas Water Heater - Four Cracked Lines

03/23/2009 4:26 PM

I think either your plumber or someone that handled the hot water heater probably did it incorrectly and cracked it. If it is not near an inlet or outlet I would not think vibration could cause it. Although minerals in you heater can cause a build up that prevents heat transfer I have never seen this build up cause a crack. Is there some way you can check it before you put it in? I think this would be best and would at least answer a big question about the handling of the heater. I have a problem with servicemen not treating the stuff they work on or other equipment they work near like they should. I am doing a remodel project on a bathroom and the guys that put in my vanity tops did a very good job and literally destroyed some stained and varnished base moulding along the way. I caught one of them standing on it once and I had it stacked out of their way. I really think they did it on purpose because it is hard to believe anyone with the skills they had could be this stupid. In the end after they left I had to replace some of the base board trim at my cost.

__________________
pipewelder
Register to Reply
Member

Join Date: Nov 2014
Posts: 5
#17
In reply to #13

Re: Gas Water Heater - Four Cracked Lines

12/24/2014 2:48 AM

I think you should consult the experts .

Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#18
In reply to #17

Re: Gas Water Heater - Four Cracked Lines

12/24/2014 10:37 PM

You will find them here David. Centuries of experience and practical wisdom reside on this forum. After 3 cracked tanks within a year, I found the pressure from the incoming supply was rising well over 120 psi at night. A pressure regulator, expansion tank & 75 psi relief valve (without heat release element, just pressure) ended the problem.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Anonymous Poster
#14

Re: Gas Water Heater - Four Cracked Lines

03/24/2009 11:42 AM

Thanks to everyone for your responses. We think we've determined it is a water pressure problem. Looks as if the pressure builds up overnight. During daytime it is 55, but under the overflow pipe from the pressure relief valve it is WET! Also, I keep finding water in that bathtub and sinks in the mornings, but no one was using them. Put in a new water heater and expansion tank this time, but will add a pressure regulator to incoming waterline as well after reading your posts.

Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#15
In reply to #14

Re: Gas Water Heater - Four Cracked Lines

03/24/2009 11:53 AM

Don't forget to also add an independent pressure relief valve on the user side of the pressure regulator. This valve should have a release setting lower than the 150# usually found on the heat/pressure relief valve of the water heater. This is because the pressure regulator creates a "trapped" water system, which can not back-flow back into the main supply line when the water heater expands the volume. The expansion tank is excellent, but has it's limits.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#16

Re: Gas Water Heater - Four Cracked Lines

03/26/2009 7:17 AM

Have you checked your water for methane gas infiltration that added pressure could cause it.

__________________
If you never do anything you never have problems.
Register to Reply
Register to Reply 18 comments

"Almost" Good Answers: