GFI for Fountain Pump?

03/20/2009 8:58 AM

Is it necessary to have a submerged fountain pump plugged into a GFI switch? The installer has the pump plugged into such an outlet, but the slightest amount of moisture from rain, etc. trips the switch and has made operation of the fountain inconvenient.

__________________
“Better to remain silent and be thought a fool than to speak out and remove all doubt. - Abraham Lincoln”
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: GFI for Fountain Pump?

03/20/2009 9:58 AM

Its tripping indicates an earth fault that requires attention on safety grounds.

Inconvenient, saving life, isn't it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: GFI for Fountain Pump?

03/20/2009 4:59 PM

If the GFI device is outside and is tripping, then you need to place a cover over it.

1- Gang Weatherproof Bubble Cover

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: GFI for Fountain Pump?

03/20/2009 5:49 PM

Check Leviton GFCI Accesories. Search for 5977 and 5997 series.

http://www.leviton.com/OA_HTML/ibeCCtpSctDspRte.jsp?section=10136&minisite=10026

Register to Reply
Commentator

Join Date: Nov 2007
Posts: 85
Good Answers: 4
#4

Re: GFI for Fountain Pump?

03/20/2009 11:06 PM

Could a GFI breaker be used instead of the GFI outlet?

ChazL

Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#5
In reply to #4

Re: GFI for Fountain Pump?

03/21/2009 12:40 AM

Yes, you can, much more expensive breaker, but like the OP mentioned about the cover, if the receptacle (with out cover) and breaker are wired correctly, you will trip the breaker now. Put that cover on and be done.

__________________
"Real Bass Players" do not use picks
Register to Reply
Commentator

Join Date: Nov 2007
Posts: 85
Good Answers: 4
#6
In reply to #5

Re: GFI for Fountain Pump?

03/21/2009 6:47 AM

Yes Jimh77,

The breaker is more expensive, but the OP did not mention anything about a cover so I was just giving another possible solution adding to the one Wareagle mentioned.

ChazL

Register to Reply
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#7

Re: GFI for Fountain Pump?

03/21/2009 11:01 AM

Yes,

It is the law, contact the AHJ and ask him to approve you're solution. (you will have to wait some hours before he stops laughing)

An alternative approach is add a junction box in the feeder line to the outlet plug and connect the cable from the pump directly to the power.

You can add clocks and other futuristic devices like to organise the functionality.

__________________
"Here we are now, entertain us"
Register to Reply
Commentator
Canada - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member

Join Date: Aug 2008
Location: St. Albert, Alberta, Canada
Posts: 65
Good Answers: 11
#8

Re: GFI for Fountain Pump?

03/23/2009 2:23 PM

Some GFI receptacles are notoriously poor quality, and tend to fail for no reason at all after a short time. It may be that you simply need to replace the receptacle itself. Adding the weatherproof cable housing mentioned earlier is a very good idea, but may not solve the issue if you have a bad GFI.

Cheers,

Steamerst

__________________
"You are, what you do, when it counts" - John Steakley (Armor) 1984
Register to Reply
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#9
In reply to #8

Re: GFI for Fountain Pump?

03/23/2009 5:25 PM

It is a real problem: the GFI becomes nervous due it's own loss and the handy neighbour takes it out.

Then the accidents happen.

__________________
"Here we are now, entertain us"
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers: